Motorised valve question

  • 01-08-2012 7:01pm
    #1
    Registered Users, Registered Users 2 Posts: 523 ✭✭✭


    I have installed a few of motorised valves to 'zone' the heating system in the house. While I was re-introducing the water to the system after draining it I had the valves in turn actuated by means of a 13a plug which worked out fine. So then I connected the valves to the controls and 2 of them are working fine but when the other one gets actuated the RCD in the fuse board tripps out:confused: Re-connect it via the 13a plug and it works fine.

    Any ideas?
    The valve in question is rated to 3a.


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Mugser wrote: »
    I have installed a few of motorised valves to 'zone' the heating system in the house. While I was re-introducing the water to the system after draining it I had the valves in turn actuated by means of a 13a plug which worked out fine. So then I connected the valves to the controls and 2 of them are working fine but when the other one gets actuated the RCD in the fuse board tripps out:confused: Re-connect it via the 13a plug and it works fine.

    Any ideas?
    The valve in question is rated to 3a.
    You may have the neutral mixed up.

    Remember if the live is fed via the RCD the corresponding neutral has to be fed through the same RCD.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    quickly confirm the actuator is fine by swapping the connections of an other actuator
    this will confirm whether the wiring or valve is the problem

    (there may be no rcd protection on the socket circuit you done a temporary on )


  • Registered Users, Registered Users 2 Posts: 523 ✭✭✭Mugser


    2011 wrote: »
    You may have the neutral mixed up.

    Remember if the live is fed via the RCD the corresponding neutral has to be fed through the same RCD.

    Nope, the polarity is definitely correct, I'm thinking maybe that 2 valves might too much of a load on the controller. Will probably stick in a wee contactor to do the job.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Mugser wrote: »
    I'm thinking maybe that 2 valves might too much of a load on the controller.

    doubtful
    you should use the auxiliary contacts on the valve to switch boiler on/off


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Mugser wrote: »
    Nope, the polarity is definitely correct, I'm thinking maybe that 2 valves might too much of a load on the controller. Will probably stick in a wee contactor to do the job.

    Its not about polarity though. Its about having both the live and neutral that is supplying the valve, through the (same) rcd. If only live is through it, or only neutral, or the neutral is connected to an earth, then the RCD will tripwhen the valve motor is energised . Reversing the valve 230v supply polarity wouldnt cause it.

    If the valve has an earth fault, then it would trip the RCD when you plug it in, unless the socket you are using is not through an RCD itself.

    The load on the control setup wouldnt have any bearing either if connections through an RCD are correct.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 523 ✭✭✭Mugser


    Major blonde moment:o:o:o:o:o:o:o
    Netral connected to the incorrect rail:o:o:o:o


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Mugser wrote: »
    Major blonde moment:o:o:o:o:o:o:o
    Netral connected to the incorrect rail:o:o:o:o

    we have all done it;)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    meercat wrote: »
    we have all done it;)
    Affirmative ! :D


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    meercat wrote: »
    doubtful
    you should use the auxiliary contacts on the valve to switch boiler on/off
    Exactly


  • Closed Accounts Posts: 54 ✭✭rum and coke


    Mugser wrote: »
    Major blonde moment:o:o:o:o:o:o:o
    Netral connected to the incorrect rail:o:o:o:o

    Guilty