Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Flushing system before installing oil boiler

  • 16-06-2014 6:37am
    #1
    Closed Accounts Posts: 51 ✭✭


    Before retrofitting an oil boiler I understand that the heating system needs to be flushed (powerflush). Is the powerflush absolutely necessary. Can the system be cleaned/flushed another way? ie fernox cleaner added to heating system and hot and cold flush, then boiler installed and an inhibitor added. Any other way than the expensive powerflush.


Comments

  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    Before retrofitting an oil boiler I understand that the heating system needs to be flushed (powerflush). Is the powerflush absolutely necessary. Can the system be cleaned/flushed another way? ie fernox cleaner added to heating system and hot and cold flush, then boiler installed and an inhibitor added. Any other way than the expensive powerflush.

    Yes there are other ways that are less effective and cheaper. If youre lucky, your system is very clean and one if the less effective ways might do. End of the day a proper powerflush can't be beaten. You get what you pay for.
    Is your boiler an A rated condensing boiler?


  • Closed Accounts Posts: 51 ✭✭Tracyk


    Dtp1979 wrote: »
    Yes there are other ways that are less effective and cheaper. If youre lucky, your system is very clean and one if the less effective ways might do. End of the day a proper powerflush can't be beaten. You get what you pay for.
    Is your boiler an A rated condensing boiler?
    Defo won't be powerflushing the system, anyway house is only bout 5 or 6 years old. There's a standard efficiency boiler installed and I'm goin to retrofit a grant condensing boiler. System water appears clean but I know it's still always hard to tell.

    What is the next best way to flushing/cleaning the system, and what chemicals should I use? And procedure?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    Defo won't be powerflushing the system, anyway house is only bout 5 or 6 years old. There's a standard efficiency boiler installed and I'm goin to retrofit a grant condensing boiler. System water appears clean but I know it's still always hard to tell.

    What is the next best way to flushing/cleaning the system, and what chemicals should I use? And procedure?

    The next best thing would be the old fashioned way of taking off the rads and using a hose. This method is useless in comparison to a proper flush but will help. Use some fernox f5 beforehand. The boiler your fitting needs a clean system to work properly. By cutting corners your gambling with the heat exchanger in it. Probably going to invalidate the warranty too. Are you going to commission the boiler too?


  • Closed Accounts Posts: 51 ✭✭Tracyk


    Dtp1979 wrote: »
    The next best thing would be the old fashioned way of taking off the rads and using a hose. This method is useless in comparison to a proper flush but will help. Use some fernox f5 beforehand. The boiler your fitting needs a clean system to work properly. By cutting corners your gambling with the heat exchanger in it. Probably going to invalidate the warranty too. Are you going to commission the boiler too?
    yes I'll be installing the boiler myself and commissioning the boiler myself, I'm not oftec registered but I am blueflame certified and have all equipment, so I'll be undertaking all the work myself. The problem was that I don't have a powerflush machine so I just wanted to know what was the next best procedure cause I wasn't sure of the best way to tackle it.

    So just to clarify. I need to add Fernox f5 into heating system and let it work it's magic, once thats done drain down system and disconnect all rads and flush each one of them out using garden hose.

    I've heard of this method before alright. As for associated pipework in the heating system really Im pretty much hoping Ferxox f5 has cleaned that to the best of it ability so.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    yes I'll be installing the boiler myself and commissioning the boiler myself, I'm not oftec registered but I am blueflame certified and have all equipment, so I'll be undertaking all the work myself. The problem was that I don't have a powerflush machine so I just wanted to know what was the next best procedure cause I wasn't sure of the best way to tackle it.

    So just to clarify. I need to add Fernox f5 into heating system and let it work it's magic, once thats done drain down system and disconnect all rads and flush each one of them out using garden hose.

    I've heard of this method before alright. As for associated pipework in the heating system really Im pretty much hoping Ferxox f5 has cleaned that to the best of it ability so.
    The best way to tackle it is a proper flush. But you might get lucky the other way.


  • Advertisement
  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Drain system, add Fernox or similar, only 1/4 fill rads. Run system. Flow of water will be maximum across bottom of rads/sludge area.
    Drain and re fill 3 times at end of treatment time.
    Rad trick works well.
    Normally no need to remove rads.
    I've never had to.


  • Closed Accounts Posts: 51 ✭✭Tracyk


    scudo2 wrote: »
    Drain system, add Fernox or similar, only 1/4 fill rads. Run system. Flow of water will be maximum across bottom of rads/sludge area.
    Drain and re fill 3 times at end of treatment time.
    Rad trick works well.
    Normally no need to remove rads.
    I've never had to.
    only problem is it's going to be hard to judge when rads are 1/4 full. Obviously I'll have to to downstairs first (isolate upstairs rads) then vice versa.


  • Posts: 0 [Deleted User]


    A poor mans power flush is like Coitus interruptus;) done by many but you only know if you've got it wrong when there's a puddle of water on the floor:D


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Tracyk wrote: »
    only problem is it's going to be hard to judge when rads are 1/4 full. Obviously I'll have to to downstairs first (isolate upstairs rads) then visa versa.
    Wrong



    Just slightly vent rads, all you need is water/heat in the bottom, you'll feel the heat.

    If self commissioning, which I don't recommend, follow instruction book to the letter. Ask boiler manufactures if its ok,as there's a problem with insurance in my opinion.
    Manufactures info is basic and don't cover everything.


  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭esox28


    When you drain your ch at best the flow of water runs at 8/ltrs/min, a powerflush dumps water at a rate of 90 ltrs/min. need i say more.

    Filling and draining the system 3 times imo waste of time and water.

    Bring rads out side and flush with garden hose as the lads suggested, just don't wet the white carpets.


  • Advertisement
  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    esox28 wrote: »
    When you drain your ch at best the flow of water runs at 8/ltrs/min, a powerflush dumps water at a rate of 90 ltrs/min. need i say more.

    Filling and draining the system 3 times imo waste of time and water.

    Bring rads out side and flush with garden hose as the lads suggested, just don't wet the white carpets.

    Agree on power flushing.
    Disagree on removing rads.
    House only 5-6 years old.
    I'd even question the economic value of replacing boiler as most are a reasonably good design for the last ten years, unless it's undersized.
    I'd sooner go down the zone and control route.
    Draining system 3 times is only a DIY recommendation for him. Not everyone has a power flushing equipment.


  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭esox28


    More than likely oversized, most I've seen anyway. Sure it doesn't make good value changing a 6 year old boiler when its running good and im sure the op has it like a new penny.

    +1 for heating controls
    -1 for draining ch 3 times like a broken pencil there's no point.


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    esox28 wrote: »
    More than likely oversized, most I've seen anyway. Sure it doesn't make good value changing a 6 year old boiler when its running good and im sure the op has it like a new penny.

    +1 for heating controls
    -1 for draining ch 3 times like a broken pencil there's no point.

    Sometimes I've to flush the toilet 3 times.
    All good things come (or go) in 3's !!!

    Sorry
    Can't do a smiley face with this phone.






    ps. No problem with our difference of
    opinions here, see ya.


  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭esox28


    Haha, im going to cork for the hoildays this year...ill bring you down a special wc it has a power-a-flush! Wan flush does plenty!


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    scudo2 wrote: »
    Agree on power flushing.
    Disagree on removing rads.
    House only 5-6 years old.
    I'd even question the economic value of replacing boiler as most are a reasonably good design for the last ten years, unless it's undersized.
    I'd sooner go down the zone and control route.
    Draining system 3 times is only a DIY recommendation for him. Not everyone has a power flushing equipment.

    I've seen houses 1-2 years old with bad sludge


  • Posts: 0 [Deleted User]


    Dtp1979 wrote: »
    I've seen houses 1-2 years old with bad sludge

    6 months for me and a autofiller was involved.


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Dtp1979 wrote: »
    I've seen houses 1-2 years old with bad sludge

    Feck , I'm lucky then, as I've only once had a problem. GB system lying idle for two years, one section blocked SOLID, disconnected downstairs F&R, tried mate with power flush, tried water mains to it 65ps tried compressed air. Nothing passed.Not a drop.
    Lucky middle Rad of three was moved with Q pex under concrete, disconnected it and rodded F&R both ways with hard wire to break up solid sludge. Got lucky. It worked. Then power flushed.
    That's the only one I got caught on, and I replace quite a few every summer.
    But I do cherry pick them.


  • Closed Accounts Posts: 51 ✭✭Tracyk


    But guys what about if ye were replacing a boiler in a very old house (old heating system) ye wouldn't be power flushing that heating system with all the leaks that could spring up. What's sort of flush would ye do in that instance, And how would that affect the warranty of the boiler?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    But guys what about if ye were replacing a boiler in a very old house (old heating system) ye wouldn't be power flushing that heating system with all the leaks that could spring up. What's sort of flush would ye do in that instance, And how would that affect the warranty of the boiler?

    Why wouldn't you flush an old house?
    It's not a high pressure operation


  • Closed Accounts Posts: 51 ✭✭Tracyk


    Dtp1979 wrote: »
    Why wouldn't you flush an old house?
    It's not a high pressure operation

    I've heard that you should not powerflush a very old heating system because the chances are the powerflush will cause leaks.

    Why is this not true? So you can powerflush any heating system of any age?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    I've heard that you should not powerflush a very old heating system because the chances are the powerflush will cause leaks.

    Why is this not true? So you can powerflush any heating system of any age?

    You heard wrong. Yes any age. The only system I'd be concerned by would be a 40 year old GB system.
    Powerflushing does not cause leaks. Once sludge is removed, it may expose a leak that the sludge was covering up.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    What is the life time on gb?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    What is the life time on gb?

    Generally about 30 + yrs but I still see systems today 40+


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    scudo2 wrote: »
    Wrong



    Just slightly vent rads, all you need is water/heat in the bottom, you'll feel the heat.

    If self commissioning, which I don't recommend, follow instruction book to the letter. Ask boiler manufactures if its ok,as there's a problem with insurance in my opinion.
    Manufactures info is basic and don't cover everything.[/QUO
    Tracyk is a blueflame certified technician,In my opinion he can fit and self commission the boiler as he is qualified to do so and still maintain the warranty with the boiler manufacturer


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    agusta wrote: »
    scudo2 wrote: »
    Wrong



    Just slightly vent rads, all you need is water/heat in the bottom, you'll feel the heat.

    If self commissioning, which I don't recommend, follow instruction book to the letter. Ask boiler manufactures if its ok,as there's a problem with insurance in my opinion.
    Manufactures info is basic and don't cover everything.[/QUO
    Tracyk is a blueflame certified technician,In my opinion he can fit and self commission the boiler as he is qualified to do so and still maintain the warranty with the boiler manufacturer

    Only a plumber should be fitting the boiler. Fair enough, if he has an analyser he can commission it.


  • Moderators, Home & Garden Moderators Posts: 6,381 Mod ✭✭✭✭Wearb


    esox28 wrote: »
    Haha, im going to cork for the hoildays this year...ill bring you down a special wc it has a power-a-flush! Wan flush does plenty!

    Local holiday tip...................stay upstream of scudo's house.

    Please follow site and charter rules. "Resistance is futile"



  • Closed Accounts Posts: 51 ✭✭Tracyk


    Dtp1979 wrote: »
    agusta wrote: »

    Only a plumber should be fitting the boiler. Fair enough, if he has an analyser he can commission it.

    Im also a qualified plumber.

    I'll be undertaking all the work as qualified to do so.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Tracyk wrote: »
    Dtp1979 wrote: »

    Im also a qualified plumber.

    I'll be undertaking all the work as qualified to do so.

    If your a qualified plumber then why are you asking us here if it's necessary to flush a system when you surely know it is??


  • Closed Accounts Posts: 51 ✭✭Tracyk


    Dtp1979 wrote: »
    Tracyk wrote: »

    If your a qualified plumber then why are you asking us here if it's necessary to flush a system when you surely know it is??
    Because I don't have powerflushing equipment and I wanted to see what was your opinions on the next best way to flush a system.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    as your going to save on the installation and commissioning of the boiler why not see if any of the lads on here are near to you and you might be able to get a special boards price wink wink for a powerflush


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    Commissioned a Combi oil boiler today for one of the most professional plumbers I know.
    Pressure vessel was flat.
    Sometimes it's good to have a second opinion.




    Photo is work by same plumber on a different job, he's good but not perfect.


  • Closed Accounts Posts: 51 ✭✭Tracyk


    scudo2 wrote: »
    Commissioned a Combi oil boiler today for one of the most professional plumbers I know.
    Pressure vessel was flat.
    Sometimes it's good to have a second opinion.




    Photo is work by same plumber on a different job, he's good but not perfect.
    What training centre did you take that picture :-)


  • Registered Users, Registered Users 2 Posts: 1,019 ✭✭✭anthonyos


    scudo2 wrote: »
    Commissioned a Combi oil boiler today for one of the most professional plumbers I know.
    Pressure vessel was flat.
    Sometimes it's good to have a second opinion.




    Photo is work by same plumber on a different job, he's good but not perfect.

    Ffs it must of taken him a month to do that


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    anthonyos wrote: »
    Ffs it must of taken him a month to do that

    Didn't know who the plumber was when customer called me, but I betted he's 1 of 3 names I could give.
    He was.


    ps. It's in utility room, customer thinks it's an eye sore and wants it boxed in.!!!!


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    scudo2 wrote: »
    Didn't know who the plumber was when customer called me, but I betted he's 1 of 3 names I could give.
    He was.


    ps. It's in utility room, customer thinks it's an eye sore and wants it boxed in.!!!!

    Make sure they paint them white first to make a right sh1te of them


  • Advertisement
Advertisement