MHRV Noise/Bathrooms

  • 13-07-2015 10:51pm
    #1
    Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭


    Finally got the MHRV installed and commissioned in the past week. Its a zehnder 550 unit. I was curious to know from anyone with a similar system, is ther a noise from your supply and extract. Mine is very shallow noise like an airplane is the distance, you really don't hear it until its silent at night. It's not something that would keep you awake but I wondered if this is the same for others. The system itself is set at "2" and the commissioned report says its running at 48% efficiency. The bathrooms are not on a boost (unit does not support boost or humidity) but the mirrors do steam up, is this the norm ? The bathroom itself clears within 5 mins after a shower.


Comments

  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    48% efficiency for a PHI approved unit?
    This is ridiculous
    http://www.zehnder.co.uk/comfosystems/index.php?pageID=63&ProductOverview:category=&category=&template=18_product_detail.html&product_detail:oid=58
    is the spec sheet
    Are you at 2 or Level 2, which is 70% of max so even if u at Level 2 why can't you up it to Level 3 even for a few minutes

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    48% efficiency for a PHI approved unit?
    This is ridiculous
    http://www.zehnder.co.uk/comfosystems/index.php?pageID=63&ProductOverview:category=&category=&template=18_product_detail.html&product_detail:oid=58
    is the spec sheet
    Are you at 2 or Level 2, which is 70% of max so even if u at Level 2 why can't you up it to Level 3 even for a few minutes

    Hi Calahonda52, the switch is at 2, I dont know the difference between your statement on "2 or Level 2", is there another setting ?

    On "why can't you up it to Level 3 even for a few minutes", why ? I'm wondering if anyone else is experiencing a noise, this would just amplify the noise level. If your referring to increasing to level 3 for showers, the unit is on another floor so you would'nt expect to do this at the unit for every shower you take and the system seemingly does not support boost which is only available on the next model and its too late now.


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    open the link and click on the technical tab and scroll down for 2 vs Level 2, assuming I have the right unit

    Have u no control panel like for normal heating?

    Any" boost" yes will move the air everywhere faster for a while but it is MHRV with a theoretical efficiency of close to 95 % :)

    How many silencers were fitted and where?

    What was the design flow rate for normal operations vs the Level 3 max of 460m3/h

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    open the link and click on the technical tab and scroll down for 2 vs Level 2, assuming I have the right unit

    Have u no control panel like for normal heating?

    Any" boost" yes will move the air everywhere faster for a while but it is MHRV with a theoretical efficiency of close to 95 % :)

    How many silencers were fitted and where?

    What was the design flow rate for normal operations vs the Level 3 max of 460m3/h

    Afriad I can't answer all the questions.

    There is a control panel on the unit itself but I've not touched that as it seemed to be set there during the commissioning and its not the most intuitive of panels.

    No silencers fitted that I'm aware off (any pic of what these look like?)


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    From Google https://www.google.ie/search?q=mhvr+silencers&lr=&safe=images&source=lnms&tbm=isch&sa=X&ved=0CAgQ_AUoAWoVChMI3oiPwpfdxgIV6Y7bCh0klwbT&biw=2560&bih=1235

    they look like car exhausts.

    Re the manual, see the pdf below, have u the Luxe version.
    Did u get the 3 or 4 page commissioning report as shown in the manual?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    From Google https://www.google.ie/search?q=mhvr+silencers&lr=&safe=images&source=lnms&tbm=isch&sa=X&ved=0CAgQ_AUoAWoVChMI3oiPwpfdxgIV6Y7bCh0klwbT&biw=2560&bih=1235

    they look like car exhausts.

    Re the manual, see the pdf below, have u the Luxe version.
    Did u get the 3 or 4 page commissioning report as shown in the manual?

    No luxe version
    No commisioning report yet

    http://info.zehnderamerica.com/blog/why-are-some-hrvs-ervs-so-noisy
    "Some HRV/ERV systems, such as Zehnder’s, are built in with sound attenuators (or silencers) to minimize noise."; makes me wonder if more are needed.


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    1: you need to get the design spec for the project:
    air flows, duct sizes, etc etc.
    2: get the tech spec for the exact model you have.
    3: itemised invoice for all the kit installed

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    1: you need to get the design spec for the project:
    air flows, duct sizes, etc etc.
    2: get the tech spec for the exact model you have.
    3: itemised invoice for all the kit installed

    Thanks; I was more interested to know if this is a common noise or should one expect complete silence.


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    Thanks; I was more interested to know if this is a common noise or should one expect complete silence.

    It all depends on the design which is why u need the data above.
    High flow rates in crap ducting that is too small in diameter will give noise.

    low flow rates in wide diameter ducting with noise attenuators will just leave the unit as the noise source so how is it mounted?
    fixed to concrete wall with rubber shock absorbers or sitting on the ceiling rafters?

    Given what you have posted here nothing would surprise me

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    It all depends on the design which is why u need the data above.
    High flow rates in crap ducting that is too small in diameter will give noise.

    low flow rates in wide diameter ducting with noise attenuators will just leave the unit as the noise source so how is it mounted?
    fixed to concrete wall with rubber shock absorbers or sitting on the ceiling rafters?

    Given what you have posted here nothing would surprise me

    It is fixed to concrete wall with rubber shock absorbers.
    2 x 75mm ducts to each supply and from each extract

    Is any level of noise common in the correct setup ?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    download a sound app onto your phone/tablet and do a noise test in the bathroom or wherever: leave the phone down on, try to have it at head height, and try be as quite as possible, take the reading and look up the spec on the technical tab.
    There will alway be some noise as its a mechanical plant with two elec motors so yes it won't be 100% silent.

    Without having the math on the cals, house size etc 2 by 75 is not useful.
    You really do need to find out what it is running at, can't help anymore till you provide this info.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    I've a beam unit 12" duct from outside vent to unit. 10" across attic, 8" to first floor bedrooms and 8" to two rooms on ground floor 6" to the rest due to height restrictions.
    There are baffles installed back from the vents in the ceiling. Unit isn't commisssioned yet. Is it better to have the larger ducts to reduce the sound.


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    hexosan wrote: »
    I've a beam unit 12" duct from outside vent to unit. 10" across attic, 8" to first floor bedrooms and 8" to two rooms on ground floor 6" to the rest due to height restrictions.
    There are baffles installed back from the vents in the ceiling. Unit isn't commisssioned yet. Is it better to have the larger ducts to reduce the sound.

    yes because say you have a requirement of 210m3/h and a preferred max flow rate of 2.5m/s and there are 3600 seconds in an hour, gives a cross sectional area of 0.0237m2 which is a 170mm dia duct or a 300mm by 77mm rectangular duct. { number from a project on my desk:eek:] 210/(2.5*3600)

    So if u make the duct bigger, the flow rate will drop and via versa, lower speed is less noise, don't know if there is a min flow rate I have seen a range of 2 to 3 m/s

    As well as the baffles, do u have silencers in line?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    Yeah silencers installed as well.


  • Registered Users, Registered Users 2 Posts: 9,372 ✭✭✭893bet


    This was one the reasons I went with the Teed off system. The 75mm pipe used in the manifold system seemed a bit small to me and I was concerned about flow rate.


  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    I had a couple of PM's re this thread but just for the wider followup; The unit it the zehnder 550 hrv unit; its a manifold system; the noise is not from the unit which is quiet but from the supplies in the rooms; simply put, its a HUGE waste of money, stress and time; the only work around is to have a 3 way timer switch installed so its on a very low setting at night - thus, why bother..


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭rampantbunny


    I had a couple of PM's re this thread but just for the wider followup; The unit it the zehnder 550 hrv unit; its a manifold system; the noise is not from the unit which is quiet but from the supplies in the rooms; simply put, its a HUGE waste of money, stress and time; the only work around is to have a 3 way timer switch installed so its on a very low setting at night - thus, why bother..


    Does the noise keep you awake (can you get used to it)? Is there mould in your house?
    If no to the above, while it's not ideal for you without boost function, it's probably still doing it's job.

    The lack of automatic boost/humidity detection would bother me TBH, but sleep is more important than fogged up mirrors. I expect some noise from my system (not installed yet), but any hotel room I've ever stayed in has always had some background ventilation noise and I even find it relaxing. A bit of white noise (as long it is consistent) is OK with me as it can drown out other noises. Even working here in office, there is constant noise from what must be 24" ducting. When the ventilation rates reduce after hours, it is a very quiet place. You can hear every key press on the keyboards it is that quiet - too quiet.


    On the lack of boost/humidity detection; I'm no sparks, but if you can lower the system level at night on a timer, you should be able to boost your system using the same approach. Instead of a timer changing the system level, a humidistat does the same thing. Should be able to place a stat in the return duct into the system and wire from there.


  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭Curious Geroge


    Does the noise keep you awake (can you get used to it)? Is there mould in your house?
    If no to the above, while it's not ideal for you without boost function, it's probably still doing it's job.

    The lack of automatic boost/humidity detection would bother me TBH, but sleep is more important than fogged up mirrors. I expect some noise from my system (not installed yet), but any hotel room I've ever stayed in has always had some background ventilation noise and I even find it relaxing. A bit of white noise (as long it is consistent) is OK with me as it can drown out other noises. Even working here in office, there is constant noise from what must be 24" ducting. When the ventilation rates reduce after hours, it is a very quiet place. You can hear every key press on the keyboards it is that quiet - too quiet.


    On the lack of boost/humidity detection; I'm no sparks, but if you can lower the system level at night on a timer, you should be able to boost your system using the same approach. Instead of a timer changing the system level, a humidistat does the same thing. Should be able to place a stat in the return duct into the system and wire from there.

    Its not noise from the boost, its noise from the normal running of the system. We have to put the system down to run at speed 1 at night and back up to 2 during the daytime. Could we get used of it ? Nope, its like having a plane fly directly over the house. The unit has no boost for the mirrors etc..


  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭rampantbunny


    Its not noise from the boost, its noise from the normal running of the system. We have to put the system down to run at speed 1 at night and back up to 2 during the daytime. Could we get used of it ? Nope, its like having a plane fly directly over the house. The unit has no boost for the mirrors etc..

    I understand that CG. I was splitting the issue into two, firstly the noise, secondly the lack of boost.
    As you said you were reducing the system to level 1 via a timer at night (therefore you can change the levels via a signal), I was suggesting using a similar mechanism to increase to level 3 when humidity is detected.


  • Registered Users, Registered Users 2 Posts: 12,822 ✭✭✭✭galwaytt


    ...I have an 'old', i.e. early HRV unit, and yes, there's (some) noise - esp as the unit is mounted directly above the bathroom. On the GF you can't hear anything. I actually don't even notice it anymore.

    But I have to say, not having a 'boost' functions is distinctly odd imho.

    There's also HRV unit in the room next to my office and is a much more advanced (aka, expensive unit), and it is noticeably noisy. Not being a manifold system, and the first outlet being in my office about 2m from the unit means I've got the jet noise too. Again, I don't notice it anymore, but in a house it would be an issue.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 907 ✭✭✭rampantbunny


    galwaytt wrote: »
    ...I have an 'old', i.e. early HRV unit, and yes, there's (some) noise - esp as the unit is mounted directly above the bathroom. On the GF you can't hear anything. I actually don't even notice it anymore.

    But I have to say, not having a 'boost' functions is distinctly odd imho.

    There's also HRV unit in the room next to my office and is a much more advanced (aka, expensive unit), and it is noticeably noisy. Not being a manifold system, and the first outlet being in my office about 2m from the unit means I've got the jet noise too. Again, I don't notice it anymore, but in a house it would be an issue.

    What diameter ducting is used for the 'old' setup?