boiler refill issue.

  • 02-02-2015 8:16pm
    #1
    Registered Users, Registered Users 2 Posts: 388 ✭✭


    Hey guys gas boilers at .5 bar. Ive the refill open and ive checked both the turn valve and one way valve both are working. I manually vented some of the pressure from the boiler and it just rose back to .5 and stopped there. Any ideas on where i need to look next?


Comments

  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    Rob32 wrote: »
    Hey guys gas boilers at .5 bar. Ive the refill open and ive checked both the turn valve and one way valve both are working. I manually vented some of the pressure from the boiler and it just rose back to .5 and stopped there. Any ideas on where i need to look next?

    Was the pressure higher before.
    What boiler
    Most boilers will happily work at 0.5 bar


  • Registered Users, Registered Users 2 Posts: 388 ✭✭Rob32


    Robbie.G wrote: »
    Was the pressure higher before.
    What boiler
    Most boilers will happily work at 0.5 bar

    Yes it was before i began bleeding the system. Was at 1bar with the boiler cold. And ive no idea what type i cant find any name or model number on it