Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Sub main cable....minimum size????

  • 16-05-2013 8:20am
    #1
    Registered Users, Registered Users 2 Posts: 876 ✭✭✭


    Hi,

    Doing a job where there has to be a new sub main cable ran to a shed and then to another shed.

    Is there now a rule that says cables feeding distribution boards have to be a minimum size. Someone mentioned to me that cable feeding any dist. board has to be minimum 16mm2. Doesn't sound right to me but I have been away from contracting for a few years.

    Thanks


Comments

  • Closed Accounts Posts: 699 ✭✭✭mikehammer67


    no never heard anything like that


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    You will need too calculate the load of the 2 new installations and then you can calculate the size of the mains cable needed allowing for volt drop.

    I mean if you were just putting a single pendant in each shed a 1.5 would prob do.but if it was for heavy duty farm machinery you might need 16's or bigger
    Also keep in mind loads on installations hardly ever fall.they mostly get added too so when you calculate the size cable NEEDED it might be better too go too the next cable up in size too allow for additional work

    *before someone says you can't use 1.5 or the like I haven't asked for the load or the distance of the run etc its just an example.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Is there now a rule that says cables feeding distribution boards have to be a minimum size.
    I have never heard of that.

    Someone mentioned to me that cable feeding any dist. board has to be minimum 16mm2.
    Makes no snese to me.

    MrMac84 has stated, you need to look at the size of the load, lenght of run (to ensure that volt drop is not excessive), the protective device for the cable, the method of installation and any unusual ambient conditions that may affect the cable (e.g. abnormally high temperature). Once you have determined that you can select a suitable cable.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Someone mentioned to me that cable feeding any dist. board has to be minimum 16mm2.

    Possibly mixing up the main cable to the meter which must be 16mm2


Advertisement