What temperature frost-stat for outside boiler?

  • 02-11-2013 6:16pm
    #1
    Registered Users, Registered Users 2 Posts: 11,879 ✭✭✭✭


    Hiya all - just wondering what people have their frost-stat set to in their boiler house. We have the outside kerosene boiler in the metal galvanised housing and our frost-stat seems to be set at +4c and the main thermostat at 75c does that sound right?


Comments

  • Registered Users, Registered Users 2 Posts: 1,907 ✭✭✭woody1


    sorry andy i dont know the answer definitively but +4 sounds about right to me, il leave it to someone else that knows what their talking about

    if its ok im going to piggyback on your thread to ask another frost stat related question.. i have a grant vortex external boiler and the frost stat is either set too high or not working properly, its going off today at 9 degrees, and in general it tends to trigger way above freezing, can they be adjusted / replaced, ive been advised to remove it but im obviously not keen on that !!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Hiya all - just wondering what people have their frost-stat set to in their boiler house. We have the outside kerosene boiler in the metal galvanised housing and our frost-stat seems to be set at +4c and the main thermostat at 75c does that sound right?

    +4C is correct as this is inside the casing. If it's +4C inside the casing, it will be minus outside the casing.
    70-75C is fine.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    woody1 wrote: »
    i have a grant vortex external boiler and the frost stat is either set too high or not working properly, its going off today at 9 degrees, and in general it tends to trigger way above freezing, can they be adjusted / replaced, ive been advised to remove it but im obviously not keen on that !!

    There was a bad batch of frost stats fitted to the Grant Vortex a while back. Put through a warranty call & the service engineer will call out & replace for you free of charge.
    Just ensure the Boiler Passport was correctly filled out with the commissioning certificate & returned to Grant to instigate your warranty.