    In an older house, old type fuseboard, if you were to install a 9.5kw electric shower with 40a RCBO, should the mains tails need to be changed from 10sq?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,655 Mod ✭✭✭✭2011


    In an older house, old type fuseboard, if you were to install a 9.5kw electric shower with 40a RCBO, should the mains tails need to be changed from 10sq?
    Yes. They should be a minimum of 16 sq. mm.

    I would recommend that you change the distribution board also.