Problem with radiator

  • 06-01-2014 12:10am
    #1
    Registered Users, Registered Users 2 Posts: 543 ✭✭✭


    Hi,

    I have problem with two radiators in the house. Basically all are roasting hot part from two that are lukewarm when gas CH on for a while

    I bled them and both seems to turned on fully.

    Any suggestions?


Comments

  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Hi,

    I have problem with two radiators in the house. Basically all are roasting hot part from two that are lukewarm when gas CH on for a while

    I bled them and both seems to turned on fully.

    Any suggestions?

    Most likely a circulation or balancing issue?
    At a guess, are the two rads downstairs, one in that hall, the other in the living room the other side of the wall?


  • Registered Users, Registered Users 2 Posts: 543 ✭✭✭Carpet diem


    shane0007 wrote: »
    Most likely a circulation or balancing issue?
    At a guess, are the two rads downstairs, one in that hall, the other in the living room the other side of the wall?

    Yep!?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Watch out Keith Barry, Shane0007 is hot on your heels


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Yep!?

    Well used to them.
    You will also have the pipes coming out of the walls to the rads downstairs & out of the floors to the rads upstairs.

    Your boiler pressure will be reading 0.5bar.

    Basically, if yes to above, you have the dreaded drop down & most likely a semi-sealed system.

    If you boiler has any age to it, it most likely only has a 5m head pump. This in a highly restrictive system with 2 rads fed on a drop down 1/2" pipe in the wall is the issue.

    Can it be fixed? Yup.