Timer wont switch off

  • 24-03-2015 11:25am
    #1
    Registered Users, Registered Users 2 Posts: 157 ✭✭


    My central heating is controlled with a room thermostat and an analogue timer switch with on, off and clock settings. Problem I have is that the switch will not
    turn the boiler off. The indicator light remains on when the switch is in the off position. I thought it may have been a faulty switch but got that replaced and the problem is still there. The only way I can turn the boiler off is by the contact breaker on the fuse board.
    Appreciate any advice?
    Many thanks


Comments

  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    You'll need to give us a little more information.

    When you say the indicator stays on, which indicator? Is it the neon on the timeswitch and does the timeswitch look a bit like this?

    FL09_31100_300x300.jpg

    If the answer is yes, then the timeswitch was replaced by someone who had no idea what they were doing. Repeat the process with someone who does know.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Yes thats exactly the same timeswitch and the neon light remains on when the slider is in the 'off' position. A qualified plumber did fit the switch for me and it worked fine for about 8 months . Now suddenly doesnt work . I have not switched the system on for a while and a neighbour suggested the problem may be a motorised valve sticking. Does this make sense ?


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    Your neighbour is using his head (better it seems than I am this morning)

    A stuck motorised valve can give this result.

    The valve has a permanent, unswitched supply, so if it sticks open - or in the case of some makes, if someone has operated the manual lever, then it will keep the boiler operating and feed back to the timeswitch, illuminating the neon.

    See if you can find the motor valve; it will look a bit like this:
    motorised_valve.png

    Check the lever on the side and make sure it is reasonably free to move. If it is, then the valve is probably stuck.

    Let me know what you find and also what the valve looks like and we can take it from there.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    nmacc, help much appreciated thank you. Where would the valve be situated? House is a bungalow and boiler is external with pipes running externally to the attic and then down the walls to the rads. I wont be back until Friday and I will have a search and take photo then. In the meantime many thanks again.


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    Try the hot press. If you have one thermostat for the house then there is possibly another thermostat on the hot water cylinder giving you separation of heating and hot water. You may have either two 2-port valves or one 3-port valve. Two separate 2-port valves would be more common in Ireland and easier to work on.

    Irrespective of the status of the central heating or hot water, either valve could be at fault. When you know what you've got, post the details & we can take it further.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Thanks again. Why is it necessary to have a motor valve ? I presume the thermostats can simply knock off the power to the boiler when the room and or water is up to temp ?


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Sorry ..stupid I get it now so that space heating and water heat are independent .


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    nmacc wrote: »

    The valve has a permanent, unswitched supply, so if it sticks open - or in the case of some makes, if someone has operated the manual lever, then it will keep the boiler operating and feed back to the timeswitch, illuminating the neon.

    Stuck valve can cause boiler to stay on but with your theory it cannot backfeed to neon on time switch. Live out would be to coil on valve, switching contacts on valve are a seperate identity.


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    Stuck valve can cause boiler to stay on but with your theory it cannot backfeed to neon on time switch. Live out would be to coil on valve, switching contacts on valve are a seperate identity.

    D'you know, you have a point there Kevin, I knew I should have gone to bed earlier.

    So we're back to incorrect wiring. Of course we don't know what kind of incorrect wiring.

    I suppose Occam's Razor suggests the original time switch died - as that type so frequently does - and the replacement was wired arseways.


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    nmacc wrote: »
    the replacement was wired arseways.

    By a taxi driver no doubt.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,381 Mod ✭✭✭✭Wearb


    It worked fine for 8 months. Probably is a faulty timer.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Many thanks really appreciate all the interest.
    The previous timer was an apt and exactly the same symptoms worked for about a year and then would not switch off. The replacement Immermat was installed by a professional as was the apt and as I said worked fine for 8 months and now wont switch off. Surely its odds on to be some issue other than the timer ?


  • Moderators, Home & Garden Moderators Posts: 6,381 Mod ✭✭✭✭Wearb


    Post this in the electrical forum.

    I have seen a problem many years ago caused by a small current being induced in a switched off wire. In the case that comes to mind, it was caused by power from a neighbouring live wire in the same conduit. That time a certain bulb holder kept blowing the bulbs.

    May not be the cause of your problem. I only mention it to show how difficult it can be to pin down some problems.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Has the room stat a permanent feed I wonder and is calling for heat, if you turn down the stat to minimum that would eliminate that.


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    Once again I didn't read carefully enough. If it was replaced and worked correctly for a year, then obviously the wiring is correct.

    My money would be on a second faulty timer. In my experience these things are definitely the most unreliable timer on the market. It seems to be a function of the design, as I've had repeated problems with Flash and APT makes.

    I suggest you go for a simple digital timeclock like this:

    54007-2.jpg

    You'll be limited to a maximum of three on/off periods per day, but it'll be much more reliable; you won't even have to reset the clock if the power fails.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Thanks Kevin , I will try that.
    On Wearb's point re the induced current, would this be sufficient to override the switch contacts in the timer ? or just affect the indicator light .

    Wondering if I can just use the boiler for rad the heating and work the hot water off the immersion heater. If I close down the h/w cylinder circuit using the manual valve at the cylinder and then disconnect the motor valve from the power supply and leave it open. The boiler then would be used to supply only the rads. Would this eliminate the motor valve and the induced current apparent issues ?
    Does this make sense ?


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Sorry nmacc , I didnt see your post until after I posted this morning. Hard to believe that these clocks are so unreliable in fact now that I think about it the Immermat is the 3rd clock that has been installed the two previous being APt.
    Though it still would not solve the induced current problem ?


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    makfli wrote: »
    Though it still would not solve the induced current problem ?

    I seriously doubt you have an induced current problem, and on another note them apt timers are rubbish so them failing is no suprise.


  • Moderators, Home & Garden Moderators Posts: 6,381 Mod ✭✭✭✭Wearb


    "Post this in the electrical forum.

    I have seen a problem many years ago caused by a small current being induced in a switched off wire. In the case that comes to mind, it was caused by power from a neighbouring live wire in the same conduit. That time a certain bulb holder kept blowing the bulbs.

    May not be the cause of your problem. I only mention it to show how difficult it can be to pin down some problems. "

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Wearb wrote: »

    I have seen a problem many years ago caused by a small current being induced in a switched off wire. In the case that comes to mind, it was caused by power from a neighbouring live wire in the same conduit. That time a certain bulb holder kept blowing the bulbs.

    This makes no logical sense whatsoever, was it mens shed that this discovery was made?


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,381 Mod ✭✭✭✭Wearb


    This makes no logical sense whatsoever, was it mens shed that this discovery was made?

    No men's sheds in those days. Do you understand how a current can be induced in another non current carrying wire by induction? Are you aware that this is how transformers work? This is not an unknown phenomenon amongst experienced electricians.

    Those sort of problems are often not understood by non electricians (you are an example of this) and that is why I asked that this question be posted in the electrical forum.

    It may be only a coincidence that both timers broke down, but there may be something else at play.

    Mod: play nice now please.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Wearb wrote: »
    No men's sheds in those days. Do you understand how a current can be induced in another non current carrying wire by induction? Are you aware that this is how transformers work? This is not an unknown phenomenon amongst experienced electricians.

    I am well aware and educated on how induction works, can you explain exactly the situation that you experienced, the voltages, cable csa, amount of cables in the conduit, what voltages were the appliances, what wattage etc.
    Those sort of problems are often not understood by non electricians (you are an example of this) and that is why I asked that this question be posted in the electrical forum.

    Ill choose to ignore that Infantile comment on my knowledge, we can all put up theories but if we cant explain them and pawning it off when put on the spot is then these theories are only a conspiracy.

    Mod:as above.


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    If its just the neon staying on , without the boiler staying on . Could there be a chance theres reverse polarity sending a bit of voltage down the neutral to power the neon ? Could be way off of course but its worth a punt


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Egass13 wrote: »
    If its just the neon staying on , without the boiler staying on . Could there be a chance theres reverse polarity sending a bit of voltage down the neutral to power the neon ? Could be way off of course but its worth a punt

    Even if you had reverse polarity the neon would not light, then again i could be wrong as im only an alleged non electrician.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Many thanks to all for continuing interest.
    Just to clarify the boiler operates and the neon light remains on regardless of the position of the slider switch. ie when switch is off boiler is firing and neon light is on.

    Also appreciate comments on the following:
    Wondering if I can just use the boiler for rad the heating and work the hot water off the immersion heater. If I close down the h/w cylinder circuit using the manual valve at the cylinder and then disconnect the motor valve from the power supply and leave it open. The boiler then would be used to supply only the rads. Would this eliminate the motor valve and the induced current apparent issues ?
    Does this make sense ?


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    There are no 'induced currents'. Your new timer is broken - replace it and use a decent one this time.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    makfli wrote: »
    Many thanks to all for continuing interest.
    Just to clarify the boiler operates and the neon light remains on regardless of the position of the slider switch. ie when switch is off boiler is firing and neon light is on.

    Also appreciate comments on the following:
    Wondering if I can just use the boiler for rad the heating and work the hot water off the immersion heater. If I close down the h/w cylinder circuit using the manual valve at the cylinder and then disconnect the motor valve from the power supply and leave it open. The boiler then would be used to supply only the rads. Would this eliminate the motor valve and the induced current apparent issues ?
    Does this make sense ?
    It doesnt make sense.Also an immersion is more expensive than oil to heat water.If it we re me id be fitting this time clock
    http://www.pjmatthews.ie/products/flash-31031-single-channel-timeclock-1 ,or a more expensive digital clock with a boost button


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    I have a Siemens RWB27 controller which was replaced in my mothers house. I think this is working ok. Before going to the expense of getting a new one installed and finding that it is not a timer problem, I would like to try this out. The connections are 4 3 2 1 L N. Could anyone advise how I sub this for the Immermat switch ?
    Many thanks again for all the interest.


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Post up picture of the timer and its connections.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Thanks Kevin will do. I wont be back home until the week end and I don't have a broadband connection so will be Tuesday before I get the pic up. From memory there are two twin cables thus 2 brown and 2 blue.


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Isolate the power, open timer, identify live out and disconnect it from the timer, power back up, boiler should now be off unless you have some other backwards wiring in your installation.


  • Registered Users, Registered Users 2 Posts: 81 ✭✭skippy5


    Have you a frost stat on your boiler. Could be faulty.


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Even if you had reverse polarity the neon would not light, then again i could be wrong as im only an alleged non electrician.

    Theres every chance a neon could light with reverse polarity. Ive seen it on boilers, spur switches and believe it or not , time clocks . But as the boiler is firing then its ruled out anyway.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    skippy5 wrote: »
    Have you a frost stat on your boiler. Could be faulty.

    Yes, this is just what I was gonna say


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Egass13 wrote: »
    Theres every chance a neon could light with reverse polarity. Ive seen it on boilers, spur switches and believe it or not , time clocks . But as the boiler is firing then its ruled out anyway.

    Im not disputing a neon lighting with reverse polarity, its the reverse polarity sending a bit of voltage down the neutral to power the neon bit that is not possible, the induced current theory is more plausible.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Im not disputing a neon lighting with reverse polarity, its the reverse polarity sending a bit of voltage down the neutral to power the neon bit that is not possible, the induced current theory is more plausible.

    Why isnt it possible?


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Egass13 wrote: »
    Why isnt it possible?

    A neon will light no matter how its connected, same as wiring a simple pendant drop, the bulb will still light.
    Are you on about if the clock is wired backwards and that the neutral of the clock will be now live that the neon stills light when the clock is off?


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    A neon will light no matter how its connected, same as wiring a simple pendant drop, the bulb will still light.
    Are you on about if the clock is wired backwards and that the neutral of the clock will be now live that the neon stills light when the clock is off?

    Not necessarily the clock. You could have a plug on an appliance wired incorrectly and when plugged in could cause reverse polarity on the circuit . and providing the timeclock is wired off the socket circut , could impact on the timeclock. Im confused when you say reverse polarity could cause it , but power on the neutral isnt possible. When my understanding of reverse polarity is just that, when the neutral becomes live ?


  • Banned (with Prison Access) Posts: 1,797 ✭✭✭Kevin McCloud


    Egass13 wrote: »
    When my understanding of reverse polarity is just that, when the neutral becomes live ?

    And the live becomes neutral, neon lights im in agreement with you as i said earlier. Or is it something else?

    If the clock was wired reverse polarity the problem of the neon lighting would be there from day 1 based on your suggestion.


  • Registered Users, Registered Users 2 Posts: 157 ✭✭makfli


    Once again thanks to everyone for the interest. I think firstly I will replace the timeswitch. I have a Siemens RWB27 digital switch which I will try. Connections are :
    IMAG0233.jpg

    The Immermat switch has connections, from the left
    Brown= L in, Blue = N in, Blue = N out, Brown= L out:
    IMAG0226.jpg

    Appreciate advice on how to wire up the Siemens switch.

    Also I found the motor valve which is a Sunvic there is no lever on this as nmacc suggested that I check for free movement:
    IMAG0232.jpg


    Many thanks again for any help