Arca LPG gas boiler wont fire up

  • 29-11-2013 9:03pm
    #1
    Registered Users, Registered Users 2 Posts: 844 ✭✭✭


    Hi there.I have Arca LPG gas boiler wich wont fire up.This morning water pressure dropped down to 0 Bar and the only way to put water to the system is to manually open valve te get pressure to 0.5 Bar.But if I do this way boiler of course will fire up but pressure goes to over 3.5 bar and water is leaking from one pipe :( I have never had that problem before.
    Can someone give some idea what to check? I dont know much about plumbing but woul like to know what to say to plumber :D


Comments

  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Expansion vessel will need to be either recharged or replaced. And most likely the prv also


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    Egass13 wrote: »
    Expansion vessel will need to be either recharged or replaced. And most likely the prv also

    To be honest I dont see any expansion vessel anywhere...Unless it is in the attic...What is the PRV?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    To be honest I dont see any expansion vessel anywhere...Unless it is in the attic...What is the PRV?

    The expansion vessel is hidden behind the boiler usually. PRV is a pressure release valve. Get an Rgi to check it out for you


  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Is it an arca pocket ? If so it's in the back as Declan suggested


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Egass13 wrote: »
    Is it an arca pocket ? If so it's in the back as Declan suggested

    Please, call me dec, only my mother calls me Declan :D


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,056 ✭✭✭Egass13


    Dtp1979 wrote: »
    Please, call me dec, only my mother calls me Declan :D

    Sorry deco ... ;)


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    Thx lads.Im going to call RGI on monday.BTW:this morning pressure was 0.2 and it took 12 minutes to fire up. :D


  • Registered Users, Registered Users 2 Posts: 1 britnic


    how did you get on with your arca boiler... i have an arca pocket that does the same thing as yours.... what did you get done o rectifiy it?? help!


  • Registered Users, Registered Users 2 Posts: 474 ✭✭Candy_Girl


    Hi I'm just wondering if you got your boiler fixed? I've the same boiler and I've been having trouble with it the past two weeks...same thing as yourself, pressure dropping and having to fill the system back up to get the boiler to fire up. That was until Tuesday when it stopped responding completely.

    Anyhow I had a plumber out yesterday to have a look and he said the expansion vessel needs to be replaced but because it's an old boiler the part is impossible to get!!!

    Did you get yours fixed?


  • Registered Users, Registered Users 2 Posts: 459 ✭✭nmacc


    You don't need the actual, specific, Arco-specified and certified expansion vessel. Just about any old expansion vessel will do and it can be fitted almost anywhere in your heating system. So a replacement vessel could go in the hotpress or, in some cases, in the loft.

    Simples.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 262 ✭✭RJF


    yes, and it also needs to be sized to fit the system. Best practice to locate as close to the boiler as possible


  • Registered Users, Registered Users 2 Posts: 474 ✭✭Candy_Girl


    Thanks guys, The plumber suggested to have the boiler replaced but as they're quite expensive it's not really an option at the moment. I'm not sure why he hasn't the same advice as you both. Anyhow I've found the part I need online so I'm just wondering if you would have any idea what the cost of fitting would be roughly?

    Thanks.


  • Registered Users, Registered Users 2 Posts: 1,115 ✭✭✭wilser


    I think ecopipe in Stillorgan are the agents for arca boilers, might be handier/cheaper than online


  • Posts: 0 [Deleted User]


    Candy_Girl wrote: »
    Thanks guys, The plumber suggested to have the boiler replaced but as they're quite expensive it's not really an option at the moment. I'm not sure why he hasn't the same advice as you both. Anyhow I've found the part I need online so I'm just wondering if you would have any idea what the cost of fitting would be roughly?

    Thanks.

    To advise a new boiler for the want of a new expansion vessel is criminal:mad:.

    Defective expansion vessels are usually a symptom of another problem which would be system water contamination ie... Sludge.

    If it were me I would find a decent RGI to fit externally a secondary expansion vessel(if practical) and magnetic filter also I'd be asking for his/her opinion on the quility of your system water to help decide whether or not any flushing is required.


  • Registered Users, Registered Users 2 Posts: 474 ✭✭Candy_Girl


    gary71 wrote: »
    To advise a new boiler for the want of a new expansion vessel is criminal:mad:.

    Defective expansion vessels are usually a symptom of another problem which would be system water contamination ie... Sludge.

    If it were me I would find a decent RGI to fit externally a secondary expansion vessel(if practical) and magnetic filter also I'd be asking for his/her opinion on the quility of your system water to help decide whether or not any flushing is required.

    Thanks I'll look into that.


  • Registered Users, Registered Users 2 Posts: 262 ✭✭RJF


    When you said you found the part was that an original exp. vessel for the arca boiler or are you talking about a standard external vessel. Was the plumber basing his recommendation to replace the boiler on any other factors other than the exp. vessel? If so what were they?