Geothermal vs Air to Water vs Oil?

  • 12-10-2012 5:22pm
    #1
    Registered Users, Registered Users 2 Posts: 5


    New build in Galway - next step is heating. Any advice? Obviously trying to worth within a budget...


Comments

  • Users Awaiting Email Confirmation Posts: 280 ✭✭engineermike


    snglovesjb wrote: »
    New build in Galway - next step is heating. Any advice? Obviously trying to worth within a budget...

    Hi,
    a rule of thumb air source - up to 20K, and ground source up to 40 K (+ a bit more if your tapping a water source).
    Oil is the variable however. I spoke to someone last week that is spending €3400 on oil per year?
    ouch :rolleyes:


  • Closed Accounts Posts: 7,410 ✭✭✭bbam


    The big mistakes I've seen with both geothermal and air to water has been the spec of the build.
    I've seen a few where a combination of poor air tightness and badly installed insulation mean that's the heating never gets to heat the space. These systems rely on a slow gradual build up of heat, any heat loss will reduce the build up and if the loss is bad enough the heat never builds up. So ensure if you're installing either of these that your build spec and detailing match it.

    Oil with rads is different as it supply's such a blast of heat the space will heat, but again if the detailing is poor the heat will loose quickly.

    We have oil and rads and burn about 6/700 litres of oil a year to heat a 2700 sq ft story and a half house.

    If your detailing and spec are good it will take very little to heat the house.


  • Closed Accounts Posts: 5,219 ✭✭✭woodoo


    bbam wrote: »

    We have oil and rads and burn about 6/700 litres of oil a year to heat a 2700 sq ft story and a half house.

    If your detailing and spec are good it will take very little to heat the house.

    How do you manage so little oil?


  • Registered Users, Registered Users 2 Posts: 458 ✭✭kboc


    I fear you have missed the boat!

    A PHPP should have been carried out before you started to build. If you have started already!


    In the absence of a PHPP you should have at least;

    HRV
    High degree of airtighness and measures used to ensure this
    insulation
    insulation
    and more insulation

    If you don't have the above, I strongly suspect your money will be wasted on any heat pump (Air, Ground, anything)

    Good luck


  • Registered Users, Registered Users 2 Posts: 5 snglovesjb


    thanks for replays, we have gone with triple glazed, A rated widows, lots in insulation and an airtight house with heat recovery so thinking we should be ok - we don't have a PHPP but confident our builder is on top of this. So thinking air to water might be a good option to look at?


  • Advertisement
  • Closed Accounts Posts: 7,410 ✭✭✭bbam


    woodoo wrote: »
    How do you manage so little oil?

    It's a combination of having the highest standard of insulation you can afford and ensuring the airtight detailing is completed to the highest of standards.

    For example our 1st floor ceilings have 50mm high density insulated slabs under the joists and 300mm of rockwoll above, laid in 2 layers at 90degrees to each other. I have no idea how this compares to current regs but ye effect is great.


  • Registered Users, Registered Users 2 Posts: 126 ✭✭HoofRocks


    Does anyone have a contact for someone who can carry out a PHPP? how much does that roughly cost? Please PM and details

    THanks


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    snglovesjb wrote: »
    thanks for replays, we have gone with triple glazed, A rated widows, lots in insulation and an airtight house with heat recovery so thinking we should be ok - we don't have a PHPP but confident our builder is on top of this. So thinking air to water might be a good option to look at?

    don't think - you should know - we had an excellant building, architect, detail specifier etc etc

    and still there we a few little issues which had to be sorted out on site

    DO NOT assume PHPP or BER will be "ok" unless you have done the maths


  • Registered Users, Registered Users 2 Posts: 73 ✭✭Dcmb1984


    Any update as to what heating system you used. Im in the sketch design of a house myself and Im wondering myself what heating system to fit. Just wondering what system you fitted for a finish. Thanks


  • Registered Users, Registered Users 2 Posts: 2,056 ✭✭✭gooner99


    Dcmb1984 wrote: »
    Any update as to what heating system you used. Im in the sketch design of a house myself and Im wondering myself what heating system to fit. Just wondering what system you fitted for a finish. Thanks

    Can't recommend a particular heat source. But one thing you should consider is what you build your house from and how you use it. If you build block (assuming it's not lined on the inside) it should heat up slowly and lose heat slowly and the thermal mass effect would benefit from the constant heat that underfloor will deliver and underfloor will be best served by a heat pump. If timber frame which will in general heat up quicker and cool down quicker, then oil and rads may work best. Also if your out all day and need quick heat for just a few hours in the evening then oil and rads again may suit best.

    Complying with Part L is the tricky one. Heat pumps should comply on their own, where as oil will need solar or wood "only" stove or maybe both to comply. And from the quotes we've seen on here recently oil installations get expensive when you add solar to the mix. Oil and PV panels are also an option, but again will push up the price. Although with the new agreement on climate change, they may well start to give a feed in rate for the extra electricity.

    Probably the best advice and it's one that will probably be reiterated in later posts is to reduce the heat demand with insulation and air-tightness and after that is sorted you will heat your house quite cheaply regardless of choice. Hell oil then would do on it's own, but alas you need to add something to comply with part L.


  • Advertisement
  • Closed Accounts Posts: 8,722 ✭✭✭nice_guy80


    gooner99 wrote: »
    Can't recommend a particular heat source. But one thing you should consider is what you build your house from and how you use it. If you build block (assuming it's not lined on the inside) it should heat up slowly and lose heat slowly and the thermal mass effect would benefit from the constant heat that underfloor will deliver and underfloor will be best served by a heat pump. If timber frame which will in general heat up quicker and cool down quicker, then oil and rads may work best. Also if your out all day and need quick heat for just a few hours in the evening then oil and rads again may suit best.

    Complying with Part L is the tricky one. Heat pumps should comply on their own, where as oil will need solar or wood "only" stove or maybe both to comply. And from the quotes we've seen on here recently oil installations get expensive when you add solar to the mix. Oil and PV panels are also an option, but again will push up the price. Although with the new agreement on climate change, they may well start to give a feed in rate for the extra electricity.

    Probably the best advice and it's one that will probably be reiterated in later posts is to reduce the heat demand with insulation and air-tightness and after that is sorted you will heat your house quite cheaply regardless of choice. Hell oil then would do on it's own, but alas you need to add something to comply with part L.

    that is ridiculous
    timber houses will hold the heat just as well as a concrete house, once insulated to a good standard


  • Registered Users, Registered Users 2 Posts: 376 ✭✭delfagio


    nice_guy80 wrote:
    that is ridiculous timber houses will hold the heat just as well as a concrete house, once insulated to a good standard


    Plus 1 on that.....

    Timber frame or block build houses once insulated well, and airtightness is extremely good, should retain heat very well and be on par with each other.


  • Registered Users, Registered Users 2 Posts: 2,056 ✭✭✭gooner99


    I wasn't saying they don't hold heat. Actually I'm a fan of timber houses myself. I was saying that blocks can act as a thermal store and therefor hold heat for longer. Of course this is if everything is equal in terms of insulation and air-tightness, which alas is something we know can be hit and miss on block builds.


  • Registered Users, Registered Users 2 Posts: 73 ✭✭Dcmb1984


    Thanks for the reply.
    I plan on having a fully block built house with concrete for the 1st floor. Concrete on first floor is more for sound proof than solely uf heating. I was originally thinking of uf heating do with a air to water heat pump but from reading posts here I'm not so sure now on the air to water. And if I were to go with oil, then the uf wouldn't be ideal either.😠


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    Dcmb1984 wrote: »
    Thanks for the reply.
    I plan on having a fully block built house with concrete for the 1st floor. Concrete on first floor is more for sound proof than solely uf heating. I was originally thinking of uf heating do with a air to water heat pump but from reading posts here I'm not so sure now on the air to water. And if I were to go with oil, then the uf wouldn't be ideal either.😠

    Only time will tell what the right option is. For me it's UFH and A2W.


  • Registered Users, Registered Users 2 Posts: 13,028 ✭✭✭✭Calahonda52


    Dcmb1984 wrote: »
    Thanks for the reply.
    I plan on having a fully block built house with concrete for the 1st floor. Concrete on first floor is more for sound proof than solely uf heating. I was originally thinking of uf heating do with a air to water heat pump but from reading posts here I'm not so sure now on the air to water. And if I were to go with oil, then the uf wouldn't be ideal either.😠


    You might want to look at this thread and especially item number 34 therein.

    heat pumps are based on extracting low temperature, low grade heat [LTLGH] and using the property of the refrigerant, converting the LTLGH into a higher temperature either in the same medium or different, [using electricity to do the necessary work.]
    so from water to water or air to air or air to water and so on.

    The critical factor is how hot is the LTLGH and what temp is required in the receiving medium.

    Clearly going from plus 20 to plus 40 is very effective
    going from minus 20 to plus 60 is madness

    read the thread above and dig out the performance curves

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 376 ✭✭delfagio


    Dcmb1984 wrote:
    Thanks for the reply. I plan on having a fully block built house with concrete for the 1st floor. Concrete on first floor is more for sound proof than solely uf heating. I was originally thinking of uf heating do with a air to water heat pump but from reading posts here I'm not so sure now on the air to water. And if I were to go with oil, then the uf wouldn't be ideal either.ðŸ˜


    Not sure about Air Source Heat Pump as I didn't go this option mainly due to cost. However oil boiler works well with UFH also.Especially condensing oil boiler as its better suited to the low temperatures of UFH.

    UFH with condensing oil boiler your water is heated to approximately 50-60degrees, the water is then mixed with the UFH return pipes to send approximately 30-35 degrees hot water through your UFH circuits.

    I turned on our UFH on Tuesday for first time as we are just moving into our new house. The house is SIP Timber Frame and well insulated and airtight (still to do final airtightness test). But I heated house up to 20degrees upstairs and downstairs. Once it reached the 20degrees in the house I turned the UFH off. It's now Thursday and the house is still 20degrees upstairs and 18.5degrees downstairs. Temperatures outside since Tuesday varied between 6-11degrees.


  • Closed Accounts Posts: 1,186 ✭✭✭stickybookmark


    For me it came down to payback.
    The most expensive to install is Geothermal (which should actually be called GSHP -ground source heat pump- unless it's a vertical collector) but it also results in the lowest bills
    Next up is Air to water, it's cheaper to install than GSHP, but the bills will be higher than GSHP
    And then oil boiler is cheapest to install, but bills will be higher than with either type of heat pump.

    If you were aiming for middle ground - so you have a bit of money to spend upfront, you'd like cheaper bills but you don't want to go for the rolls royce upfront, then A2W jumps out. I think that's why it's so popular - coz it's the middle ground option

    If money upfront is an issue, and it would be easier for you to pay more in bills every year than to come up with the capital now, then oil is the obvious choice


  • Registered Users, Registered Users 2 Posts: 73 ✭✭Dcmb1984


    Thanks for the replys.
    What about a condensing oil boiler, Underfloor heating and a heat recovery system. Hoping to have the house well insulated and air tight.


  • Registered Users, Registered Users 2 Posts: 376 ✭✭delfagio


    Dcmb1984 wrote:
    Thanks for the replys. What about a condensing oil boiler, Underfloor heating and a heat recovery system. Hoping to have the house well insulated and air tight.


    Well heat recovery is pretty much a definite in New builds, there isn't really any sense in not installing one in a new well insulated airtight house. For approximately 5-6k it's the best investment in a new build and typically BER will require it in order to meet the building regulations.

    As I said oil condensing boiler with UFH works very well. This is what we have installed in our house. I myself would be expecting to be using approximately 300-400 Euro a year on oil to heat our house. That's it. It's cheap to install approximately 1000euro for oil and tank, 1200euro for boiler and approximately 500euro to fit and commission.

    Our house tonight is still at 20degrees upstairs and its actually gone from 18.5degrees to 20degrees downstairs today. Still haven't had the heating on since Tuesday morning.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 73 ✭✭Dcmb1984


    Thanks for your help delfagio. Greatly appreciated

    What do you use to heat your water? Since you've had no heating on since Tuesday?


  • Registered Users, Registered Users 2 Posts: 12,823 ✭✭✭✭galwaytt


    Dcmb1984 wrote: »
    Thanks for the reply.
    I plan on having a fully block built house with concrete for the 1st floor. Concrete on first floor is more for sound proof than solely uf heating. I was originally thinking of uf heating do with a air to water heat pump but from reading posts here I'm not so sure now on the air to water. And if I were to go with oil, then the uf wouldn't be ideal either.😠


    There is no need to build blockwork to have either UFH or concrete upstairs - both are possible in a TF system. You can have a very silent timber build if done properly - that's the key.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users, Registered Users 2 Posts: 12,823 ✭✭✭✭galwaytt


    Dcmb1984 wrote: »
    Thanks for the replys.
    What about a condensing oil boiler, Underfloor heating and a heat recovery system. Hoping to have the house well insulated and air tight.

    Good economical choice imho, with proviso the building you put it in is well-built.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users, Registered Users 2 Posts: 376 ✭✭delfagio


    Dcmb1984 wrote:
    Thanks for your help delfagio. Greatly appreciated
    Dcmb1984 wrote:
    What do you use to heat your water? Since you've had no heating on since Tuesday?


    I have solar panel which heat the water


  • Registered Users, Registered Users 2 Posts: 590 ✭✭✭ArraMusha


    I think stickybookmark's post above is a good analysis and good advice for people who are deciding on a heating system in a new build. I'm planning to use a condensing oil boiler, wood stove & pv on a new a build as it is the most appropriate system for our needs. I researched A2W and GSHP and although I like the theory of operation there were a number of items that did not work for us.
    Oil will be on a timer and the stove will override the oil as the main heat source of heat once it comes up to temperature. Longterm timber supply makes this setup practical in our case, even though many people will question the practicality of having to clean out ashes daily and haul in timber. (free exercise IMO)
    As posted above insulation is very important and keeping the envelope airtight is also a must.


  • Registered Users, Registered Users 2 Posts: 862 ✭✭✭tails_naf


    I think the case for A2W and GSHP becomes less favourable when a house is built to a high spec. The paybacks I've seen on these systems have break-even points around 10-15 years in vs oil - and this assume burning approx 1,800 euro of oil per year.

    I have a 3,400 sq ft house, built to a reasonable standard and use 1,500 euro of oil per year on UFH and hot water. The UFH works well as I have a buffer tank so the oil does not cut in an out all day.

    Given one poster already is using 700L of oil a year, the payback for A2W for a house of such a high spec would be probably never.

    That said, I do like the idea of A2W from a green point of view and if money was not a major factor would probably go with it. However, being practical, at todays prices for a well insulated house it does not make sense to me.


  • Registered Users, Registered Users 2 Posts: 220 ✭✭Wegian


    tails_naf wrote: »
    I think the case for A2W and GSHP becomes less favourable when a house is built to a high spec. The paybacks I've seen on these systems have break-even points around 10-15 years in vs oil - and this assume burning approx 1,800 euro of oil per year.

    I have a 3,400 sq ft house, built to a reasonable standard and use 1,500 euro of oil per year on UFH and hot water. The UFH works well as I have a buffer tank so the oil does not cut in an out all day.

    Given one poster already is using 700L of oil a year, the payback for A2W for a house of such a high spec would be probably never.

    That said, I do like the idea of A2W from a green point of view and if money was not a major factor would probably go with it. However, being practical, at todays prices for a well insulated house it does not make sense to me.


    I would agree with all of the above but the main thing that is catching people (like me) out is compliance to Part L Regulations. Once you add up the technology you need to invest in to meet the Part L, the Air to Water is about as cost effective as the alternatives


  • Closed Accounts Posts: 1,186 ✭✭✭stickybookmark


    Wegian wrote: »
    I would agree with all of the above but the main thing that is catching people (like me) out is compliance to Part L Regulations. Once you add up the technology you need to invest in to meet the Part L, the Air to Water is about as cost effective as the alternatives

    So in other words if you go for an oil boiler, you have to put in solar panels?


  • Registered Users, Registered Users 2 Posts: 220 ✭✭Wegian


    So in other words if you go for an oil boiler, you have to put in solar panels?

    Yes, or PV, or something else to bring up your Renewables contribution. You would also need to offset your Carbon Co-Efficient somehow


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Its actually harder than that - if you house is super insulated then you will find it hard to "find" the 4kwh/m2/annum needed to meet part L

    in a passive house we only fitted PV so as to comply with Part L - we have a HP (which provides "some renewable") and we have a timber only stove (more "renewables") - but this was not enough

    Funny but true - if we "lost" our passive window cert and reverted to the DEAP defaults then our build would have complied without the PV - the conundrum which is DEAP


  • Registered Users, Registered Users 2 Posts: 12,823 ✭✭✭✭galwaytt


    fclauson wrote: »
    Its actually harder than that - if you house is super insulated then you will find it hard to "find" the 4kwh/m2/annum needed to meet part L

    in a passive house we only fitted PV so as to comply with Part L - we have a HP (which provides "some renewable") and we have a timber only stove (more "renewables") - but this was not enough

    Funny but true - if we "lost" our passive window cert and reverted to the DEAP defaults then our build would have complied without the PV - the conundrum which is DEAP

    "Conundrum" ? You're being too polite - it's completely unfit for purpose.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users, Registered Users 2 Posts: 26 Landys


    galwaytt wrote: »
    "Conundrum" ? You're being too polite - it's completely unfit for purpose.

    Find this thread very interesting....and agree with the illogical situation everyone seems to find themselves in when trying to comply with Part L. more we insulate and get air tight the harder to comply !! We were going to go geo thermal but ,due to initial cost , payback time ,have changed to oil, wood burning stove, heat recovery and need PV or solar panels to comply ..... Also came across these new thermostat dynamic solar units .....which seem to be a cross between PV and small air to water unit....slightly more expensive than PV but guaranteed hot water 365 days of year....just wondering has anyone used them and how do they perform...?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Landys wrote: »
    Find this thread very interesting....and agree with the illogical situation everyone seems to find themselves in when trying to comply with Part L. more we insulate and get air tight the harder to comply !! We were going to go geo thermal but ,due to initial cost , payback time ,have changed to oil, wood burning stove, heat recovery and need PV or solar panels to comply ..... Also came across these new thermostat dynamic solar units .....which seem to be a cross between PV and small air to water unit....slightly more expensive than PV but guaranteed hot water 365 days of year....just wondering has anyone used them and how do they perform...?

    I think oil is poor choice for the following reasons - a well insulated build needs very little heat BUT it needs it regularly - my HP will run for 1 to 2 hrs at night when it's cold (driven by outside air temp) - and delivers water at 28c when 0c - oil does not do this well

    Also remember I got 0.2kwh from a 4kwp array Christmas Day - last year I got 7kwh (enough to cook turkey) - so think again before your final decision


  • Registered Users, Registered Users 2 Posts: 458 ✭✭kboc


    I am with fclauson on this. I think almost regardless what way the house is built heat pump is way to go.
    The biggest expense is the initial infrastructural cost, e.g. Loops in ground, insulated pipes from the machine into house etc, etc. These are once off. In years to come you can change the machine or get parts for it. These are dependent that a cowboy did not install the system!
    If the government bring in something like is in the UK, grants for installing and further yearly money for having the system in your house, this will definely change the goal posts.
    I can't see how anybody can really really give oil a go with the alternatives available. Oil was a goer when you could buy it for single pennies per litre and there was no other way of heating a house conveniently. This was in the 70s and 80s, not now.
    B

    I have a gshp in my house. It is easily the best decision I made. It has been working since winter 2011 and has easily paid for itself in that short time. It offers so much more than any other heating system. For example, Unexpectedly, in a good way, I am selling my house in 14 months time (building another one) the hp has added a completely different selling point to my house now.


    I just can't see why not. I don't say this blindly, as I put many hours of research into this before I started to build. If it didn't pay its way it was not going into my house.

    Go for it.


  • Registered Users, Registered Users 2 Posts: 13,028 ✭✭✭✭Calahonda52


    kboc wrote: »

    ....I have a gshp in my house. It is easily the best decision I made. It has been working since winter 2011 and has easily paid for itself in that short time. .....


    My underline

    Can u provide the math behind this please.

    Its not for a moment that I am doubting you its just I am assuming say a 25k euro initial spend and u are saying you got that back in 4 years.
    I spend about 2,400 euro pa on gas and elec in a leaky '70s house.........

    “I can’t pay my staff or mortgage with instagram likes”.



  • Advertisement
  • Closed Accounts Posts: 8,722 ✭✭✭nice_guy80


    kboc wrote: »
    I am with fclauson on this. I think almost regardless what way the house is built heat pump is way to go.
    The biggest expense is the initial infrastructural cost, e.g. Loops in ground, insulated pipes from the machine into house etc, etc. These are once off. In years to come you can change the machine or get parts for it. These are dependent that a cowboy did not install the system!
    If the government bring in something like is in the UK, grants for installing and further yearly money for having the system in your house, this will definely change the goal posts.
    I can't see how anybody can really really give oil a go with the alternatives available. Oil was a goer when you could buy it for single pennies per litre and there was no other way of heating a house conveniently. This was in the 70s and 80s, not now.
    B

    I have a gshp in my house. It is easily the best decision I made. It has been working since winter 2011 and has easily paid for itself in that short time. It offers so much more than any other heating system. For example, Unexpectedly, in a good way, I am selling my house in 14 months time (building another one) the hp has added a completely different selling point to my house now.


    I just can't see why not. I don't say this blindly, as I put many hours of research into this before I started to build. If it didn't pay its way it was not going into my house.

    Go for it.
    have you solar PV and selling it back to the ESB?


  • Registered Users, Registered Users 2 Posts: 26 Landys


    all

    thanks for the feedback. it was my understanding from the earlier posts that a lot of people were choosing gas and oil instead of geothermal....I have nothing against geothermal but it will cost an extra 15/20k to install and with the electricity bills I have seen from users its difficult to see how it would pay for itself in the short terms --surprised it could pay for it self in 4 years ??

    as no incentives available now for installation even if something introduced presume it wont be retrospective and was not aware there was some annual incentive in UK as mentioned in previous post ?

    I accept any house needs a regular input of heat , but if insulated well and warm all evening a short boost of oil during night should keep warm and this should not add to too much expenses..........

    like I say absoloutley nothing against Geothermal other than the initial outlay and ability to pay for itself....

    is there no experience of the solar PV panel I mentioned ?


  • Registered Users, Registered Users 2 Posts: 458 ✭✭kboc


    My underline

    Can u provide the math behind this please.

    Its not for a moment that I am doubting you its just I am assuming say a 25k euro initial spend and u are saying you got that back in 4 years.
    I spend about 2,400 euro pa on gas and elec in a leaky '70s house.........

    Mar - Apr and Sept - Oct (4 months)

    On average it takes 3 hours to heat house and 1 hour to heat hot water. 4 hours in total per night.
    1 hour = 3 units of elec. So, 4 hours per night = 12 units of elec.
    12 units of elec = £0.075 x 12 = £0.90 cost per night.
    there is 122 days in these 4 months.
    total cost for these months = £0.90 x 122 = £109.80

    May - Aug

    No heat requirement. 1 hour to heat hot water.
    1 hour = 3 units of elec.
    1 unit of elec = £0.075 x 1 = £0.075 cost per night.
    there is 123 days in these 4 months.
    total cost for these months = £0.075 x 123 = £9.225

    Nov - Feb

    On average it takes 8 hours to heat house and 1 hour to heat hot water. 9 hours in total per night, broken up into 7 hours off peak elec (£0.075/unit) and 2 hours full rate elec (£0.15/unit)
    1 hour = 3 units of elec. So, 8 hours per night = 24 units of elec. Broken up into 7 units off peak and 2 hours full price
    Off peak:
    21 units of elec (7 hours x 3 units/hour) = £0.075 x 21 = £1.575
    On peak:
    6 units of elec (2 hour x 3 units/hour) = £0.15 x 6 = £0.90
    total cost of the 2 rates above is £1.575 + £0.90 = £2.475
    there is 120 days in these 4 months.
    total cost for these months = £2.475 x 120 = £297

    The total of all of the above is:
    £109.80 + £9.225 + £297 = £416.025

    Around £1.13/day to heat my house and provide hot water.


    I am part of the RHI scheme by the NI government. As part of this scheme I have received a £3000 lump sum and a yearly amount of £1878.38 for 7 years. I received the first payment this month, Dec 2015.

    As part of this scheme an energy ass had to be done of my house. the assessor predicted through their model that my house would use £2,500 p.a. in oil.

    So how have I got my money back?

    I am in the house 4 years and 9 months = 4.75 years.

    Oil would have cost me £2,500 x 4.75 = £11,875
    The OFCH would have cost approx £1000.

    Potential total for oil to date = £12,875.

    GSHP has cost me £416.025 x 4.75 = £1,976.1187 approx £1,976.12
    The GSHP did cost me £12,000.

    Total for GSHP to date = £13,976.12
    Subtract £3,000 lump sum and £1878.38
    This gives a new figure of £9,097.74

    As part of the RHI scheme I will get a six further payments of £1878.38.
    so £1878.38 x 6 = £11,269.80, to come off further down the line. Actually by the time the RHI scheme is finished I will have received £3,000 + (£1878.38 x 7) £13,148.66 = £16, 148.88 in total.

    As it stands right now, I am better off to the tune of (£12,875 - £9,097.74) £3,777.26 by having GSHP rather than OFCH.


  • Registered Users, Registered Users 2 Posts: 862 ✭✭✭tails_naf


    kboc wrote: »
    Mar - Apr and Sept - Oct (4 months)

    The total of all of the above is:
    £109.80 + £9.225 + £297 = £416.025

    Around £1.13/day to heat my house and provide hot water.

    <snip>

    Oil would have cost me £2,500 x 4.75 = £11,875

    Taking into account the cost of a unit of power (Oil vs Elec) and COP efficiency of heat pumps, the cost of heat is approx 2x to 3x less for a heat pump vs oil. Given you pay £416 a year for the GSHP, it would suggest your costs if you had used oil would be between £800 and £1200 a year, and nowhere near £2500.

    That said, the cost you paid for the GSHP, and the govt scheme does make it much more attractive, however the economics are still favour the oil (slightly).


  • Registered Users, Registered Users 2 Posts: 458 ✭✭kboc


    tails_naf wrote: »
    Taking into account the cost of a unit of power (Oil vs Elec) and COP efficiency of heat pumps, the cost of heat is approx 2x to 3x less for a heat pump vs oil. Given you pay £416 a year for the GSHP, it would suggest your costs if you had used oil would be between £800 and £1200 a year, and nowhere near £2500.

    That said, the cost you paid for the GSHP, and the govt scheme does make it much more attractive, however the economics are still favour the oil (slightly).

    From my previous post:

    "As part of this scheme an energy ass had to be done of my house. the assessor predicted through their model that my house would use £2,500 p.a. in oil."

    I didn't model this, I don't know what the energy assessor did (but it is certified by some over arcing English/European body), that is the figure the certificate gives me. So I take it on face value. I am not sure where you get £1200 from? In the absence of me ever having an OFCH in the house, I have to take the energy assessor on his professional view point.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 862 ✭✭✭tails_naf


    kboc wrote: »
    From my previous post:

    "As part of this scheme an energy ass had to be done of my house. the assessor predicted through their model that my house would use £2,500 p.a. in oil."

    I didn't model this, I don't know what the energy assessor did (but it is certified by some over arcing English/European body), that is the figure the certificate gives me. So I take it on face value. I am not sure where you get £1200 from? In the absence of me ever having an OFCH in the house, I have to take the energy assessor on his professional view point.

    1200 came from multiplying what you spend on electric by 3. A unit of energy is the same no matter the source in terms of how it will heat your house - the only difference is the cost of that unit. Dividing the cost of a unit of electricity by the heat pump cop gives the cost of a unit of heat from it. I was estimating the ratio between this and oil to be 3x. 2500 vs 400 would put this factor at over 6x. I have never heard of a factor this large, which would suggest the 2500 estimate to be too big.