Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Boiler pressure rising when turned on!

  • 03-11-2012 5:18pm
    #1
    Registered Users, Registered Users 2 Posts: 13


    Hi guys,
    Having an problem with my boiler at the minute. When its turned on the pressure gradually (over a period of about 30 mins) rises by about 1.5 bar. When turned off the pressure slowly drops again. I've set the cold pressure to about .3 bar so at the minute so it stays below 2 bar when hot. Any ideas what is causing this? Its a closed system btw.
    Tagged:


Comments

  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    Raise the presure to 1 bar, vent all rads and recheck and set to 1 bar, test.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Silkwood wrote: »
    Hi guys,
    Having an problem with my boiler at the minute. When its turned on the pressure gradually (over a period of about 30 mins) rises by about 1.5 bar. When turned off the pressure slowly drops again. I've set the cold pressure to about .3 bar so at the minute so it stays below 2 bar when hot. Any ideas what is causing this? Its a closed system btw.
    Your expansion vessel is probably split. Test at the pressure test point to see if water comes out. If just air, it may need re-pressurising but you will need to drain water away from the vessel to test.


  • Registered Users, Registered Users 2 Posts: 13 Silkwood


    I've already vented all the rads, didn't help.


  • Registered Users, Registered Users 2 Posts: 13 Silkwood


    Hi Shane, there was no air in the expansion vessel.. I just got a very slow drop of water coming out.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    The diaphragm in the vessel is split. You will need to replace it. Do not use the heating until this is done as further problems will arise and therefore more cost.
    Replacing the vessel is very simple. Is it gas or oil and is the vessel an integral part of the boiler or is it located externally of the boiler?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 13 Silkwood


    It's a gas boiler. The vessel itself is on the heating pipe into the cylinder, well away from the boiler.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Then it is a job you could do yourself if you feel capable. Drain enough of the system zero pressure & to below the level of the vessel. Unscrew the vessel, use ptfe or hemp & uni-white on the thread of the vessel. Ensure pressure of new vessel is 1.0 bar. Screw on new vessel and refill system to between 1.0 and 1.5 bar pressure. Bleed system, especially the auto air vent at the coil of the cylinder.


  • Registered Users, Registered Users 2 Posts: 13 Silkwood


    Thanks Shane.


Advertisement