RCD tripping for iron, laptop

  • 08-11-2013 7:03am
    #1
    Registered Users, Registered Users 2 Posts: 250 ✭✭


    Hi. Any advice appreciated please.
    10 y.o. house. About 2 months ago the iron tripped the kitchen sockets from one particular socket. Working fine elsewhere, so just left that one socket as a dud.

    In the last few days, laptop has tripped all the sockets in the house, regardless of where plugged in. New charger ordered.:-(

    This morning, iron is now tripping all the sockets suddenly...no reason (ironed short, half way through pants...gone). Kettle works fine on the same socket.

    I'm presuming it's a qualified electrician job in-house, but just want to be sure am I missing something obvious? Could iron and laptop be both (suddenly) faulty?

    Thanks for any pointers.
    ironwalk


Comments

  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    If both laptop and iron are both consistently tripping the RCD regardless of the socket it's plugged into I'd say it's your laptop and iron that's the problem


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    Yup you'll need REC for this with the correct test instruments.


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Thanks.

    Am confused....are you saying the opposite?

    If it's the house electrics, wouldn't the kettle/ microwave trip them too?


  • Registered Users, Registered Users 2 Posts: 1,115 ✭✭✭chrismon


    Id think the iron and laptop charger are at fault here.
    You won't know until you get it checked by an electrician.


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    Yes more than likely if it was the wiring other appliances would trip the RCD.

    Maybe bring the iron and laptop to a friend's house and test them


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Thanks.

    Am confused....are you saying the opposite?

    If it's the house electrics, wouldn't the kettle/ microwave trip them too?


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Thanks all. Very helpful.
    I'll test them over weekend. I'll come back if it's obviously not a device problem.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    ptogher14 wrote: »
    If both laptop and iron are both consistently tripping the RCD regardless of the socket it's plugged into I'd say it's your laptop and iron that's the problem

    I would think the laptop has no earth connection to its switching adaptor/transformer. So its likely, or at least possibly anyway, the problem lies with the installation. Possibly the neutral-earth fault scenario again.

    You never know though.


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    Bruthal wrote: »
    I would think the laptop has no earth connection to its switching adaptor/transformer. So its likely, or at least possibly anyway, the problem lies with the installation. Possibly the neutral-earth fault scenario again.

    You never know though.

    But a laptop charger is usually double isolated


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    ptogher14 wrote: »
    But a laptop charger is usually double isolated

    Double insulated? Yea, that`s the point i`m making. Its an interesting one to see how it will be tripping an RCD with no earth connection to it.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    A fault on the primary side maybe


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    ptogher14 wrote: »
    A fault on the primary side maybe

    They are usually switching mode transformers rather than windings.

    But even if it was a wire wound transformer, Id say it would be a curious one if a fault on it tripped an RCD, when there is no earth connection to the adaptor/transformer for any fault current to cause an imbalance in L/N current.

    Its a curious one anyway, if them two items only, are tripping the RCD. Possibly, the high loading of the iron, and the operation of the switching mode laptop transformer, are tripping the RCD through an intermittent neutral-earth fault within the installation.

    Or perhaps there is indeed a problem with them 2 items. Id just say it would be unusual for a double insulated, non earthed item to cause trips on an RCD.


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Gentlemen..thanks for the technical discussion-way over my head :)

    Brought laptop to a friend's house...charged away lovely. Used it all evening without a hitch.

    What's the advice on what to do now?


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    ironwalk wrote: »
    Gentlemen..thanks for the technical discussion-way over my head :)

    Brought laptop to a friend's house...charged away lovely. Used it all evening without a hitch.

    What's the advice on what to do now?

    Time to call an electrician:-D


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    ironwalk wrote: »
    Gentlemen..thanks for the technical discussion-way over my head :)

    I will summarise: I am agreement with Bruthal, the problem is the wiring in your home not the laptop.
    What's the advice on what to do now?

    As ptogher14 said, call an electrician.
    Should be a simple fix for a sparks.


  • Registered Users, Registered Users 2 Posts: 326 ✭✭marathont


    Hi

    I had a problem with the RCD tripping seemingly randomly. Often happened when someone plugged something in, any socket. didnt happen all the time only now and then.

    I replaced the RCD and never had any more problems.


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Thanks for advice on here. Had the electrician out....he was stumped but seems to think my iron is the source of the problem not the house wiring.
    I'm not sure myself if we've solved the problem but I think it's wait and see if things start tripping again.
    Thanks for the advice.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    ironwalk wrote: »
    Thanks for advice on here. Had the electrician out....he was stumped but seems to think my iron is the source of the problem not the house wiring.
    I would be surprised, time will tell :)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    marathont wrote: »
    I had a problem with the RCD tripping seemingly randomly. Often happened when someone plugged something in, any socket. didnt happen all the time only now and then.

    I replaced the RCD and never had any more problems.

    Occasionally RCD's have been know to fail (sometimes they are over sensitive).


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Ok. If there was a grrrrr emoticon, I'd have it here.

    Interesting last comment by 2011 re RCD being sensitive, as I was comparing it to a stroppy teenager this morning.
    No problem all week. New iron. Laptop charging fine.
    This morning I turned on laptop ....have work to do for Monday morning.

    Tripped immediately. Now phone charger is tripping it too....all while kettle is happily boiling on same circuit.

    Do electricians work Saturdays....need to get work done for client.


  • Advertisement
  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    ironwalk wrote: »
    Ok. If there was a grrrrr emoticon, I'd have it here.

    Interesting last comment by 2011 re RCD being sensitive, as I was comparing it to a stroppy teenager this morning.
    No problem all week. New iron. Laptop charging fine.
    This morning I turned on laptop ....have work to do for Monday morning.

    Tripped immediately. Now phone charger is tripping it too....all while kettle is happily boiling on same circuit.

    Do electricians work Saturdays....need to get work done for client.

    Where in Ireland are you?


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Waterford


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    ironwalk wrote: »
    Waterford

    Sorry i dunno anyone out that way.

    http://www.reci.ie/ConsumerServices/FindanElectrician.aspx

    had a quick look here and theres 28 REC in Waterford who do domestic works so SURELY one of those can sort it out today. Even if its just too tide you over till Monday and rectfy it then!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    ironwalk wrote: »
    Ok. If there was a grrrrr emoticon, I'd have it here.

    Interesting last comment by 2011 re RCD being sensitive, as I was comparing it to a stroppy teenager this morning.
    No problem all week. New iron. Laptop charging fine.
    This morning I turned on laptop ....have work to do for Monday morning.

    Tripped immediately. Now phone charger is tripping it too....all while kettle is happily boiling on same circuit.

    Do electricians work Saturdays....need to get work done for client.

    Did it trip immediately you actually switched laptop on, or when you plugged it into the wall socket? Did you notice the trip switch tripping, or only notice it because laptop didnt start?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    you should have had some definite answers after the electrician called..

    you should know if there was a earth fault in the iron (not hard to check)

    and if the rcd is operating correctly and if there's faults showing in the rcd protected circuits

    it could happen then that you have you some intermittent problem at a socket wiring


  • Registered Users, Registered Users 2 Posts: 250 ✭✭ironwalk


    Thanks mrmac, bruthal & tomdempsey.

    Have an electrician who says he'll call later. On phone, he says he should be able to work something over weekend to keep me going (so I can work done for Mon morning client at least).

    I plugged laptop into socket, turned socket on, switched laptop on. 15 seconds later desk lamp beside laptop went off so I knew RCD had gone.

    I've replaced the iron, after advice from last week's electrician.
    If it was a socket problem, would that cause RCDs to trip, even when laptop plugged in on a different circuit?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    sounds like you're back to square 1 ...the iron should been tested and a fault showing



    you'll have to test rcd and circuits for faults anyhow


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    ironwalk wrote: »
    Thanks mrmac, bruthal & tomdempsey.

    Have an electrician who says he'll call later. On phone, he says he should be able to work something over weekend to keep me going (so I can work done for Mon morning client at least).

    I plugged laptop into socket, turned socket on, switched laptop on. 15 seconds later desk lamp beside laptop went off so I knew RCD had gone.

    I've replaced the iron, after advice from last week's electrician.
    If it was a socket problem, would that cause RCDs to trip, even when laptop plugged in on a different circuit?

    Iron should have been tested, rather than guessed at.

    If you have an immersion, switch it off at its immersion switch, and see if problem persists.

    For an electrician, RCD needs to be tested. If ok, a neutral to earth test on the RCD neutral bar. If it shows a fault, unplug everything, switch immersion off. Test again. If still showing a fault, then all neutrals removed from RCD neutral bar and tested individually to earth. If a neutral shows a problem, identify circuit and locate problem by splitting the circuit and isolating sections of it and testing.

    Neutral to earth faults can trip RCD from items on a different circuit, but in this case, when the RCD trips, it wont be known which circuit, if any, has the problem.

    If it was a Live to earth fault, it would trip without anything plugged in. These things are usually neutral to earth faults.

    Another thing an electrician could try, is fitting a second RCD, and splitting the socket circuits over the existing and new one. That might get closer to reducing the circuits that need to be checked, or it may stop tripping problems either.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    and how big is the installation(house) btw?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,908 ✭✭✭zom


    Just if I can have some similar question - room of 10 old PC's (office). RCD tripping every first working day after weekend or longer break. I have to disconnect half of machines and let another half work for few hours - then I can connect the others and everything works fine. I checked RCD, cables, wiring - no fix. I am about to check all power supplies (PCs and screens) but maybe someone have better idea?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    zom wrote: »
    Just if I can have some similar question - room of 10 old PC's (office). RCD tripping every first working day after weekend or longer break. I have to disconnect half of machines and let another half work for few hours - then I can connect the others and everything works fine. I checked RCD, cables, wiring - no fix. I am about to check all power supplies (PCs and screens) but maybe someone have better idea?

    too many pc's on rcd
    recommended is about 4-6
    cumulative leakage


  • Registered Users, Registered Users 2 Posts: 1,908 ✭✭✭zom


    too many pc's on rcd
    recommended is about 4-6
    cumulative leakage

    It would be easy if they trip RCD all the time but it only happen after few days of no use. I forgot to mention - they trip it while not working - just connected to mains. I have to physically disconnect half of them and after few hours connect back.
    I suspect some damp somewhere but not sure in PCs or in power wiring (walls)? Any thoughts?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    test rcd and final circuit
    if nothing shows
    balance pc's over 2 rcd/rcbo

    you can test all the iec leads for damp by leaving them plugged in to wall and disconnected from pc/monitor while testing circuit

    can't think of much else unless you've narrowed it down to a faulty pc


    it might be worth replacing rcd if it's old
    and is there anything else on circuit except office?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    too many pc's on rcd
    recommended is about 4-6
    cumulative leakage

    Agreed, a few circuits fed by RCBOs would be preferable.

    Surge protection devices have also been known to contribute to this problem.

    There is some interesting suggestions made by ABB here:

    http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/7115a45a1e2da408c1256cbc0054f193/$file/2csc421002b0201.pdf

    From page 3:
    To obtain continuity of service for priority circuits and, at the same time, protect the loads and installations from transient overvoltage peaks, we recommend combining the AP range of RCCBs and RCD blocks with OVR surge protective devices (SPD)."


    It should also be noted that it is permitted to install IT equipment (such as PCs) from non standard type sockets fed from circuits that do not have RCD protection. Here is an example of a non standart socket with a "T" section earth pin. Needless to say that other standad type general services/cleaners sockets with RCD/RCBO should also be provided if this option is used. K1246WHI.jpg


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    yes, a few good points there

    the SPDs can be a problem with tripping might be worth testing without them


    it is permissible to omit rcd if sockets are not for general use



    i'm not sure that the AP rcds are specifically designed for this issue although simply replacing the rcd may cure it


    prob just simply splitting the pcs will cure it...


  • Advertisement
  • Closed Accounts Posts: 9,088 ✭✭✭SpaceTime


    Some places actually use RCD-sockets like you'll see them in M&S and on Irish Rail trains quite a lot.

    This still provides you with RCD coverage, but won't trip the whole circuit, just that one local socket.

    I think kitchen and utility room circuits should be on RCBOs at least.

    Kettles, irons, coffee machines, dishwashers and occasionally laundry appliances are the most likely RCD-tripping culprits due to their relationship with water!


  • Registered Users, Registered Users 2 Posts: 2,099 ✭✭✭spankmemunkey


    I bet i know whats happening here!

    Your pulling the sockets when you pull the plug on the Iron or the Charger for laptop. The Microwave i bet never gets unplugged and one of the connections to the rear of the socket is loose. Did the electrician check all your sockets by removing them and checking that all connections are secure at the back? when you push and pull plugs in and out they can loosen connections at the back of the socket, it could be the socket needing replacing too it may be faulty.


  • Registered Users, Registered Users 2 Posts: 3,518 ✭✭✭stefan idiot jones


    2011 wrote: »
    Occasionally RCD's have been know to fail (sometimes they are over sensitive).

    Correct. I am a Maintenance Officer in an Aged Care Residence and we have hundreds of RCDs.

    I have to deal with issues like this daily.
    I deal with our electrician about these such matters and you're right. When a RCD trips, or continually trips it 'wears out' and becomes too sensative.

    We have had to replace a few RCDs as for example, an old bainmarie used to constantly trip has been replaced with a new one but still trips the circuit. The new piece of equipment is perfect and not overloading the circuit but the RCD is defective and had to be changed.