6mm power for shower?

  • 14-02-2013 6:32pm
    #1
    Registered Users, Registered Users 2 Posts: 48


    Hi I unfortunately only a 6mm cable is there and want to move from a pump to a electric shower any units that can be used?


Comments

  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    I'm open to correction but i believe most shows with a max 8.5kw can be run on 6mm cable, obviously length of run would be a major factor.


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    6mm sq cable running a pump!! What type of pump is it?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Moved to Electrical


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    hmm

    you want to change from a power shower
    to an instantaneous electric shower?


  • Registered Users, Registered Users 2 Posts: 48 detonator1979


    yep just wanted to see was there on that didn't require 10mm or should 10mm be there to start with.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 652 ✭✭✭Just An Opinion


    6sq will be fine once it's not an extensive run, 8.5kw shower will draw around 37amps so protect the cable with a 40amp RCBO.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    are the common triton/mira models 230v/9kw now
    -they are if i recall

    what's the capacity of 6sq t+e for the most common installation methods used here?


  • Registered Users, Registered Users 2 Posts: 652 ✭✭✭Just An Opinion


    M cebee wrote: »
    are the common triton/mira models 230v/9kw now
    -they are if i recall

    what's the capacity of 6sq t+e for the most common installation methods used here?

    Don't have a cable sizing table to hand but on a 9kw unit I'd probably go 10sq under a 45amp RCBO to be safe.


  • Registered Users, Registered Users 2 Posts: 79 ✭✭johnnyryan22


    45 amp rcbo?? seriously?
    6sq on a 40A rcbo. careful who u take advice from........


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    45 amp rcbo?? seriously?
    6sq on a 40A rcbo. careful who u take advice from........

    If it was a 9.5kw shower, you see a problem with a 45 amp RCBO on 10 square?