ETCI Reg Quries

  • 20-08-2013 10:16am
    #1
    Registered Users, Registered Users 2 Posts: 163 ✭✭


    Hey,

    Wondering if any body has any information on the following:

    Cable sizing:
    If sizing a NYMJ is it corrrect to use the PVC/Copper tables or the XLPE/EPR table? Something I have been wondering.
    I was looking at cable spec for NYMJ and it was PVC and PVC outer.

    Cable sizing:
    Cable sizing and factoring in Ci (thermal insulation) properties similar to grouping factor and ambient temp factor. Is there a derating table in the regs for thermal insulation as I can not find any? (was it in the old regs?)

    10 lights per circuit:
    Is this limit still in the regs? I have not been able to find it but it says it on one of the etci/reci sites. I feel its impracticable if you have a lot of say LED downlights that would be pulling very little.

    Thanks

    BD


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    mymj- i think you'd be using pvc table


    thermal insulation -don't think so...just ambient temp here afaik

    they have it as a correction factor in the uk alright


    10 lights per circuit-thats gone

    you still need to fit a number of cccts the installation to prevent widespread blackout in event of trip