Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Determining transformer resistance and reactance.

  • 16-02-2013 10:06pm
    #1
    Registered Users, Registered Users 2 Posts: 4,394 ✭✭✭


    Hi guys, I need some help regarding a fictional 200 kVA 3-phase transformer. I am trying to find the resistance and reactance values for this transformer as part of an overall short circuit calculation, in the form of: a + j a where 'a' is the resistance value in ohms and 'j a' is the reactance value in ohms (and j signifies a complex number).

    The information I have is as follows:

    Primary/Secondary = 10000V/400V
    % Impedance = 4%
    Load Losses = 2850 W
    No-Load Losses = 550 W

    I can't seem to get a definitive solution online so I thought I may ask here. I'm guessing it could have something to do with the power formula P =(I^2)(R), however that is just a stab in the dark.

    Any help would be great!


Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Pac1Man wrote: »
    Hi guys, I need some help regarding a fictional 200 kVA 3-phase transformer. I am trying to find the resistance and reactance values for this transformer as part of an overall short circuit calculation, in the form of: a + j a where 'a' is the resistance value in ohms and 'j a' is the reactance value in ohms (and j signifies a complex number).

    The information I have is as follows:

    Primary/Secondary = 10000V/400V
    % Impedance = 4%
    Load Losses = 2850 W
    No-Load Losses = 550 W

    I can't seem to get a definitive solution online so I thought I may ask here. I'm guessing it could have something to do with the power formula P =(I^2)(R), however that is just a stab in the dark.

    Any help would be great!

    200 KVA IS 200,000 VA.

    Full load amps is 200,000/(400 x root 3) = 288 amps per phase.

    Impedence 4% probably means if the secondary is short circuited when the secondary voltage is 4% of 400 (16v), full load current will flow.

    So with the primary voltage raised to a level to give secondary voltage of 16v, and the secondary being direct shorted, full load current will flow, assuming the primary supply level to give such an output, can supply the demand.

    So impedance = V/I = 16/288 = 0.0555 ohms.

    Short circuit current is 400/0.05714 = 7200 amps.

    Another way to get the short circuit current is to get the full load current, which = 4% of the short circuit current, due to 4% of the secondary voltage giving full load current when the secondary side is shorted. So the 288 amps full load = 4% of the short circuit current. 280 x 100/4 = 7200 amps.

    For resistance, the full load copper losses are I squared x R.

    I^2 x R = 2850watts.
    280 x 280 x R = 2850, so R = 2850/(280 x 280) = 0.0364 ohms.

    Of course, someone might come along and fix all the mistakes. But its something along those lines.


  • Registered Users, Registered Users 2 Posts: 4,394 ✭✭✭Pac1Man


    Thanks a million Bruthal, much appreciated. I tried to research it online but the more I read, the more confused I got.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    No bother, just updated it a little. I was a bit rough with getting the full load as 280 which should have been 288 amps.


Advertisement