Overloaded...????

  • 18-12-2013 1:29pm
    #1
    Registered Users, Registered Users 2 Posts: 7,101 ✭✭✭


    A while back we bought a new electric kettle and matching toaster in Debenhams...Have been impressed with the kettle since day one, it will boil a full load in less than 3 minutes...on inspection/cleaning yesterday i noticed that it was rated at 3kw...:eek:...thats three bars on yer old electric fire (Jim Royle would have a stroke).....combined with the toaster at 1.8kw thats 4.8kw on one 2.5mm t+e cable....the washing machine is also on the same circuit....

    So my question is , if its safe to have all three going at the same time...:confused:

    TBH...it looks like theres only one cable feeding the entire kitchen...


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    A while back we bought a new electric kettle and matching toaster in Debenhams...Have been impressed with the kettle since day one, it will boil a full load in less than 3 minutes...on inspection/cleaning yesterday i noticed that it was rated at 3kw...:eek:...thats three bars on yer old electric fire (Jim Royle would have a stroke).....combined with the toaster at 1.8kw thats 4.8kw on one 2.5mm t+e cable....the washing machine is also on the same circuit....

    So my question is , if its safe to have all three going at the same time...:confused:

    TBH...it looks like theres only one cable feeding the entire kitchen...

    there may be a ring circuit feeding the kitchen...that is rated higher than 1 t+e

    the norm now is a few radial(single) circuits

    the t+e is protected by the mcb at the distribution board(fusebox)


    it may trip if you plug too much in


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    So my question is , if its safe to have all three going at the same time.


    If your wiring complies with the regulations then yes it is safe to use all 3 devices at the same time.

    TBH...it looks like theres only one cable feeding the entire kitchen...


    At present the requirement is that a kitchen should be served by a minimum of 2 dedicated radial socket circuits.

    Typically these circuits would be protected by a 20A B type MCB.
    A 4.8kW resistive load will draw in the region of 20.8 amps. Even if the total load peaked at 25A for a minute or two the 20A B Type MCB would not trip.
    Well within the time frame the kettle would have boiled and the toaster would have to popped.








  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    A while back we bought a new electric kettle and matching toaster in Debenhams...Have been impressed with the kettle since day one, it will boil a full load in less than 3 minutes...on inspection/cleaning yesterday i noticed that it was rated at 3kw...:eek:...thats three bars on yer old electric fire (Jim Royle would have a stroke).....combined with the toaster at 1.8kw thats 4.8kw on one 2.5mm t+e cable....the washing machine is also on the same circuit....

    So my question is , if its safe to have all three going at the same time...:confused:

    TBH...it looks like theres only one cable feeding the entire kitchen...
    What KW rating is on your washing machine?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Just to add:

    Although the wiring may comply with the regulations and switching on all 3 devices simultaneously may not be dangerous, however the installation may be suffering from poor design and/or a lack of socket circuits!


  • Registered Users, Registered Users 2 Posts: 7,101 ✭✭✭Max Headroom


    Thanx lads...its a 70's house...theres up sockets, down sockets and kitchen...thats it...only one wire at each (3 x20a) cb.....might get a couple of new ones run in after chrimbo.......;)


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    .might get a couple of new ones run in after chrimbo.......;)
    Good idea.