Vokera Boiler Bubbling

  • 15-02-2015 11:37am
    #1
    Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭


    Hi All

    Quick question, I have Vokera Mynute 25A

    This morning its starting bubbling like a kettle when the water is boiling.

    Am gonna call Vokera in the morning

    is it ok to still use it ? pressure is showing 1.5bar

    Its still fecking cold and need to heat the house

    Thanks

    DT

    The narrower a man’s mind, the broader his statements.



Comments

  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Hi All

    Quick question, I have Vokera Mynute 25A

    This morning its starting bubbling like a kettle when the water is boiling.

    Am gonna call Vokera in the morning

    is it ok to still use it ? pressure is showing 1.5bar

    Its still fecking cold and need to heat the house

    Thanks

    DT

    Sounds like condensate is blocked . If you can trace it to point of termination and see if you can see anything obvious first , obviously I can't give you any direction to within the boiler . It's an expensive call to Vokera if it's just a blocked drain. Had one last week that was blocked with leaves at the shore


  • Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭Deep Thought


    Egass13 wrote: »
    Sounds like condensate is blocked . If you can trace it to point of termination and see if you can see anything obvious first , obviously I can't give you any direction to within the boiler . It's an expensive call to Vokera if it's just a blocked drain. Had one last week that was blocked with leaves at the shore

    Out outlet is about 7 foot off the ground.

    It sounds like air bubbling in the boiler.

    I am wondering if its ok to use, as it seems to still heat the rads even though its making a racket.

    The narrower a man’s mind, the broader his statements.



  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Out outlet is about 7 foot off the ground.

    It sounds like air bubbling in the boiler.

    I am wondering if its ok to use, as it seems to still heat the rads even though its making a racket.

    Your condense pipe is a 22mm plastic pipe , it should be going to a drain , I'd say your looking at the flue if it's 7ft off the ground .
    If it's bubbling , and you have 1.5bar , and assuming you have vented rads , it's going to be most likely a blocked condensate and not air in the system , could also be kettling from a dirty system . But my money is on condensate . Have you a pic of pipes under boiler ?


  • Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭Deep Thought


    Egass13 wrote: »
    Your condense pipe is a 22mm plastic pipe , it should be going to a drain , I'd say your looking at the flue if it's 7ft off the ground .
    If it's bubbling , and you have 1.5bar , and assuming you have vented rads , it's going to be most likely a blocked condensate and not air in the system , could also be kettling from a dirty system . But my money is on condensate . Have you a pic of pipes under boiler ?

    sorry ...was at work..

    pic, i did go outside and saw a 22mm white pipe going to the ground, i checked it and its ok, would there be a problem further up beneath the unit itself ?

    IMG_0173_zpsd3to4syl.jpg

    The narrower a man’s mind, the broader his statements.



  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    sorry ...was at work..

    pic
    IMG_0173_zpsd3to4syl.jpg

    If the condensate was blocked would it not back up into the heat exchanger?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭Deep Thought


    Dtp1979 wrote: »
    If the condensate was blocked would it not back up into the heat exchanger?

    and as you mentioned...prob new Heat Exchanger if this is the case ?

    The narrower a man’s mind, the broader his statements.



  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Dtp1979 wrote: »
    If the condensate was blocked would it not back up into the heat exchanger?

    It's a down firing burner, it would back up and fill the sump below the heat exchanger and the fan will be blowing down into it , creating the bubbling sound . I wouldn't call Vokera , €230 odd , to fix something that could be done during a routine service .


  • Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭Deep Thought


    Egass13 wrote: »
    It's a down firing burner, it would back up and fill the sump below the heat exchanger and the fan will be blowing down into it , creating the bubbling sound . I wouldn't call Vokera , €230 odd , to fix something that could be done during a routine service .

    The boiler is still under warranty, so thats why was going to call them, maybe better to get local RGI bloke in.?

    The narrower a man’s mind, the broader his statements.



  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    The boiler is still under warranty, so thats why was going to call them, maybe better to get local RGI bloke in.?

    Ah well if it's under warranty then fair enough , get them out. . But it dsnt sound like a manufacturing fault so I don't know how it works with charges etc. best say it to them on the phone.


  • Registered Users, Registered Users 2 Posts: 4,564 ✭✭✭Deep Thought


    Egass13 wrote: »
    Ah well if it's under warranty then fair enough , get them out. . But it dsnt sound like a manufacturing fault so I don't know how it works with charges etc. best say it to them on the phone.

    yeah, thats what I was thinking, will see what they say and then prob call local chap.

    Thanks for all the help and advice

    DT

    The narrower a man’s mind, the broader his statements.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1 Itsmeinnit


    Cheers alot. I googled volkera boiler bubbling and found this thread.
    Found the 22mm pipe and flicked and wobbled it around a bit and heard water run down and out. Tried boiler and the noise stopped boiler all good again.

    Lee


  • Registered Users, Registered Users 2 Posts: 10 abc2000


    MOD NOTE:
    Deleting this post as it discussed restricted works on a gas boiler.

    This is a public forum and some sorts of advice is deemed dangerous in the wrong hands.

    No infraction issued ABC. I know you were trying to be helpful.


  • Registered Users, Registered Users 2 Posts: 10 abc2000


    Hello,
    Just wanted to say thank you to the forum users that gave me an idea how to find and fix this common problem.
    Any way follow the logic :pipes- water - blockage and you will eventually find the problem.
    And of course -Always cut power to boiler .
    Thanks


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    abc2000 wrote: »
    Hello,
    Just wanted to say thank you to the forum users that gave me an idea how to find and fix this common problem.
    Any way follow the logic :pipes- water - blockage and you will eventually find the problem.
    And of course -Always cut power to boiler .
    Thanks

    AND stay within the law concerning working on gas boilers. You could end up a lot worse off than Daniel O’Donnell :(