CS350 Zone Problem

  • 08-11-2012 3:14pm
    #1
    Registered Users, Registered Users 2 Posts: 5


    hi kool kid i have cs350 and im having a problem with a zone there is a back door and 2 windows ive disconnected the sensors and when i bell it out at the panel its a closed circuit i replaced a resistor yesterday and it worked but then last night it showed open zone again any ideas ????? cheers


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    And what is the resistance on that zone if you meter it out now.


  • Registered Users, Registered Users 2 Posts: 5 vavo12


    im not 100% sure should it be 4k7ohms , i have taken the cables out and just put a resistor in the zone and the fault clears, there are two resistors in the circuit what should the reading be then ?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Using duel end off line it will read 4k7 if closed and 9k4 if open.


  • Registered Users, Registered Users 2 Posts: 5 vavo12


    KoolKid wrote: »
    Using duel end off line it will read 4k7 if closed and 9k4 if open.
    Il try that cheers