fire regulations internal lining timber

Options
  • 09-04-2013 9:25pm
    #1
    Registered Users Posts: 5


    Hi all

    Is there any building regulation restriction on use of timber cladding (Class 3 (National) material) to interior of living area on wall/ ceiling of dwelling.

    Part B requires that:


    Part of the surface of a wall in a room may be of a class lower than specified in 2.1, (but not
    lower than Class D - s3, d2 (European) or Class 3 (National)) if the area of that part (or, if there are two or more such parts, the total area of those parts) does not exceed, the lesser of the following -
    (i) half the floor area of the room, or
    (ii) 20 m2

    Thats fine so far -that tells me that I can have 20m2 or half floor area in timber internal cladding.


    but then the regs seem to contradict this by saying:

    In the case of a wall surface in a building of Purpose Group 1, 2, or 5 the area of that part should not exceed 5 m 2 and should be separated from any other such part by a distance of not less than 2 m

    which would suggest to me that I can only have 5m2 of a class 3 material (i.e. timber).

    I am unsure which should be the case 20m2 or 5m2????

    thanks






Comments

  • Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


    DAVIDLE wrote: »
    Hi all

    Is there any building regulation restriction on use of timber cladding (Class 3 (National) material) to interior of living area on wall/ ceiling of dwelling.

    Part B requires that:


    Part of the surface of a wall in a room may be of a class lower than specified in 2.1, (but not
    lower than Class D - s3, d2 (European) or Class 3 (National)) if the area of that part (or, if there are two or more such parts, the total area of those parts) does not exceed, the lesser of the following -
    (i) half the floor area of the room, or
    (ii) 20 m2

    Thats fine so far -that tells me that I can have 20m2 or half floor area in timber internal cladding.


    but then the regs seem to contradict this by saying:

    In the case of a wall surface in a building of Purpose Group 1, 2, or 5 the area of that part should not exceed 5 m 2 and should be separated from any other such part by a distance of not less than 2 m

    which would suggest to me that I can only have 5m2 of a class 3 material (i.e. timber).

    I am unsure which should be the case 20m2 or 5m2????

    thanks




    Purpose groups are not the same thing as class of materials
    Please read part b again


  • Registered Users Posts: 5 DAVIDLE


    Im fully aware of that.

    Any other advise from anybody?
    thanks.


  • Subscribers Posts: 41,154 ✭✭✭✭sydthebeat


    total unprotected area in a room should not exceed 20 m2 but:

    no area of cladding shall be more than 5m2 in total and then separated from the next area by at least 2m

    so 4 x 5m2 'panels' can be used as long as they are separated by at least 2m


  • Registered Users Posts: 5 DAVIDLE


    Thanks Syd.
    seems to mean that the idea of a timber paneled interior is a complete 'no-no.'

    I have always wondered how timbered paneled pubs/ holiday chalets can comply???


  • Subscribers Posts: 41,154 ✭✭✭✭sydthebeat


    DAVIDLE wrote: »
    Thanks Syd.
    seems to mean that the idea of a timber paneled interior is a complete 'no-no.'

    I have always wondered how timbered paneled pubs/ holiday chalets can comply???

    you can treat the wood so that it has accepetable fire spread performance.

    google impregnated fire treatment.


  • Advertisement
  • Registered Users Posts: 5 DAVIDLE


    thanks again Syd.
    problem solved.