2 Electric Showers.. no priority unit.

  • 23-10-2013 5:14pm
    #1
    Registered Users, Registered Users 2 Posts: 5


    I have been asked to install a second 'mains' shower in a converted attic.

    There is only 2 people living in the house and they say that they will be observant of shower use and they wont use them at the same time. :confused:

    I know you can purchase a priority unit to solve this, but I have heard of an sufficient rated immersion switch being used to do a similar task. This would cost far less then the priority unit.

    Something about you wiring the showers as follows.... 1st as the sink feed and the 2nd as the bath feed. And then switch between the two. Both shower cable supplies run by each other in a boxed unit in the landing, so wiring this would be handy enough.

    Just wondering has any one come across this and if so is it technically alright.


Comments

  • Registered Users, Registered Users 2 Posts: 5,477 ✭✭✭Hootanany


    Rocker switch is needed


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    you can fit a 4-pole contactor(2no/2nc) in the distribution board and control it with a 2-way switch

    or even a suitably rated manual changeover switch in a suitable location

    priority control with 2-pole contactor and current sensing relay is prob the handiest....


    do you know what you're doing btw?..:)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    you can fit a 4-pole contactor(2no/2nc) in the distribution board and control it with a 2-way switch

    or even a suitably rated manual changeover switch in a suitable location

    priority control with 2-pole contactor and current sensing relay is prob the handiest....
    +1 if they are instantaneous showers.
    Can you confirm the size of the loads?
    Either way a standard immersion switch is not the solution.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    There is only 2 people living in the house and they say that they will be observant of shower use and they wont use them at the same time.

    That is the type of statement that any electrician worth his salt would completely disregard.


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    2011 wrote: »
    That is the type of statement that any electrician worth his salt would completely disregard.

    +1

    And of course the house will be sold or leased to some poor unsuspecting person.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    you can fit a 4-pole contactor(2no/2nc) in the distribution board and control it with a 2-way switch

    Won't need a 2 way switch for that setup:p


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    ya 1 way ..


  • Registered Users, Registered Users 2 Posts: 5 Rizlablueby2


    Ya thought it was to good to be true.... just wondered had ne1 seen/heard of this way... could be handy for other wiring configurations....

    Got them to pay up for the priority unit... Said it wasn't worth the chance for them, or me in skipping it...

    All the same,thanks for speedy response.....,

    Site is fair handy....


  • Registered Users, Registered Users 2 Posts: 203 ✭✭ptogher14


    Double up. Wire them both off the same 40A RCBO.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    ptogher14 wrote: »
    Double up. Wire them both off the same 40A RCBO.

    no...


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    no...

    Why not?
    There may be 2 showers, but only one can be powered at a time.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    2011 wrote: »
    Why not?
    There may be 2 showers, but only one can be powered at a time.

    seriously?

    it's not good or acceptable practice for a start..

    i would hazard a guess it also contravenes wiring rules somewhere


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    if you double them up at the mcb it's 1 circuit..

    circuit design current then exceeds rating of protective device...


    not allowed..


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    if you double them up at the mcb it's 1 circuit..


    You do not need to double up at the MCB.
    The MCB feeds the contactor.
    The contactor feeds either one load or the other.
    circuit design current then exceeds rating of protective device...

    Incorrect.

    The connected load is a single shower at any given time.
    Therefore the design current is always less than the rating of the protective device.

    By the way if you wanted an RCBO for each shower then they would have to be installed downstream of the contactor.
    In this case a protective device would have to be installed upstream of the contactor (MCB or fuse) unless it was rated for 63A.

    What would the adavantage of this set up be?
    I can't see how it would be safer or better practice.
    I can see that it requires more components (and consequently a higher chance of failure), takes up more space in the board and costs more money on materials and installation.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    i think you have misinterpreted ptogher14 post

    he is suggesting to use the 40a rcbo as the controller... to prevent overcurrent


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    i think you have misinterpreted ptogher14 post

    he is suggesting to use the 40a rcbo as the controller... to prevent overcurrent

    Really?
    If that is his suggestion as you say this would be against regulations and very bad practice. It is not the way I read it though.


  • Registered Users, Registered Users 2 Posts: 22,656 ✭✭✭✭Tokyo


    i think you have misinterpreted ptogher14 post

    he is suggesting to use the 40a rcbo as the controller... to prevent overcurrent

    That's the way I read it too - wire both showers separately all the way back to the 40A RCBO. Either shower on it's own will run fine, both showers get switched on together and the RCBO trips. Sounds like a terrible idea.....


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    i know lads that did it

    i tried it once myself before i knew better ...and she didn't trip btw

    dunno what the shower ratings were at the time maybe 6-7kw or thereabouts


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    mike_ie wrote: »
    That's the way I read it too - wire both showers separately all the way back to the 40A RCBO. Either shower on it's own will run fine, both showers get switched on together and the RCBO trips. Sounds like a terrible idea.....

    Perhaps I misunderstood the post.

    Either way, wiring 2 instantenious showers directly to a single RCBO is not the way to go.


  • Registered Users, Registered Users 2 Posts: 22,656 ✭✭✭✭Tokyo


    Not that I'm the biggest on following every rule in the book or anything, but don't showers now fall well outside of what's permitted for the average homeowner to wire in themselves?? OP should be getting in a sparky either way....


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    mike_ie wrote: »
    Not that I'm the biggest on following every rule in the book or anything, but don't showers now fall well outside of what's permitted for the average homeowner to wire in themselves?? OP should be getting in a sparky either way....

    OP sounds clueless unfortunately for the customer...

    at least he's been persuaded to fit a proper controller


  • Registered Users, Registered Users 2 Posts: 22,656 ✭✭✭✭Tokyo


    OP sounds clueless unfortunately for the customer...

    at least he's been persuaded to fit a proper controller

    Thats the point I'm trying to make. Not questioning anyones knowledge or anything, but at the end of the day the customer has to stand in under this thing every day and dowse himself in water - I'd be hoping it'd be done by someone who didn't have to google the answer...


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    plumbers and diy fit them all the time

    i see miscellaneous bodges like doubling up in 1 rcbo

    last one i seen was shower wired into main isolating switch before main ocpd(63amp fuse)...done by a plumber


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    mike_ie wrote: »
    don't showers now fall well outside of what's permitted for the average homeowner to wire in themselves?? OP should be getting in a sparky either way....


    I agree. "Major heart surgery" on the distribution board such as this should only be carried out by an electrician, without a doubt.

    Unfortunately a minority of qualified electricians will cut corners/gunter/ignore regulations. Threads such as this enable customers that have little or no electrical knowledge to understand what is compliant. They can also learn what the various options are, what is practical, cost effective, advantages/disadvantages etc. It also helps them to understand the terminology so that they can understand what the electrician is trying to explain to them.

    The idea of a thread like this is not to encourage a DIYer to start poking about in a distribution board.