Power in the attic

  • 06-01-2015 8:12pm
    #1
    Registered Users, Registered Users 2 Posts: 1,094 ✭✭✭


    Mounted a TV on the bedroom wall and I want to hide the cables. Therefore I would like to power it from the attic.
    I can see the cables in the attic running to the bedroom ceiling lights.

    Would it be okay to simply cut one of those cables rejoin it through a new plug socket?
    Will I be safe to cut it if I turn off the power at the fuse box?
    Will it be good to power a tv and a sky box and not affect the light?

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 1,217 ✭✭✭moonshadow


    Please get an electrician ASAP .


  • Registered Users, Registered Users 2 Posts: 563 ✭✭✭robclay26


    BraveDonut wrote: »
    Mounted a TV on the bedroom wall and I want to hide the cables. Therefore I would like to power it from the attic.
    I can see the cables in the attic running to the bedroom ceiling lights.

    Would it be okay to simply cut one of those cables rejoin it through a new plug socket?
    Will I be safe to cut it if I turn off the power at the fuse box?
    Will it be good to power a tv and a sky box and not affect the light?

    Thanks

    Get electrician, as the other guy said. Most of the cable in light circuits is 1.5mm twin and earth, sockets for bedrooms (light loads) is normally 2.5mm twin and earth. Lighting cable it too light.


  • Registered Users, Registered Users 2 Posts: 1,094 ✭✭✭BraveDonut


    Thanks both - you answered my question - don't do it myself! :)


  • Registered Users, Registered Users 2 Posts: 2,880 ✭✭✭2012paddy2012


    if you get a fused spur (elec shop will tell ya 13 Amp?) ,turn off elec - cut into a 2,5 [EMAIL="T@E"]T@E[/EMAIL] , wire..... in attic... wire ...... in an extension lead (fused)
    will be grand.. turn on the ELCB , at board first , then plug in a lamp.

    test the extension lead , ensure lamp goes out, then switch off elcb ensure lamp goes out , write note on elcb , that ext lead wired in...will be grand.


    generally you cant go1.5 lights to 2.5 sockets , load too heavy..you can go 2.5 to1.5.......presume you have some diy exp.

    every shed in the country has similar set up!!! as well as most attics


  • Registered Users, Registered Users 2 Posts: 1,094 ✭✭✭BraveDonut


    I am going to assume that the attic does not have any 2.5 (modern semi-d) and engage an electrician to do this.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 9,605 ✭✭✭gctest50


    if you get a fused spur (elec shop will tell ya 13 Amp?) ,turn off elec - cut into a 2,5 T@E , wire..... in attic... wire ...... in an extension lead (fused)
    will be grand.. turn on the ELCB , at board first , then plug in a lamp.

    test the extension lead , ensure lamp goes out, then switch off elcb ensure lamp goes out , write note on elcb , that ext lead wired in...will be grand.


    generally you cant go1.5 lights to 2.5 sockets , load too heavy..you can go 2.5 to1.5.......presume you have some diy exp.

    every shed in the country has similar set up!!! as well as most attics


    DON'T do this - the breaker is sized to protect the weakest link