wiring slatted shed

  • 22-10-2013 6:33pm
    #1
    Registered Users, Registered Users 2 Posts: 119 ✭✭


    Ive a2.5 swa running from my garage to shed which is protected with a 63amp breaker and then a 25amp rcbo would i need any more breakers in shed at other end for one socket and a few lights


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    ya you need 'isolating switch' and breakers

    25amp will protect a buried 2.5 swa


    it's not a good idea to fit rcd on the supply side...you have to walk back with no light if she trips

    there's main bonding as well usually

    and testing lol:pac: