Condensate Drain

  • 20-08-2015 10:13pm
    #1
    Closed Accounts Posts: 63 ✭✭


    Im fitting a grant boiler in garage attached to the house.There is a sink on the opposite wall to where the boiler is fitted.im going to connect up 1 1/4 abs pipe through the wall and bring it into the garage and use this as a condesate drain.I will also fit a trap on the abs pipe in the garage.
    1/ Will this arrangement be ok?
    2/ If the boiler is not running during the summer ,would the trap run dry and cause back smells,and would there be a better solution to this?


Comments

  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    pat35 wrote: »
    Im fitting a grant boiler in garage attached to the house.There is a sink on the opposite wall to where the boiler is fitted.im going to connect up 1 1/4 abs pipe through the wall and bring it into the garage and use this as a condesate drain.I will also fit a trap on the abs pipe in the garage.
    1/ Will this arrangement be ok?
    2/ If the boiler is not running during the summer ,would the trap run dry and cause back smells,and would there be a better solution to this?

    I don't think anyone is going to assist you on here with a diy install of a boiler that could potentially give off high CO if not installed correctly. If the condensate pipework isn't installed correctly it could also leak dangerous co fumes


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    pat35 wrote: »
    Im fitting a grant boiler in garage attached to the house.There is a sink on the opposite wall to where the boiler is fitted.im going to connect up 1 1/4 abs pipe through the wall and bring it into the garage and use this as a condesate drain.I will also fit a trap on the abs pipe in the garage.
    1/ Will this arrangement be ok?
    2/ If the boiler is not running during the summer ,would the trap run dry and cause back smells,and would there be a better solution to this?

    Yes ,bring out the 1 1/4 pipe from the bathroom.connect 3/4 qualpex from the condensate trap at the boiler to the pipe from bathroom,making sure both ends are SEALED.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    Yes ,bring out the 1 1/4 pipe from the bathroom.connect 3/4 qualpex from the condensate trap at the boiler to the pipe from bathroom,making sure both ends are SEALED.

    As far as I know any pex pipe isn't yet approved for condensate.
    And sealing off the pipe completely is a bad idea because with no air break, there's a high risk that the condensate trap will have its water syphoned out and therefore your pipe becomes a flue for a period of time. If this pipe is a flue, and the boiler is installed by a DIYer and not commissioned, then you've a good chance there's gonna be high CO in the waste pipe


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Dtp1979 wrote: »
    As far as I know any pex pipe isn't yet approved for condensate.
    And sealing off the pipe completely is a bad idea because with no air break, there's a high risk that the condensate trap will have its water syphoned out and therefore your pipe becomes a flue for a period of time. If this pipe is a flue, and the boiler is installed by a DIYer and not commissioned, then you've a good chance there's gonna be high CO in the waste pipe

    What pipe is approved?,what pipe do you use for condensate?


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Dtp1979 wrote: »
    As far as I know any pex pipe isn't yet approved for condensate.
    And sealing off the pipe completely is a bad idea because with no air break, there's a high risk that the condensate trap will have its water syphoned out and therefore your pipe becomes a flue for a period of time. If this pipe is a flue, and the boiler is installed by a DIYer and not commissioned, then you've a good chance there's gonna be high CO in the waste pipe[/QUOT
    would the air break not be in sink


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    What pipe is approved?,what pipe do you use for condensate?
    I've ever used pex for condensate
    Id always use 22mm plastic waste


  • Registered Users, Registered Users 2 Posts: 360 ✭✭Kealyboy


    pat35 wrote: »
    Im fitting a grant boiler in garage attached to the house.There is a sink on the opposite wall to where the boiler is fitted.im going to connect up 1 1/4 abs pipe through the wall and bring it into the garage and use this as a condesate drain.I will also fit a trap on the abs pipe in the garage.
    1/ Will this arrangement be ok?
    2/ If the boiler is not running during the summer ,would the trap run dry and cause back smells,and would there be a better solution to this?
    Yes this arrangement should be ok. Just follow the MI when installing/connecting condensate drain pipe work into 1 1/4 wastepipe. If instated properly it should not cause any siphonage from trap and finally on completion get the boiler commissioned.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Kealyboy wrote: »
    Yes this arrangement should be ok. Just follow the MI when installing/connecting condensate drain pipe work into 1 1/4 wastepipe. If instated properly it should not cause any siphonage from trap and finally on completion get the boiler commissioned.

    No decent self respecting service engineer is going to commission a diy boiler install


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    Dtp1979 wrote: »
    As far as I know any pex pipe isn't yet approved for condensate.
    And sealing off the pipe completely is a bad idea because with no air break, there's a high risk that the condensate trap will have its water syphoned out and therefore your pipe becomes a flue for a period of time. If this pipe is a flue, and the boiler is installed by a DIYer and not commissioned, then you've a good chance there's gonna be high CO in the waste pipe[/QUOT
    would the air break not be in sink

    How so? I'd put the air break close to the boiler if possible, depending on pipe run length


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Dtp1979 wrote: »
    I've ever used pex for condensate
    Id always use 22mm plastic waste

    Any plastic pipe is approved,copper is not


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    Any plastic pipe is approved,copper is not

    Are u sure?
    I'm not 100% sure myself. Maybe Pex is ok on a very short run but it bends too easy which could leave sagging pipe on horizontal areas and it Wouldn't be neat or straight on vertical


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Dtp1979 wrote: »
    agusta wrote: »

    How so? I'd put the air break close to the boiler if possible, depending on pipe run length

    i dont think this is approved.if you leave an air gap and the condensate trap runs dry,are you potentially leaving a gap for co to escape, the grant vortex manual says it should be sealed to an internal waste


  • Registered Users, Registered Users 2 Posts: 360 ✭✭Kealyboy


    Dtp1979 wrote: »
    No decent self respecting service engineer is going to commission a diy boiler install

    Could be a bit tricky alright but if you ask nicely and on inspection if everything is found to be ok I don't see why a service engineer wouldn't commission the boiler and fill out passport. This is assuming now that on inspection boiler is installed to MI.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    Dtp1979 wrote: »

    i dont think this is approved.if you leave an air gap and the condensate trap runs dry,are you potentially leaving a gap for co to escape, the grant vortex manual says it should be sealed to an internal waste

    True on the vortex alright. But in many gas boilers, they insist on a tundish being fitted. So each to their own I guess


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Kealyboy wrote: »
    Could be a bit tricky alright but if you ask nicely and on inspection if everything is found to be ok I don't see why a service engineer wouldn't commission the boiler and fill out passport. This is assuming now that on inspection boiler is installed to MI.

    In fairness no DIYer is gonna fit a boiler correctly. And no self respecting service engineer will sign off on it.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    except in this case going by op previous post he is not a Diyer,more than likely a plumber


  • Closed Accounts Posts: 5,681 ✭✭✭JustTheOne


    Kealyboy wrote: »
    Could be a bit tricky alright but if you ask nicely and on inspection if everything is found to be ok I don't see why a service engineer wouldn't commission the boiler and fill out passport. This is assuming now that on inspection boiler is installed to MI.

    Why in God's name would you put your name to someone else's work?

    Madness.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    JustTheOne wrote: »
    Why in God's name would you put your name to someone else's work?

    Madness.

    Some plumbers fit boilers and dont have a flue gas analyser or coursers done to commision or sign off the boiler to validate the warranty.it quite normal for a plumber to get a service technician to do this


  • Closed Accounts Posts: 5,681 ✭✭✭JustTheOne


    agusta wrote: »
    Some plumbers fit boilers and dont have a flue gas analyser or coursers done to commision or sign off the boiler to validate the warranty.it quite normal for a plumber to get a service technician to do this

    Fair enough.

    But in my opinion anyone who cares about their work and name or even not wanting to end up in front of a judge would be stupid to sign off on someone elses installation of a boiler.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    except in this case going by op previous post he is not a Diyer,more than likely a plumber

    I seriously doubt it if he's asking about a simple waste solution to a condensate pipework problem


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 360 ✭✭Kealyboy


    JustTheOne wrote: »
    Why in God's name would you put your name to someone else's work?

    Madness.
    Well when you service any boiler your putting your name to that boiler. If anything happens to that boiler in the mean time it falls back on the service engineer who serviced the boiler last whether or not a 1000 Cowboys were at the boiler previous to you.

    So what's the difference if installed correctly.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    JustTheOne wrote: »
    Fair enough.

    But in my opinion anyone who cares about their work and name or even not wanting to end up in front of a judge would be stupid to sign off on someone elses installation of a boiler.

    Not the case,its either installed correctly or its not,and the persons commissions the boiler sets up the burner to mi .so the guy who commissions the boiler is signing off on his own work


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Dtp1979 wrote: »
    I seriously doubt it if he's asking about a simple waste solution to a condensate pipework problem

    point taken.so lets take it he is a plumber..,what advice would you give to connect a condensate waste from a Oil boiler to a internal waste?. What seems to be a "simple waste solution to a condensate pipework",doesnt seem so simple after all,and if op is competent we should be adviseing him correctly..


  • Posts: 0 [Deleted User]


    agusta wrote: »
    Not the case,its either installed correctly or its not,and the persons commissions the boiler sets up the burner to mi .so the guy who commissions the boiler is signing off on his own work

    In the event of a incident the commissioning engineer doesn't get to choose which bit is their responsibility and which bit is the installers, they have Duty Of Care and the level of responsibility is decided for them.

    When you sign off on somebody else's work there is a level of risk for any issues that may arise irrespective of who's work it is. I don't put my name to other people's work as I have trust issues.

    As a manufacturers representative I have seen many situations where it becomes a petty blame game when I identify faux pars on a installation.

    Condensate lines are simple but yet mistakes are made, why take a risk by following online advice, the safe option would be to have a local tame Oftec engineer looking at the installation and giving advice.


  • Registered Users, Registered Users 2 Posts: 360 ✭✭Kealyboy


    As I said in a previous post.

    "Well when you service any boiler your putting your name to that boiler and saying that the boiler is installed and running to manufacture specification. If anything happens to that boiler in the mean time it falls back on the service engineer who serviced the boiler last whether or not a 1000 Cowboys were at the boiler previous to you".

    So what's the difference in commissioning and signing off this installation if installed correctly, as I am sure you don't just only service boilers that you have installed.


  • Posts: 0 [Deleted User]


    Kealyboy wrote: »
    As I said in a previous post.

    "Well when you service any boiler your putting your name to that boiler and saying that the boiler is installed and running to manufacture specification. If anything happens to that boiler in the mean time it falls back on the service engineer who serviced the boiler last whether or not a 1000 Cowboys were at the boiler previous to you".

    So what's the difference in commissioning and signing off this installation if installed correctly, as I am sure you don't just only service boilers that you have installed.

    It's only a problem when it's a problem.

    Servicing a boiler and signing off on a new installation are two completely different things in respect of responsibility as I have witnesses.