plumbing problems

  • 12-01-2015 4:07pm
    #1
    Registered Users, Registered Users 2 Posts: 3


    Looking for some advice. I build my house in 2008 its around 3100 sq feet. The contractor put in a baxi he 25 combi boiler to run the underfloor heating through out the house. It has never really worked properly and really struggles when its cold. I have had two plumbers look at the system, one is advising that I need a bigger boiler 30kw and the other wants to increase the pipe size from the boiler to the manifold from 3/4 inch to 1 inch and put a header in, so the boiler feeds it not the manifold. Any comments grateful


Comments

  • Registered Users, Registered Users 2 Posts: 6,033 ✭✭✭Slippin Jimmy


    You will probably get a better reply in the heating and plumbing forum.


  • Registered Users, Registered Users 2 Posts: 7,786 ✭✭✭slimjimmc


    Moved to Plumbing & Heating.


  • Registered Users, Registered Users 2 Posts: 12,822 ✭✭✭✭galwaytt


    pkd09 wrote: »
    Looking for some advice. I build my house in 2008 its around 3100 sq feet. The contractor put in a baxi he 25 combi boiler to run the underfloor heating through out the house. It has never really worked properly and really struggles when its cold. I have had two plumbers look at the system, one is advising that I need a bigger boiler 30kw and the other wants to increase the pipe size from the boiler to the manifold from 3/4 inch to 1 inch and put a header in, so the boiler feeds it not the manifold. Any comments grateful

    [sigh]..sounds like my house !

    Seriously, only for my boiler is currently AWOL, my UFH has worked off a 30kW boiler - but the boiler is not feeding the manifolds directly.

    I have a buffer tank that the UFH draws to it's manifolds from, and the boiler is on a very short leg to the buffer. I think this is better, from a boiler-cycling perspective.

    My point being I think a boiler connected directly to an UFH manifold is not the best solution imho - and this is something I had in my previous house.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users, Registered Users 2 Posts: 3 pkd09


    galwaytt wrote: »
    [sigh]..sounds like my house !

    Seriously, only for my boiler is currently AWOL, my UFH has worked off a 30kW boiler - but the boiler is not feeding the manifolds directly.

    I have a buffer tank that the UFH draws to it's manifolds from, and the boiler is on a very short leg to the buffer. I think this is better, from a boiler-cycling perspective

    My point being I think a boiler connected directly to an UFH manifold is not the best solution imho - and this is something I had in my previous house.

    thanks for that,boiler awol makes two of us.mine is airlocked in the top of the house.dont know much about boilers but i keep being told mine is for a 3 bed house


  • Registered Users, Registered Users 2 Posts: 225 ✭✭froshtyv


    pkd09 wrote: »
    Looking for some advice. I build my house in 2008 its around 3100 sq feet. The contractor put in a baxi he 25 combi boiler to run the underfloor heating through out the house. It has never really worked properly and really struggles when its cold. I have had two plumbers look at the system, one is advising that I need a bigger boiler 30kw and the other wants to increase the pipe size from the boiler to the manifold from 3/4 inch to 1 inch and put a header in, so the boiler feeds it not the manifold. Any comments grateful

    You can probably be sure that the mechanical side of the system is not correct.
    What i mean by this is that when connecting the underfloor heating to the boiler, there is no by-pass valve or header arrangement used. When the mixing valve on the ufh starts to close, the boiler pump has no where to circulate to and will try to force the mixing valve open.
    A simple solution is to install a by-pass valve or header between the boiler and underfloor heating pump and mixing valve.
    A bigger boiler will not solve your current issue.
    What type of pipes were used to feed your ufh manifolds? Copper or multilayer?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3 pkd09


    Thanks for the advise. Since posting i have contacted manufacturer and they gave same advice. So will be getting plumber to put in a header and a weather compensating valve. Fingers crossed. In relation to the pipes,the plumber used copper.


  • Registered Users, Registered Users 2 Posts: 28 jack_t


    Hi pkd09,

    could you advise which weather compensating valve and controller you're installing? I am planning to install it for my system before next winter.


  • Registered Users, Registered Users 2 Posts: 9,815 ✭✭✭antoinolachtnai


    I don't know much about it really, but would turning the boiler down low solve this problem? You would obviously need to leave to leave the boiler running longer to get the same amount of heat output, but that's no big deal.


  • Registered Users, Registered Users 2 Posts: 225 ✭✭froshtyv


    I don't know much about it really, but would turning the boiler down low solve this problem? You would obviously need to leave to leave the boiler running longer to get the same amount of heat output, but that's no big deal.

    Your boiler is designed to work at high temperatures to achieve its best efficiency so by turning its flow temperature down you will end up using more oil in the long run.
    A mechanical mixing valve would be the easiest solution, but i assume there is one fitted on your UFH already?


  • Registered Users, Registered Users 2 Posts: 225 ✭✭froshtyv


    pkd09 wrote: »
    Thanks for the advise. Since posting i have contacted manufacturer and they gave same advice. So will be getting plumber to put in a header and a weather compensating valve. Fingers crossed. In relation to the pipes,the plumber used copper.

    Depending on the length of run, you generally get enough flow using 3/4" copper.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 9,815 ✭✭✭antoinolachtnai


    froshtyv wrote: »
    Your boiler is designed to work at high temperatures to achieve its best efficiency so by turning its flow temperature down you will end up using more oil in the long run.
    A mechanical mixing valve would be the easiest solution, but i assume there is one fitted on your UFH already?

    It's a condensing gas boiler, no? These are by and large designed to run at their greatest efficiency at lower temperatures. Obviously the differential is very important too.

    http://www.cleaver-brooks.com/About-Us/News/Articles/2013/Operating-A-Hydronic-Boiler.aspx


  • Registered Users, Registered Users 2 Posts: 225 ✭✭froshtyv


    It's a condensing gas boiler, no? These are by and large designed to run at their greatest efficiency at lower temperatures. Obviously the differential is very important too.

    http://www.cleaver-brooks.com/About-Us/News/Articles/2013/Operating-A-Hydronic-Boiler.aspx

    My mistake, i was referring to an oil boiler.
    A gas boiler is a different story when it comes to modulating.
    This needs to be setup correctly though, along with the mechanical setup of the system.
    Depending on the pump in the gas boiler there could be case where you wouldnt need an additional pump for the UFH or a mixing valve if the flow temperature can be controlled correctly.


  • Registered Users, Registered Users 2 Posts: 9,815 ✭✭✭antoinolachtnai


    I just mention it because turning down the temp and running the heating for a longer period might solve the OP's immediate problem for the short term. It probably isn't a fantastic solution, but it might help.