Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Dampness in cavity wall help

  • 04-06-2012 7:55pm
    #1
    Closed Accounts Posts: 132 ✭✭


    The house is built 15 years to specifications at the time, there is sheets of insulation 60mm thick and 40mm empty space in the cavity wall.
    There are no leaks but there is a slight dampness above the damp coarse on the outer wall in the cavity
    Could this be caused by condensation or any other reason?

    Thank you.


Comments

  • Closed Accounts Posts: 37 BE_MIEI


    Is the external ground level at least 150mm below the DPC level? Is there any dampness evident internally by the way?


  • Closed Accounts Posts: 132 ✭✭ow9654


    Yes the external ground level is 150mm below the DPC level.
    There is absolutely no internal dampness.
    Why I investigated the dampness was because there is some efflorescence salts on the outside wall which is pushing some paint off.
    Thanks


  • Closed Accounts Posts: 37 BE_MIEI


    If there is no dampness evident internally, I would say that that the wall is doing its job in keeping the moisture out. It sounds like there could be some latent defect causing the wall to take in water. Is the problem throughout the house or located specifically in certain areas, for example under windows?


  • Closed Accounts Posts: 132 ✭✭ow9654


    The dampness may have started 2ft under windowsill but now has spread to between windows and down to the top of the damp coarse at the back of the house only.
    But the groove under the windowsill is clear.


  • Closed Accounts Posts: 37 BE_MIEI


    The DPC could be missing from beneath the window sill allowing water to penetrate into the wall. You should be able to check this yourself. The DPC should be just about visible protruding slightly from the wall at the underside of the window sill.


  • Advertisement
  • Closed Accounts Posts: 132 ✭✭ow9654


    Thank you for your help,
    But I still don`t understand how it would be damp in the cavity above the damp coarse, could this possibly be condensation?
    Thank you.


  • Closed Accounts Posts: 7,410 ✭✭✭bbam


    I'd say poor detailing at the window sills is allowing rain water into the cavity rather than shielding it out. There may be no DPC, poorly fitted one or it may even have been punctured laying the sill in place.
    The water is exiting the cavity at the DPC level.


Advertisement