Vokera Mynute 23 SE not responding to timer

  • 25-01-2013 5:26pm
    #1
    Registered Users, Registered Users 2 Posts: 74 ✭✭


    hi all

    we have a Vokera Mynute 23 SE boiler with a Towerchron QE2 timer and but the boiler does not respond to the timer. I have set up the days and times etc for it to come on but the boiler doesnt start up. The time lloks to be working as the red light ofr heating and hot water come on for the specified times. Do i need to change any settings on the boiler? all i have on the front of it is a dial which goes from 1 to 10. Any help appreciated.

    thanks a mil


Comments

  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Do you mean Vokera 20SE?
    Is it a new clock installed or existing & always working but has developed a fault?


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    nd2no wrote: »
    hi all

    we have a Vokera Mynute 23 SE boiler with a Towerchron QE2 timer and but the boiler does not respond to the timer. I have set up the days and times etc for it to come on but the boiler doesnt start up. The time lloks to be working as the red light ofr heating and hot water come on for the specified times. Do i need to change any settings on the boiler? all i have on the front of it is a dial which goes from 1 to 10. Any help appreciated.

    thanks a mil
    Just had me cousin on the phone with the EXACT same problem!


  • Registered Users, Registered Users 2 Posts: 74 ✭✭nd2no


    i'm not sure about the model there is a sticker on the bottom right "Mynute 24 SE". It was here when I moved in and hasnt worked so I have no background knowledge. I do know its a new boiler but the timer looks a lot older.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    If it has not been in operation for a while, the boiler circulating pump is probably stuck. This will not energise the boiler flow switch and it will not carry out any other ignition process until this is proved.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Are there any power lights on the boiler to signify that the boiler has power?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 74 ✭✭nd2no


    yes the boiler works perfectly when i turn it on manually


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Then it is a timeclock issue & nothing wrong with the boiler.


  • Registered Users, Registered Users 2 Posts: 74 ✭✭nd2no


    is there anything I can do with the timeclock? a factory reset perhaps?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    You could try. There is a reset button on the unit. Are you sure you have it in TMD as the arrow on those can sometimes look like it is pointing to that but is actually misaligned.

    This may help:
    http://www.thermsaver.co.uk/media/pdf/controls/qe1-and-qe2-gb-instructions.pdf