wall thermostat for electric storage heater

  • 24-09-2012 11:20am
    #1
    Registered Users, Registered Users 2 Posts: 764 ✭✭✭


    I want to connect a room thermostat to my storage heater so that it turns off when the room reaches the desired temperature. (I know that the storage heater will only be live at night)

    The storage heater is a Creda TSR24MW 3.4KW Manual, so what current rating does the room stat need to be?
    I'm looking at a basic dial thermostat that can handle 15a....would that be suitable?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Normally thermostats only switch small loads.
    In this case I would reccomend that you use the thermostat to switch a contactor that in turn switches the storage heater that you intend to control.

    The load in this case is about 15A.
    I always use a larger contactor than required as this extends the life of the unit and increases overall reliability.
    So I would suggest using a 20 or 25A contactor.

    Connections should always be tight!


  • Registered Users, Registered Users 2 Posts: 764 ✭✭✭buzz11


    Excellent, thanks for that.

    Its just one heater in a room so I'm hoping it will prevent the massive overheating that comes with predicting Irish weather


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    No bother.

    Remember: The stat should be protected by a suitabely rated MCB. So if the stat is rated to switch 6A then the MCB should be rated for no more than 6A.

    Working on a distribution board and making a modification such as this should only be done by a qualified electrician IMHO.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    that was the old method of adjusting the input to heaters
    .stat and contactor

    -im not certain that a room stat will regulate the input correctly on a storage heater as you envisage


  • Site Banned Posts: 957 ✭✭✭leeomurchu


    M cebee wrote: »
    that was the old method of adjusting the input to heaters
    .stat and contactor

    -im not certain that a room stat will regulate the input correctly on a storage heater as you envisage

    Agree storage heaters aren't a very precise form of heating a room perhaps a time clock on the heater might be a better idea.

    Have storage heaters not got a built in stat anyway?


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the devireg will adjust the input to the weather outside
    im not sure that a room stat will work well


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    As stated above, on off control such as the OP is suggestion will not work well with storage heaters.

    For example:
    Say the room stat has a set point is 20 DegC.
    Although the stat will switch off the heater when it registers this 20 DegC the heater will continue to emit heat after it is switched off, which could raise the room temperature to a peak of say 25 DegC. Eventually the room will cool and the stat will "call" for heat again once it registers a temperature of less than 20 DegC. When this happens the heater will be switched on once more. However it can take quite some time for the heater to emit heat once more to the point that the room temperature starts to increase (due to the large time constant of storage heaters). During this lag time the room may cool to 15 DegC. So despite the fact that the desired room temperature is 20 DegC the actual temperature may fluctuate either side of this from 10 to 25 DegC.
    This is illustrated on the graph below.

    A time clock is not going to help this situation at all as the temperature will still overshoot and undershoot the set point.

    If this were an industrial application that had to use storage heaters and these fluctuations had to be eliminated a PI or PID type controller may well be used.


    Despite the fact that this on off control is very crude, some control is better than none.

    My experience with storage heaters has always been very negative. They are always expensive to run and the end user is always too hot or too cold. If they were mine I would bin them.


    On-OFF_control.gif


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    the devireg will adjust the input to the weather outside
    im not sure that a room stat will work well

    Room stat wont work properly at all. All that can be done is regulate the input to the storage heater, through a stat in the heater, or outside temp stat probably.

    It has to be sort of predicted what the weather/temperature will be like the next day, to even decide if the heater will be required, so controlling it with a room stat is a waste of time and effort.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    As stated above, on off control such as the OP is suggestion will not work well with storage heaters.

    For example:
    Say the room stat has a set point is 20 DegC.
    Although the stat will switch off the heater when it registers this 20 DegC the heater will continue to emit heat after it is switched off, which could raise the room temperature to a peak of say 25 DegC. Eventually the room will cool and the stat will "call" for heat again once it registers a temperature of less than 20 DegC. When this happens the heater will be switched on once more. However it can take quite some time for the heater to emit heat once more to the point that the room temperature starts to increase (due to the large time constant of storage heaters). During this lag time the room may cool to 15 DegC. So despite the fact that the desired room temperature is 20 DegC the actual temperature may fluctuate either side of this from 10 to 25 DegC.
    This is illustrated on the graph below.

    A time clock is not going to help this situation at all as the temperature will still overshoot and undershoot the set point.

    If this were an industrial application that had to use storage heaters and these fluctuations had to be eliminated a PI or PID type controller may well be used.


    Despite the fact that this on off control is very crude, some control is better than none.
    None of that works with storage heaters. They are designed to heat up but retain their heat at night, and release during the day, so the room stat will not work properly at all.

    Temperatures overshooting set points applies to real time heating. A storage heater is supposed to be able to regulate the heat being released, well after the electrical input has ceased, and this cant be regulated by a room stat, only by mechanical means.

    A time clock will actually work better, as it can be timed to come on at 4am and off at 9am as an example, to enable the storage heater to heat to around half capacity etc.

    But that also is crude. Storage heaters themselves are crude, their main intention being to even out the base load generated over 24 hours.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    None of that works with storage heaters.
    +1
    As I said: My experience with storage heaters has always been very negative. They are always expensive to run and the end user is always too hot or too cold. If they were mine I would bin them.
    They are designed to heat up but retain their heat at night, and release during the day
    In theory they are yes, in reality things work quite differently.
    Storage heaters themselves are crude, their main intention being to even out the base load generated over 24 hours.
    +1
    But they never deliver this.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    +1
    As I said: My experience with storage heaters has always been very negative. They are always expensive to run and the end user is always too hot or too cold. If they were mine I would bin them.


    In theory they are yes, in reality things work quite differently.


    +1
    But they never deliver this.

    Indeed


  • Registered Users, Registered Users 2 Posts: 764 ✭✭✭buzz11


    I agree with above observations about storage heaters, they appear to be designed for 'consistent' climates where it might stay below/near freezing all winter.

    Anyhow my purpose with the room stat is to crudely eliminate room-overheating which is a regular event, but with heat emmission from the storage heater being so delayed and limits by night clock, I don't know how it will work in reality.

    The application is an office so people rarely check the settings, except to turn them to max when a few days are cold, then when mild weather comes nobody turns down the controls and the place overheats. This overheating is what I hope the room stat may reduce.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Perhaps the simplest solution is to replace the storage heaters with panel heaters.

    The stat will not help you maintain a set point during the day as the supply to the heater will be off.

    However panel heaters can be powered on during the day and if controlled by a stat can provide reasonable temperature control. Panel heaters are also available with built in timers, so you can ensure that they are off during the hours that the office is empty.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    Perhaps the simplest solution is to replace the storage heaters with panel heaters.

    The stat will not help you maintain a set point during the day as the supply to the heater will be off.

    However panel heaters can be powered on during the day and if controlled by a stat can provide reasonable temperature control. Panel heaters are also available with built in timers, so you can ensure that they are off during the hours that the office is empty.


    prob not for office hours

    storage would be cheaper and better than panel heating

    a timer will be ok as robbie said -set for the end of the off peak period

    if i recall the devireg also outputs similarly at the end of the off-peak period
    http://www.devi.co.nz/index.cfm/3,124,350/710.pdf


  • Site Banned Posts: 957 ✭✭✭leeomurchu


    Eh hmmm did I not say time clock :D:)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    storage would be cheaper and better than panel heating
    It would be cheaper in terms of each unit of electricity costs less.
    But what I have found is that the storage heaters give out quite a bit of heat when powered up i.e at night when nobody is present. Then when the power is off they give out all of the stored heat too quickly. After lunch time they are cold. Messing around with the dampers helps, but not much.

    I have found that they dump so much of their heat in the morning that people open windows to cool down. After lunch they either freeze or plug in/switch on other heaters at peak rate. This can negate any saving made by using the off peak rate to heat the storage heater.

    Perhaps other people have had better experiences than me.

    This is why I would prefer to use a panel heaters. Although they may be using peak rate electricity the control is so much better that savings can be made.
    a timer will be ok as robbie said -set for the end of the off peak period
    Yes, I see what he is trying to achieve but this is about using a timer to save money rather than to keep the temperature at a set point.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Yes, I see what he is trying to achieve but this is about using a timer to save money rather than to keep the temperature at a set point.

    The less heat put into the storage heater blocks, the less hot the room being heated will likely be.

    It will do the same thing as the input stat really, except it could control more than one heater.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    On-OFF_control.gif

    The on/off square wave needs to move a quarter wavelength to the right in that diagram imo, or does it?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    The on/off square wave needs to move a quarter wavelength to the right in that diagram imo, or does it?

    No, the diagram is accurate.

    Remember the room temperature continue to increase for a time after the electrical supply is switched off.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    The less heat put into the storage heater blocks, the less hot the room being heated will likely be.
    True.

    Less heat into the storage blocks could be an issue on very cold days as it could mean that the room never gets to the desired temperature.
    It will do the same thing as the input stat really, except it could control more than one heater.
    Not really.
    A stat takes ambient temperature into account which ensures that the supply to the heater will only be switched on when the ambient temperature is below the set point.

    On the other hand the timer will switch the power on to the heater at the appropriate time regardless of the temperature.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    No, the diagram is accurate.

    Remember the room temperature continue to increase for a time after the electrical supply is switched off.

    The diagram shows the stat going on and off at exactly the same temp, which is a problem for stats. They need a hysteresis setup, something inherent in mechanical stats, or they could rapidly switch on and off at the set point,.

    If that diagram is correct, then none exists for the stat or stats the diagram is based on.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    The diagram shows the stat going on and off at exactly the same temp, which is a problem for stats. They need a hysteresis setup, something inherent in mechanical stats, or they could rapidly switch on and off at the set point,.

    You are correct, stats are designed (and do) have an amount of hysteresis for the reason you stated.

    However I think that the diagram should be taken for what it is: A basic sketch of a graph that is designed to illustrate the limitations of on/off control.
    A more detailed graph should show exactly what you are saying.
    You could also argue that it is highly unlikely that the temperature would rise at exactly the same rate that it would fall, so the graph is inaccurate from that aspect as well :D

    When I said that the diagram was correct it was in response to your post stating that:
    The on/off square wave needs to move a quarter wavelength to the right in that diagram imo, or does it?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »

    When I said that the diagram was correct it was in response to your post stating that:
    he on/off square wave needs to move a quarter wavelength to the right in that diagram imo, or does it?
    If the on/off part was moved to the right, that would then show a hysteresis in the stat. Off would be just above set point, and on would be just below it.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »


    Not really.
    A stat takes ambient temperature into account which ensures that the supply to the heater will only be switched on when the ambient temperature is below the set point.

    On the other hand the timer will switch the power on to the heater at the appropriate time regardless of the temperature.

    Do the same as the input stat in terms of varying the on to off time during charging. I think everyone on boards knows how a stat works compared to a timeclock.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    If the on/off part was moved to the right, that would then show a hysteresis in the stat. Off would be just above set point, and on would be just below it.

    If you moved the "on/off square wave needs a quarter wavelength to the right" as you suggested the graph would be incorrect.

    It would incorrectly show that once the stats switches off the temperature immediately stops increasing. It would also show that once the stat switches the supply back on the temperature immediately stops dropping, again this is incorrect.

    I would think that the purpose of the graph is to demonstrate the limitations of on/off control.


  • Site Banned Posts: 957 ✭✭✭leeomurchu


    Goin around in a nice big circle there lads :eek:


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    leeomurchu wrote: »
    Goin around in a nice big circle there lads :eek:
    Yeah, you are right. I'm off to my bed :)

    Summary:
    1) Don't use storage heaters or expect good control from them with a stat and/or time clock.

    2) Don't use crude graphs to illustrate a point :D:D


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    leeomurchu wrote: »
    Goin around in a nice big circle there lads :eek:

    This is war. Get out now or become collateral damage:)


  • Site Banned Posts: 957 ✭✭✭leeomurchu


    robbie7730 wrote: »
    This is war. Get out now or become collateral damage:)

    Feck that I'm takin me ball and goin home, good luck :D


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    leeomurchu wrote: »
    Feck that I'm takin me ball and goin home, good luck :D

    :D


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    True.

    Less heat into the storage blocks could be an issue on very cold days as it could mean that the room never gets to the desired temperature.


    Not really.
    A stat takes ambient temperature into account which ensures that the supply to the heater will only be switched on when the ambient temperature is below the set point.

    On the other hand the timer will switch the power on to the heater at the appropriate time regardless of the temperature.

    timer or input stat can adjust stored heat similarly




    www.fenixgroup.cz/pages/en/products/storage-heaters/other-technical-information/regulation-storage-heaters

    good link there


    "Storage heaters (dynamic as well as static) are therefore equipped with what is known as a charge control thermostat. Using this, the temperature to which the core temperature is heated when charging can be limited"

    also describes the thermostatic control of 'output' for comfort