vokera compact he Question

Options
  • 26-03-2013 6:44pm
    #1
    Registered Users Posts: 3,404 ✭✭✭


    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing


Comments

  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    corkgsxr wrote: »
    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing
    Try the RGI tech forum


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    Dtp79 wrote: »
    Try the RGI tech forum

    could never find that


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    corkgsxr wrote: »

    could never find that[/Quote
    Pm sent


  • Registered Users Posts: 2,409 ✭✭✭sullzz


    corkgsxr wrote: »
    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing

    Did you check the venturi


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    sullzz wrote: »
    Did you check the venturi

    Couldn't see one. Suspect there might be one inside the fan fitting for the short hose


  • Advertisement
  • Registered Users Posts: 2,409 ✭✭✭sullzz


    corkgsxr wrote: »

    Couldn't see one. Suspect there might be one inside the fan fitting for the short hose
    I presume your rgi from your previous posts , i suggest you join the rgi tech forum for future gas boiler repair questions


  • Registered Users Posts: 3,404 ✭✭✭corkgsxr


    sullzz wrote: »
    I presume your rgi from your previous posts , i suggest you join the rgi tech forum for future gas boiler repair questions

    Iv the pm sent just waiting