Ferroli Oil Boiler

  • 30-09-2014 9:21pm
    #1
    Registered Users, Registered Users 2 Posts: 81 ✭✭


    Hi lads,
    Was doing a service on a cast iron ferroli boiler fitted with an riello 40 g5 burner today.

    max output - 64
    min output - 44
    Nozzle fitted 0.75 S 80deg
    pump pressure 14 bar.(gas oil)

    I know this set up dosnt quite give you the min output , but has being set up like this for 10 years or more.
    My problem is I cant get the co2 % over 10.20.

    02% - 7.2
    c0 ppm - 118
    C02%- 10.2
    Ratio- 0.0012
    pressure- 0.26
    temp net- 122
    temp flue- 151
    eff gross%- 87.4
    xs air%- 52.7

    Maybe someone with a bit more experience than me could point me in the right direction to improving these readings.
    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    skippy5 wrote: »
    Hi lads,
    Was doing a service on a cast iron ferroli boiler fitted with an riello 40 g5 burner today.

    max output - 64
    min output - 44
    Nozzle fitted 0.75 S 80deg
    pump pressure 14 bar.(gas oil)

    I know this set up dosnt quite give you the min output , but has being set up like this for 10 years or more.
    My problem is I cant get the co2 % over 10.20.

    02% - 7.2
    c0 ppm - 118
    C02%- 10.2
    Ratio- 0.0012
    pressure- 0.26
    temp net- 122
    temp flue- 151
    eff gross%- 87.4
    xs air%- 52.7

    Maybe someone with a bit more experience than me could point me in the right direction to improving these readings.
    Thanks

    Turn the air down till O2 is 5-6 percent


  • Registered Users, Registered Users 2 Posts: 81 ✭✭skippy5


    Hi Dtp,
    Tried this and it just sent the C0 way up and C02% down even more.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    skippy5 wrote: »
    Hi Dtp,
    Tried this and it just sent the C0 way up and C02% down even more.

    How is your smoke test at those readings?

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Been giving this some more thought. You should have higher co2 readings with those 02 readings. I would check the integrity of your FGA sample. Is there a chance that there is air getting in after the combustion chamber and before your sample point.
    Where are you taking the sample from?

    I would also do a complete check of the flue way for even the slightest blockage.

    Have you chosen correct fuel on your analyser?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    are you sure this is the original burner/nozzle combination

    seems grossly overaired as it is at 53% e air

    this would explain the high co as well

    it wouldn't surprise me if this is not the original burner

    just try a .60/65 nozzle and see hot it effects things

    sorry just read your post again ignore my comment re trying a smaller nozzle didn't see the output range half asleep


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Oil pressure is too high swell, 12bar.

    Which Ferroli is it, GN 1 or 2?

    If boiler output range is 44-64kw, then your nozzle is also undersized (150k-220k BTU with a .75 nozzle??)


  • Registered Users, Registered Users 2 Posts: 257 ✭✭kscobie


    I would change the nozzle, sometimes a brand new nozzle wont atomise the fuel properly


  • Registered Users, Registered Users 2 Posts: 1,775 ✭✭✭JamesM


    I'm retired over a year now and it is amazing how quickly you forget things when you are not dealing with them every day :eek: But, I do remember that a G5 was almost impossible to get right with gas oil. It's meant to run on kerosene. The head that is usually fitted is just not suitable for gas oil.


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Always was techy, very straight tube IMHO, but have run them on ClassD many times


  • Registered Users, Registered Users 2 Posts: 81 ✭✭skippy5


    Hi Lads.
    Thanks for all the replies.
    Just to answer some of your question.
    - sample taken 500mm above flue center (twin walled flue)
    - the model is GN1 N 05
    - flue ways are good and clean
    - nozzle is small. I will change that
    - had pump at 12 bar and the readings were worse
    - heading back there on friday to try get my head around it


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    skippy5 wrote: »
    Hi Lads.
    Thanks for all the replies.
    Just to answer some of your question.
    - sample taken 500mm above flue center (twin walled flue)
    - the model is GN1 N 05
    - flue ways are good and clean
    - nozzle is small. I will change that
    - had pump at 12 bar and the readings were worse
    - heading back there on friday to try get my head around it

    If you are sure that your flue sample is good and no air leaks, then see how you get on with a 1.0 or even a little larger nozzle at 12 bar. If still a problem then try 60 degree nozzle and see if that improves it. After that (as Jim suggested) it may be an incompatable burner or burner head. I have no idea what originally came with them.

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Play around with burner head adjustments and nozzles.
    It will take time but you will add to your future knowledge.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    1.00 US/gal at 12 bar will give you an output of 45kw approx. id be trying the 60 degree nozzle first


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    how u get on with this yesterday


  • Registered Users, Registered Users 2 Posts: 81 ✭✭skippy5


    Hi Lads,
    Only got back back to this on Friday as they ran out of fuel.
    Sorry for delay.

    - Changed nozzle for an 0 .85 60 deg solid at 12 bar
    - Sealed up flue where air was getting in after chamber and before sample point.
    - Results

    - co 43
    - co2% 11.20
    - Ratio 0.0004
    - O2% 5.80
    - xs Air 38.50
    - Flue temp 185
    - Eff 86.0%

    Thanks lads you were fairly on the ball.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    skippy5 wrote: »
    Hi Lads,
    Only got back back to this on Friday as they ran out of fuel.
    Sorry for delay.

    - Changed nozzle for an 0 .85 60 deg solid at 12 bar
    - Sealed up flue where air was getting in after chamber and before sample point.
    - Results

    - co 43
    - co2% 11.20
    - Ratio 0.0004
    - O2% 5.80
    - xs Air 38.50
    - Flue temp 185
    - Eff 86.0%

    Thanks lads you were fairly on the ball.

    Not too bad at all. Were you tempted to try a 1.0 at near 10 bar?

    Please follow site and charter rules. "Resistance is futile"



  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    10 bar would be a little low for Class D, may not get proper atomisation of fuel.

    FGA flue temp a little on the low side, either boiler was not to temperature (FGA completed too early in cycle) or the boiler is under firing as the nozzle is too small


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    DGOBS wrote: »
    10 bar would be a little low for Class D, may not get proper atomisation of fuel.

    FGA flue temp a little on the low side, either boiler was not to temperature (FGA completed too early in cycle) or the boiler is under firing as the nozzle is too small

    Loops! Missed out on the gas oil bit. +1 on under fired. Don't want to turn it into a condensing boiler :(

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 81 ✭✭skippy5


    Would say 1 gal would have being ideal but I was getting better readings with the 0.85 gal.