Veritas r8 plus problem

  • 09-07-2014 3:41pm
    #1
    Registered Users, Registered Users 2 Posts: 42


    Hi,
    When I set my alarm and leave the alarm activates after 30 seconds. When I cancel it the zone 1 light is flashing. Zone 1 is a hall PIR that is set as an entry/exit zone. In a walk through test everything works fine, and I've no tamper light.
    The power light is flashing green when unset on the unit and the control panel. Would a flat battery cause the false alarm?

    Regards

    Denis


Comments

  • Registered Users, Registered Users 2 Posts: 11,855 ✭✭✭✭altor


    nippy wrote: »
    Hi,
    When I set my alarm and leave the alarm activates after 30 seconds. When I cancel it the zone 1 light is flashing. Zone 1 is a hall PIR that is set as an entry/exit zone. In a walk through test everything works fine, and I've no tamper light.
    The power light is flashing green when unset on the unit and the control panel. Would a flat battery cause the false alarm?

    Regards

    Denis

    A low battery can cause false alarms. Have you checked this with the meter?
    If it is the battery it could be pulling down the 12V supply to the PIR.