Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Viessmann Vitotronic 200

  • 27-11-2012 8:19pm
    #1
    Registered Users, Registered Users 2 Posts: 1


    Good evening anybody any advise on setting up a Vitotronic 200 Kw2 as not working correctly. Ony one zone seems to be working.


Advertisement