Oven and combi oven

  • 08-06-2014 11:24am
    #1
    Registered Users, Registered Users 2 Posts: 30


    Hi Folks,

    I'm getting an oven and separate combi oven installed. (both rated @16A)

    The cable is 10 sq and MCB is 32a - the question is can both units be switched from the existing cooker switch. i.e 2 tails coming out of the 1 switch. Is this ok regulation wise and will both cables fit in the terminals??

    Any help would be great


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    you can connect 2 cooking appliances as long as the loading is ok

    each appliance has to be a maximum 2m from the switch

    you can wire the appliances into an outlet plate or box


  • Registered Users, Registered Users 2 Posts: 30 frostydog


    Thanks Tom.

    Any chance you could send on a link to the outlet plate you would recommend?


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Each appliance isnt being fused correctly, you said each appliance is rated at 16 amps and your mcb is 32amps. The cable has plenty capacity to power the two appliances its the fusing is the problem.


  • Registered Users, Registered Users 2 Posts: 30 frostydog


    What do you recommend Sir Arthur?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    frostydog wrote: »
    What do you recommend Sir Arthur?

    an electrician


  • Advertisement
  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Fuse down that 10 square to suit the loading on one appliance and install a new supply cable for second appliance and fuse it appropriately.


  • Registered Users, Registered Users 2 Posts: 30 frostydog


    So 2 completely separate cable runs MCB and switch for each appliance?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    I think prob 2 16amp circuits

    they're not an oven and hob that would normally double up on the circuit


  • Registered Users, Registered Users 2 Posts: 30 frostydog


    Cheers. So do i need 2 separate switches on the wall. aesthetically wise i was hoping just to have 1


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    if they're not combined on the 1 isolator

    then they need 1 each

    the rules refer to "oven and hob" on 1 isolator


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 30 frostydog


    Ok Cheers thanks for your help