HKC SABB not sounding

  • 13-12-2014 5:52pm
    #1
    Registered Users, Registered Users 2 Posts: 61 ✭✭


    Hi all,

    I'm hoping someone can help me.I have just installed a HKC SW-1070 alarm. At the minute I have only 4 wired PIR zones. The problem I am having is that when the alarm sounds the siren on the SABB doesn't sound. The internal siren does sound when the alarm is triggered.

    The way I have it wired is as follows:

    - External Bell +- on the SABB goes to External Bell +- on the panel
    - SAB Hold (BHO) on SABB goes to SABB Hold on the panel
    - The tamper goes back to the panel but I twisted it with one of the tamper cores
    from the internal siren and the other internal siren tamper core goes into the tamper return on the panel
    - STROBE +- on the SABB goes to the Internal Bell +- on the panel along with the Internal siren +-

    Any help would be greatly appreciated.

    Thanks guys.
    Tagged:


Comments

  • Registered Users, Registered Users 2 Posts: 6,562 ✭✭✭kub


    Have you anything connected to EXT Bell - ?


  • Registered Users, Registered Users 2 Posts: 61 ✭✭rustalan


    Hi, yes EXT bel on the SABB both + & - are going to EXT bell in the panel.


  • Registered Users, Registered Users 2 Posts: 6,562 ✭✭✭kub


    How did you test it?


  • Registered Users, Registered Users 2 Posts: 61 ✭✭rustalan


    Just set the alarm off on a full set by walk past a PIR. The Blue LED's are flashing, its just the siren didn't sound.


  • Registered Users, Registered Users 2 Posts: 855 ✭✭✭Evolution1


    Try 0#9
    Are the white leds flashing side to side on the bell?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 61 ✭✭rustalan


    Hi, thanks for the replies. Yes both the internal and external siren went off when I did 0#9. I triggered the alarm and waited longer this time and after 15-20 seconds the external siren sounded. I didn't realise that there was a delay on it. Seems to be working fine now. Thanks for the help.


  • Registered Users, Registered Users 2 Posts: 6,562 ✭✭✭kub


    It all depends on how the zone which you activated was programmed.
    Also I find in most cases as well that the testing procedure is flawed and as a result an exit fault alarm is what occurs and in this situation the external sounder does not sound.


  • Registered Users, Registered Users 2 Posts: 61 ✭✭rustalan


    Thanks Kub. I see, I probably should have set the alarm and went outside and came back in after it armed rather than jumping around like a clown trying to set it off from the inside :)