Ecoflam burner keeps running

  • 10-10-2012 7:51pm
    #1
    Registered Users, Registered Users 2 Posts: 21


    Hi all im renting a 7 bedroom house and recently had he boiler serviced its a heat age 60/90 with an ecoflam burner,it heats the water an rads at the same time the problem is that it seems to keep running,the house has no thermostat or motorised valves there is a thermostat on the boiler,the house has 17 radiators and it is just drinking my oil,help needed


Comments

  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    If it started after the service its possible it got too small a nozzle fitted or hasn't been set up correctly, did you get a service report and print out from his flue gas anyliser ???


  • Registered Users, Registered Users 2 Posts: 3,990 ✭✭✭jimf


    is the thermostat on boiler cutting out at set temp is the boiler short cycling
    {cutting on and off frequently} or have you noticed
    is the heavy oil consumption the reason you had it serviced did u get fga print out
    on service completion


  • Registered Users, Registered Users 2 Posts: 3,990 ✭✭✭jimf


    sorry billy we posted almost together i must look like a parrot some of my
    points are the same as yours


  • Registered Users, Registered Users 2 Posts: 21 Reddevilman


    The guy who serviced it took the printout to the landlord,the boiler doesnt cut out at all once its switched on it stays on,i have the stat on the boiler set to 65degrees when i turn the stat down it doesnt switch off until i turn it down to about the 40 degree mark


  • Registered Users, Registered Users 2 Posts: 3,990 ✭✭✭jimf


    this means whoever serviced your boiler didnt bother to check the thermostat was
    working correctly on your boiler and in my opinion is not very competent fga prinout or not you never leave a boiler without checking on/off operation of stat maybe he did at a very low temp but then fga would not be accurate from your post above your boiler is struggling to get up to temp and as billy pointed out may be grossly downrated


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 21 Reddevilman


    Phoned the landlord this morning and told him all you said,he is sending a new guy out this tomorrow morning so will keep you posted.