Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Should a new extension be tied to the to the main house?

  • 14-05-2014 9:56am
    #1
    Closed Accounts Posts: 141 ✭✭


    Apologies if this is in the wrong forum. A question arose yesterday on site. One guy says that the extension should be blocked in to the house while another says that the extension should be freestanding. Can some one advise as to which is the correct procedure?


Comments

  • Subscribers Posts: 41,862 ✭✭✭✭sydthebeat


    getaroom wrote: »
    Apologies if this is in the wrong forum. A question arose yesterday on site. One guy says that the extension should be blocked in to the house while another says that the extension should be freestanding. Can some one advise as to which is the correct procedure?

    both are wrong

    Assuming its a block build.. the blockwork should started using "starter rail" systems such as this:
    http://www.ancon.co.uk/products/wall-ties-and-restraint-fixings/wall-starter-systems

    this allows the extension to settle independently of the existing building (which it will do anyway) without 'pulling away' from the original building. I would always specify an expansion joint here too.


  • Moderators, Home & Garden Moderators Posts: 10,143 Mod ✭✭✭✭BryanF


    + 1 with Syd

    if no one has thought/drawn/specified the junction detail from a structural perspective, then what about cold bridging/ insulation continuity..