Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

vokera compact he Question

  • 26-03-2013 5:44pm
    #1
    Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭


    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing


Comments

  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    corkgsxr wrote: »
    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing
    Try the RGI tech forum


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    Dtp79 wrote: »
    Try the RGI tech forum

    could never find that


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    corkgsxr wrote: »

    could never find that[/Quote
    Pm sent


  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    corkgsxr wrote: »
    just want a opinion before i deliver bad news.

    boilers turning on the fan and keeps going like that. wont fire.

    take off the short pressure switch hose and it fires.

    tryed a new air pressure switch. same thing.

    no blocks in the flue.

    am i right saying must be the fan? my doubt comes from the fan sounds and looks perfect.

    anything im missing

    Did you check the venturi


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    sullzz wrote: »
    Did you check the venturi

    Couldn't see one. Suspect there might be one inside the fan fitting for the short hose


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    corkgsxr wrote: »

    Couldn't see one. Suspect there might be one inside the fan fitting for the short hose
    I presume your rgi from your previous posts , i suggest you join the rgi tech forum for future gas boiler repair questions


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    sullzz wrote: »
    I presume your rgi from your previous posts , i suggest you join the rgi tech forum for future gas boiler repair questions

    Iv the pm sent just waiting


Advertisement