Volkera Mynute 25a, pump continuously running

  • 08-01-2013 01:11AM
    #1
    Registered Users, Registered Users 2 Posts: 1


    Volkera Mynute 25a used in conjunction with heating controls (programmer, 2 room stats, cylinder stat, 3 saute motorised valves). problem = when all zones are off pump continues to run and heat. wired using S plan. Any help would be appreciated. Thanks in advance


Comments

  • Registered Users, Registered Users 2 Posts: 8,560 ✭✭✭K.Flyer


    Volkera Mynute 25a used in conjunction with heating controls (programmer, 2 room stats, cylinder stat, 3 saute motorised valves). problem = when all zones are off pump continues to run and heat. wired using S plan. Any help would be appreciated. Thanks in advance

    Apart from the pump does the boiler keep running and heating as well?

    If it has always been like this since its installation then it has not been wired up correctly.
    If it always worked fine and has just started to behave this way, it is most likely a motorised valve problem.
    Difficult to be certain without looking at it.

    If the zone valves are the newer Sauter model then the electrical connection to the valves are like a usb connector and can be disconnected at the valve. Try un-plugging one at a time to see if the boiler shuts down. The cable connectors to the valve have a little button that you have to push down on in order to disengage them from the valve.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Volkera Mynute 25a used in conjunction with heating controls (programmer, 2 room stats, cylinder stat, 3 saute motorised valves). problem = when all zones are off pump continues to run and heat. wired using S plan. Any help would be appreciated. Thanks in advance

    The 25a is a low voltage/volt free boiler. Your problem is not using separate cables for the 240v circuit and the 12v circuit, i.e. running the cables together to the motorized valves.
    The fix is either run separate cables or use a relay at the boiler.

    If this is not the problem, then you may have a pcb issue.