Nibe glass lined Enamel Vs Joule SAF2304 Stainless Tank

  • 15-02-2014 9:02pm
    #1
    Registered Users, Registered Users 2 Posts: 2,106 ✭✭✭


    I bought this house a few months ago and today the hot water tank started leaking through the wall of the tank . It's a glass lined tank but the sacrificial anode may never have been changed , I don't know. So now I'm looking at options for a replacement . The area I live in has very soft water , so copper is not suitable and my options are glass lined enamel or stainless steel. It will be tied into a solar system and a geothermal heat pump. After a bit of looking I have come up with these 2 options

    NIBE VPAS Glass lined Enamel tank

    http://www.nibe.eu/Domestic-heatingcooling/Storage-tanks/Product-range/NIBE-VPAS/


    Joule Cyclone Heat Pump Cylinder SAF 2304 grade stainless steel

    http://www.joulesolutions.ie/Cyclone_HeatPump_Un_Vented/324



    I'm looking for any advice you may have on which would be the better option.
    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 107 ✭✭Tommyboy08


    I bought this house a few months ago and today the hot water tank started leaking through the wall of the tank . It's a glass lined tank but the sacrificial anode may never have been changed , I don't know. So now I'm looking at options for a replacement . The area I live in has very soft water , so copper is not suitable and my options are glass lined enamel or stainless steel. It will be tied into a solar system and a geothermal heat pump. After a bit of looking I have come up with these 2 options

    NIBE VPAS Glass lined Enamel tank

    http://www.nibe.eu/Domestic-heatingcooling/Storage-tanks/Product-range/NIBE-VPAS/


    Joule Cyclone Heat Pump Cylinder SAF 2304 grade stainless steel

    http://www.joulesolutions.ie/Cyclone_HeatPump_Un_Vented/324



    I'm looking for any advice you may have on which would be the better option.
    Thanks

    What size is your heat pump
    The size of your heat pump will be relevant to its performance if you go with the joule tank as the coil size in the tank may not be large enough for your heat pump


  • Registered Users, Registered Users 2 Posts: 2,106 ✭✭✭SpannerMonkey


    Not sure . This is the plate on the pump


  • Registered Users, Registered Users 2 Posts: 2,106 ✭✭✭SpannerMonkey


    That joule tank is supposedly specifically for heat pumps ?


  • Registered Users, Registered Users 2 Posts: 107 ✭✭Tommyboy08


    Not sure . This is the plate on the pump

    17kw, must be a very big house,
    Go for the nibe tank, that heat pump won't work on the joule tank,
    I know its a heat pump tank but pretty much only for small inverter air to water units


  • Registered Users, Registered Users 2 Posts: 2,106 ✭✭✭SpannerMonkey


    3000 sq ft . thanks for the advice . im just wary of the glass after the last one going . i assume if i keep proper maintenance of the anode it would be ok ?