Bathroom fan

  • 20-03-2015 10:20am
    #1
    Registered Users, Registered Users 2 Posts: 108 ✭✭


    Hi all sparkies, a question for you. I've just installed a a ceiling fan in my shower room and I've wired it from the switched live in the ceiling rose, is this Ok ???.


Comments

  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    It will be OK as long as the installation work complies with ET 101:2008 as amended to 2011 and functions the way that you intend.


  • Registered Users, Registered Users 2 Posts: 108 ✭✭sjfoley


    I suppose what I should have asked is, do I need to put a fuse between the connection in the ceiling rose, and the fan ,


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    The manufacturers' instructions for many fans will stipulate that a 3A BS 1362 (IS number?) fuse should be used - however this would have to be arranged so as to protect both the permanent and switched phase conductors. Generally this would be achieved by feeding the bathroom luminaire from a fused connection unit.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,655 Mod ✭✭✭✭2011


    @ sjfoley

    Traditionally water and electricity are a bad mix. As a consequence of this the electrical regulations are very strict. In Ireland the the applicable regulations are "The National Rules for Electrical Installations fourth edition ET101:2008". Within this you will find that bathrooms containing a shower or bath a split into different zones. Different types of electrical equipment may be installed in different zones. To determine what is and is not allowed will be determined by several factors. For this reason it is difficult to answer the questions that you have asked.

    If you can answer the questions below it would help.

    What is the IP rating of the fan?

    From this diagram can you determine what zone your fan and light (with the ceiling rose) is in?

    Have you installed a suitable fan isolator? If so where is it?

    Does the fan have a timer?