Flue Very Hot- Firebird

  • 07-11-2014 2:09pm
    #1
    Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭


    I have a Firebird Super 90 with a Riello burner. It is in the utility room and I notice that the area around the flue is quite hot. There is some cracking in the plaster. The thermostat is set at 70 degrees.
    It is due the annual service and I am wondering is there something I can get done inside the boiler to reduce heat loss to the flue? Is there some internal insulation which could be redone etc. ?


Comments

  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    when you get your boiler serviced is it set up correctly using a flugas analyser

    baffle condition wrong nozzle fuel pump pressure non obstructed flue can all have a bearing on the flugas temp

    the fact you have the stat set to 70 would really only reflect on the water temp

    if you have a flugas analyser printout from the last service have a look at what the flue temp was

    personally I find older fb boilers can have high flugas temp without any obvious reason


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks jimf for your reply.
    Here are the temps from last service:

    Flue : 126 C
    Inlet: 12.6 C
    Nett: 113.4 C

    How do they look ?

    Thanks


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Cerco wrote: »
    Thanks jimf for your reply.
    Here are the temps from last service:

    Flue : 126 C
    Inlet: 12.6 C
    Nett: 113.4 C

    How do they look ?

    Thanks

    if im honest with you I would have to say your boiler was set up long before it was anyway near its operating temp

    usually you would be expecting the above temp to be around 220/240


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Should I run the boiler for a couple of hours before the engineer calls or would that make it awkward for him?


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    no need to run it before service guy arrives

    running up to the operating temp is something you have to be prepared to do this is 1 of the reasons a boiler service done properly should be taking in the region of 90 mins to complete


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks jimf , that's great information. I know a little more now.

    Thanks again,
    Cerco


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    if im honest with you I would have to say your boiler was set up long before it was anyway near its operating temp

    usually you would be expecting the above temp to be around 220/240

    Or under fired, under sized boiler, contaminated sample or sample taken too far away from heat source.

    Op What was O2 readings on that sample? Do you know how long the boiler was running for when sampled?

    Anyway your flue should be capable of handling any normal high temperature IF sealed and installed properly.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks Wearb.
    The O2 reading is % 7.7
    CO2 : 9.8
    CO2 pps: 22

    I don't know how long it was running before samples taken.

    Thanks.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Wearb wrote: »
    Or under fired, under sized boiler, contaminated sample or sample taken too far away from heat source.

    Op What was O2 readings on that sample? Do you know how long the boiler was running for when sampled?

    Anyway your flue should be capable of handling any normal high temperature IF sealed and installed properly.


    good points as well wearb


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Cerco wrote: »
    Thanks Wearb.
    The O2 reading is % 7.7
    CO2 : 9.8
    CO2 pps: 22

    I don't know how long it was running before samples taken.

    Thanks.

    Not a very good setup. It may have been caused by a poor sample. But it could be lots of other things also. Service person needs to work out why he is not able to improve on those results.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    good points as well wearb

    Yes good points, but if I were to bet on it I would bet that your explanation is mostly the correct one.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks Wears and jimf. I have a contact for an engineer , who is recommended, so I will get him to service it.
    I thought it might have been heat loss in the boiler but now I know that is not the issue

    Thanks again.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Wearb wrote: »
    Not a very good setup. It may have been caused by a poor sample. But it could be lots of other things also. Service person needs to work out why he is not able to improve on those results.


    it could be one of the i have fga but i haven't a clue how to use it brigade as well :rolleyes::rolleyes:


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Cerco wrote: »
    I thought it might have been heat loss in the boiler but now I know that is not the issue

    Thanks again.

    Well with the information given here, you cannot say that for certain either.

    Perhaps you will let us know what your new service guy says about it.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    it could be one of the i have fga but i haven't a clue how to use it brigade as well :rolleyes::rolleyes:

    I have come across them. They service the way they did years ago. Then stick in the analyser and print off the results.

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Cerco wrote: »
    Thanks Wearb.
    The O2 reading is % 7.7
    CO2 : 9.8
    CO2 pps: 22

    I don't know how long it was running before samples taken.

    Thanks.
    What is the ratio figure on your printout?, You should see see three zeros after the decimal point,
    Your last service guy didnt know how to set up the boiler with the analyser,your boiler is over aired which is blowing the flame out the flue too fast which would make the flue hotter than it should be.
    What your looking for from next service guy
    A/ oil pressure set to manufacturers instructions
    B/nozzle as per manufacturers instructions for the output required
    C/ 02- between 3-6
    D/ Co2 between 11.2-12 [check manual for exact]
    E/Flue temp 190-240 [check manual for exact]
    f/Ratio-three zeros after the decimal point
    g/ Co- as low as possible
    d/X Air % 33 to 37 approx


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks Agusta.
    The CO/CO2 is 0.0002
    Other readings are:

    EFF (N). 94.1
    Losses: 5.9
    XAir % : 58.3

    O2%. 7.7
    CO2% 9.8
    CO pp 22
    PRS ?bar -2.04

    Thanks for the guide readings. Useful reference.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Cerco wrote: »
    Thanks Agusta.
    The CO/CO2 is 0.0002
    Other readings are:

    EFF (N). 94.1
    Losses: 5.9
    XAir % : 58.3

    O2%. 7.7
    CO2% 9.8
    CO pp 22
    PRS ?bar -2.04

    Thanks for the guide readings. Useful reference.


    the more info you post cerco the more convinced i am who ever did
    your boiler the last time hadn't a clue :(


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    It was first time I used him, jimf. He was baffled by the tiger loop so I was a bit suspicious. Anyway I thought he could do the boiler itself and I was impressed when he drilled a hole and fitted a screw to measure the gases in the outlet.

    I have learned a lot today and glad I asked the questions. Thanks for all the replies.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Cerco wrote: »
    It was first time I used him, jimf. He was baffled by the tiger loop so I was a bit suspicious. Anyway I thought he could do the boiler itself and I was impressed when he drilled a hole and fitted a screw to measure the gases in the outlet.

    I have learned a lot today and glad I asked the questions. Thanks for all the replies.

    Did he highlight any problems on the service report?

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    There was no service report, just the ticket from the analyser.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    your boiler is grossly overaired at 58% xa if this was brought down to in or around 35% xa it might bring the rest of the settings into more acceptable parameters then i would like to see what your fg temp would be reading once the boiler is up to operating temp


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    Thanks jimf for all your replies.