Am I going crazey?

  • 12-01-2014 9:39pm
    #1
    Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭


    Because of a recent post, I looked up the Grant 2004 manual for the 50/90 modular burner and this is what I see.

    288528.jpg
    There has to be something wrong with the settings for the firing ranges highlighted. How are they getting increased output by using the same nozzle at same (in 1 instance) and lower pressure (in other instance)?

    Please follow site and charter rules. "Resistance is futile"



Comments

  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    yes, crazey is spelt crazy,manual appears to be wrong in the bar pressure column,so not crazy


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    yes, crazey is spelt crazy,manual appears to be wrong in the bar pressure column,so not crazy
    Is it rong in the pump pressure or the nozzle size?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    id say your wight its wong


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Wearb wrote: »
    Because of a recent post, I looked up the Grant 2004 manual for the 50/90 modular burner and this is what I see.

    288528.jpg
    There has to be something wrong with the settings for the firing ranges highlighted. How are they getting increased output by using the same nozzle at same (in 1 instance) and lower pressure (in other instance)?

    based on the utility and boilerhouse models they should read
    7bar 9bar 7bar and 9.5bar according to my bible


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    based on the utility and boilerhouse models they should read
    7bar 9bar 7bar and 9.5bar according to my bible

    The reason that I thought it might be incorrect nozzle listed is because the kg colum seems like it might be giving correct rate.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    This was on an old 2004 manual for the standard 50/90 Outdoor Module, and was a printers error.
    Find the correct settings here

    288844.jpg


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    WTF, Grant 70/90 with 50/70 baffles. I assume it is a 50-70 boiler (both labels say 70-90) unless the baffles are interchangeable and just happen to be fitted by mistake.
    Which boiler was I servicing???


    288882.jpg

    288884.jpg

    Must be my week for Grant anomalies :(:(

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    do grant do a 50/70 multipass I could be wrong I thought they started at 70/90 ???


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    do grant do a 50/70 multipass I could be wrong I thought they started at 70/90 ???
    Its listed on the manual anyway Jim, and the baffles on the one I was working on are the type listed for the 50-70. How am I to set it up with such contradictions.
    In the end, I hedged my bets and set it up for the lowest firing rate for the 70-90, which is near enough the same configuration as the highest rate for the 50-70.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    your having great fun this week just checked manual I have doc022 rev9 jan 05 no listing for mp 50/70 they start at 70/90 jaysus this gets better by the day


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    jimf wrote: »
    your having great fun this week just checked manual I have doc022 rev9 jan 05 no listing for mp 50/70 they start at 70/90 jaysus this gets better by the day

    Always nice to keep upto date... :-)


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    Always nice to keep upto date... :-)

    sounds like I need to so shane :eek:


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Even some Mods are known to say "keeping upto date is a beautiful thing...."


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    Even some Mods are known to say "keeping upto date is a beautiful thing...."

    funny thing about the manuals I have I got them all from grant about 2 1/2 years ago

    so its time for an update me thinks


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Think that's bad, look at the Vokera Mynute manual section for LPG and calculate the gross input from the gas rate listed


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    your having great fun this week just checked manual I have doc022 rev9 jan 05 no listing for mp 50/70 they start at 70/90 jaysus this gets better by the day

    Just checked their website and they don't even have the one you have on there, only the 04 one. F in great and I still don't know which one I was working on.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Wearb wrote: »
    Just checked their website and they don't even have the one you have on there, only the 04 one. F in great and I still don't know which one I was working on.

    what manual do u have

    but as shane says its good to keep up to date its only when you come across 1 of these boilers these issues start high lighting themselves


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    jimf wrote: »
    what manual do u have

    but as shane says its good to keep up to date its only when you come across 1 of these boilers these issues start high lighting themselves

    Part No. DOC 02 Rev.12 October 2004

    I regularly check manufacturers sites for updates, but that is the newest I could find.
    How else do you keep up to date?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 257 ✭✭kscobie


    jimf wrote: »
    do grant do a 50/70 multipass I could be wrong I thought they started at 70/90 ???

    Your on the ball jimf, that is a 70/90 Multipass, there was a 50/70 Euroflame alright


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    kscobie wrote: »
    Your on the ball jimf, that is a 70/90 Multipass, there was a 50/70 Euroflame alright

    Well they are on two versions of intallation manuals and they certainly made baffles for them, see photo. How do you explain that?:confused:

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Wearb wrote: »
    Well they are on two versions of intallation manuals and they certainly made baffles for them, see photo. How do you explain that?:confused:

    Maybe Scudo built those ones.
    Any sign of any biscuit tins behind them?
    ;-)


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    The baffles in your image look like they are same baffles in the grant 50/70 utility/kitchen model.My thinking is there probally is very little difference[in operation] between these baffles and the baffles shown in the manual for the 70/90 boiler house model


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    shane0007 wrote: »
    Maybe Scudo built those ones.
    Any sign of any biscuit tins behind them?
    ;-)

    They were stamped USA. I could find no reference to that in the MI. :)

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 257 ✭✭kscobie


    All the Multipass baffles are removed from the front, as they have water jackets down the middle, the Euroflames baffles come out the top, I never seen a 50/70 Multipass, did you ring Grant ?


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    agusta wrote: »
    The baffles in your image look like they are same baffles in the grant 50/70 utility/kitchen model.My thinking is there probally is very little difference[in operation] between these baffles and the baffles shown in the manual for the 70/90 boiler house model

    I don't see the similarities between the two, but could have looked at the wrong image on the PDF

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    kscobie wrote: »
    All the Multipass baffles are removed from the front, as they have water jackets down the middle, the Euroflames baffles come out the top, I never seen a 50/70 Multipass, did you ring Grant ?

    Emailed them. They have someone here on Boards that will (maybe has) commented on it.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    Maybe Scudo built those ones.
    Any sign of any biscuit tins behind them?
    ;-)

    your not up to date shane they only work with warmflow :p


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    jimf wrote: »
    your not up to date shane they only work with warmflow :p

    I know, sorry.
    It's was the USA that threw me (Under Scudo's Authority).


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Wearb, it was me who commented on their behalf (they rang me) and asked that I posted the correct setup info page that I did.

    They also commented that currently all manuals (including discontinued products) are in process of being rewritten for the website.
    (no I don't work for Grant, just know the lads their well)

    Always though USA was Under Shane's Authority

    I find lots of manufacturer's instructions have discrepancies, have come across so many (even more on gas)


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    DGOBS wrote: »
    Wearb, it was me who commented on their behalf (they rang me) and asked that I posted the correct setup info page that I did.

    They also commented that currently all manuals (including discontinued products) are in process of being rewritten for the website.
    (no I don't work for Grant, just know the lads their well)

    Always though USA was Under Shane's Authority

    I find lots of manufacturer's instructions have discrepancies, have come across so many (even more on gas)

    Thanks Dgobs. Did they ask you to comment on the multipass 70-90 with 50-70 baffles?

    I think Shane and Scudo are in cahoots and sometimes just put on a belligerent front here :)

    I suppose it's too much to expect manufactures to provide a web page to announce those corrections. Even though it would be very useful, they would fear it would undermine confidence.

    Please follow site and charter rules. "Resistance is futile"



  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Sorry, I was speaking to them before you poster re the baffles.
    I'll ask them to have a look when I get a chance