New imersion switch

  • 09-09-2013 9:04pm
    #1
    Registered Users, Registered Users 2 Posts: 2,163 ✭✭✭


    Couple of questions

    From what I can work out the imersion is tripping out the RCD on the fuse board. Thought it might be the imersion switch so went and bought a new one but the new one seems to have more connections.

    Old unit has:
    Live/ Nuetral in-Neutral out-Live goes into Bath and the black cable goes into sink- both earth in & out join together.

    New unit has:
    Live/ Nuetral in- Live/Nuetral out-Bath & sink- earth connections- and then a slot in the bottom left corner (marked in red) with no markings.

    IF its not the imersion can I get a meter and bell out the stat/ element, if so what am i looking for

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    if it trips the rcd when you switch it on


    then usually the immersion needs to be replaced


  • Registered Users, Registered Users 2 Posts: 2,163 ✭✭✭cubix


    Noooooo. Was hoping for something simple. Have a meter in the van, can anyone confirm how to bell out before I organise getting the tank drained and new element fitted.


  • Registered Users, Registered Users 2 Posts: 2,637 ✭✭✭brightspark


    If the RCD doesn't trip after removing the wires supplying the element, then the element needs replacing.

    Never seen a switch trip the RCD, usually a bad switch just either stays on or off or won't switch between bath/sink.


  • Registered Users, Registered Users 2 Posts: 688 ✭✭✭maxfresh


    Regarding the new switch(if you are going to change it) the terminal marked with the arrow is the common terminal for the sink and bath ,you will have to take a short piece of brown wire from live out to the common.
    some switches have this link internally yours dosn't


  • Registered Users, Registered Users 2 Posts: 2,163 ✭✭✭cubix


    Thanks lads, changed out the element and am back in the game. Maxfresh, thanks. Ended up putting the old switch back on. Any idea why the new switches are done this way, ie what elements need these extra connections


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 688 ✭✭✭maxfresh


    Its not an extra connection there is just a link inside the old switch (from live in to either sink or bath depending on what way that switch is) that you have put in the new switch


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    cubix wrote: »
    Any idea why the new switches are done this way, ie what elements need these extra connections

    Link from L out to the red arrow terminal, and thats the new switch sorted with regards to the extra terminal. As said, the old switch just has that done internally during manufacture.


  • Registered Users, Registered Users 2 Posts: 2,163 ✭✭✭cubix


    Thanks, the curious in me is wondering in what situation would you not need to use the link from the live to the common.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    None, if using the switch for a dual immersion.