    Got an extension built a couple of years ago and the builders only put in a extractor fan in the bathroom now the motor is gone on it, just wondering if I put a vent in the wall plus if I take out the extractor fan an got a vent for the roof tile and ran it from the roof to the ceiling would that be alright, the shower is used 3 or 4 times a week.

    spud65


Comments

  • Registered Users, Registered Users 2 Posts: 1,473 ✭✭✭tred


    spud65 wrote: »
    Got an extension built a couple of years ago and the builders only put in a extractor fan in the bathroom now the motor is gone on it, just wondering if I put a vent in the wall plus if I take out the extractor fan an got a vent for the roof tile and ran it from the roof to the ceiling would that be alright, the shower is used 3 or 4 times a week.

    spud65

    Must be missing something, why dont you just replace the extractor. Probably a cheap one installed by builder.


  • Registered Users, Registered Users 2 Posts: 116 ✭✭spud65


    if the vents will do the the job that will be sound, saves me having to replace/install a new one every few years.


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    spud, small suggestion - get an extractor fan that is connected to a humidity sensor instead of the usual light or pulley option


  • Registered Users, Registered Users 2 Posts: 1,516 ✭✭✭Maudi


    spud65 wrote: »
    if the vents will do the the job that will be sound, saves me having to replace/install a new one every few years.
    id replace the the fan...a vent only opening is fine for a bedroom where its just static air flowing back and forth...but the extractor fan is essential to take out moisture laden air from shower steam...


  • Registered Users, Registered Users 2 Posts: 116 ✭✭spud65


    BryanF wrote: »
    spud, small suggestion - get an extractor fan that is connected to a humidity sensor instead of the usual light or pulley option

    any suggestions on which type to put in?


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    pm sent


  • Registered Users, Registered Users 2 Posts: 116 ✭✭spud65


    Maudi wrote: »
    id replace the the fan...a vent only opening is fine for a bedroom where its just static air flowing back and forth...but the extractor fan is essential to take out moisture laden air from shower steam...

    thanks maudi
    very useful info, always thought just the vents were ok, now i have to get a fan for upstairs bathroom


  • Registered Users, Registered Users 2 Posts: 116 ✭✭spud65


    BryanF wrote: »
    pm sent

    thanks a mill BryanF


  • Registered Users, Registered Users 2 Posts: 1,473 ✭✭✭tred


    Good stuff. your going to save yourself so much hassle this route. Not sure what Bryanf sent u, but there are also new ones out there not with door type dampers on the front that open and close when fan is on/off. Meaning no cold draughts in the winter blowing in!


  • Registered Users, Registered Users 2 Posts: 196 ✭✭L driver


    Bryan, could you pm me humidity fan details please?


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    L driver wrote: »
    Bryan, could you pm me humidity fan details please?
    aren't you building a new house? why not MVHR???


  • Registered Users, Registered Users 2 Posts: 196 ✭✭L driver


    going with localised units, so I still need good humidity fans for the bathroom and en suite.


  • Registered Users, Registered Users 2 Posts: 196 ✭✭L driver


    got pm. Thanks.


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    L driver, would you mind outlining your building design:
    1. are you going with positive input or demand controlled ventilation?
    2. how has this impacted your BER rating (maybe your working to 08 regs)?
    3. what air-tightness level are you aiming for?
    4. what heating system are you using?
    5. and have you assessed how many more kw's are required over using the MVHR?


  • Registered Users, Registered Users 2 Posts: 196 ✭✭L driver


    BryanF wrote: »
    L driver, would you mind outlining your building design:
    1. are you going with positive input or demand controlled ventilation?
    2. how has this impacted your BER rating (maybe your working to 08 regs)?
    3. what air-tightness level are you aiming for?
    4. what heating system are you using?
    5. and have you assessed how many more kw's are required over using the MVHR?

    hello,
    1 the localised units will have sensors, so I guess it is demand controlled.
    2 BER only takes efficiency % for it's calcs, as far as I remember, these units are a bit more efficient than regular mvhr. I don't think the difference was notable.
    3 I am aiming for passive levels, 0.6ach, but as it is a self build I am doubtful but I will post results here.
    4I am going with a GSHP with UFH.
    5No I have not.

    I will post more details and my experience when I am a bit further down the road. My build is taking time. Sorry if my answers above seem short. Ask/criticize anything, I will give an honest answer, I am not one of these that say everything about their build or choices is perfect.


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    L driver wrote: »
    hello,
    1 the localised units will have sensors, so I guess it is demand controlled.
    2 BER only takes efficiency % for it's calcs, as far as I remember, these units are a bit more efficient than regular mvhr. I don't think the difference was notable.
    3 I am aiming for passive levels, 0.6ach, but as it is a self build I am doubtful but I will post results here.
    4I am going with a GSHP with UFH.
    5No I have not.

    I will post more details and my experience when I am a bit further down the road. My build is taking time. Sorry if my answers above seem short. Ask/criticize anything, I will give an honest answer, I am not one of these that say everything about their build or choices is perfect.
    1. best to get some advice on this - as I understand it, a centralised unit is required also. PM me if there is a specific product you had in mind.
    2. best to do your provisional BER now


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    L driver wrote: »
    hello,
    1 the localised units will have sensors, so I guess it is demand controlled.
    2 BER only takes efficiency % for it's calcs, as far as I remember, these units are a bit more efficient than regular mvhr. I don't think the difference was notable.
    3 I am aiming for passive levels, 0.6ach, but as it is a self build I am doubtful but I will post results here.
    4I am going with a GSHP with UFH.
    5No I have not.

    I will post more details and my experience when I am a bit further down the road. My build is taking time. Sorry if my answers above seem short. Ask/criticize anything, I will give an honest answer, I am not one of these that say everything about their build or choices is perfect.

    LDriver - not good enough I am afraid

    at 0.6ACH MHRV is critical and necessary for the health of the building and yourself.

    Please read Part F building regs on ventalation - it will save you a LOAD of hassle later


  • Subscribers Posts: 42,171 ✭✭✭✭sydthebeat


    L driver wrote: »
    hello,
    1 the localised units will have sensors, so I guess it is demand controlled.
    .
    L driver wrote: »
    2 BER only takes efficiency % for it's calcs, as far as I remember, these units are a bit more efficient than regular mvhr. I don't think the difference was notable.
    .

    efficient at what? MHRV efficiencies relate to heat recovery.
    How does non heat recovery affect your head demand loads?
    L driver wrote: »
    3 I am aiming for passive levels, 0.6ach, but as it is a self build I am doubtful but I will post results here.
    .

    SAS who posts here is also a self build, achieved a q50 of 0.39, n50 of 0.32. So its very possible to achieve with attention to detail and educated and interested trades.


  • Registered Users, Registered Users 2 Posts: 196 ✭✭L driver


    the units have heat recovery, CO2 and RH sensors. The interested trades can be the problem, but I am very happy with my air tightness work and especially the guy who installed the attic membrane and pumped the cellulose. I have to wait and see the results.
    What mvhr and heat system did SAS go with do you know?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Ldriver

    just to clairfy - those individual vents are fine for a bathroom etc - but in a 0.6 ACH house you need to ventalte the corridors, bedroom, sitting room etc etc

    Part F gives you the details - there is a certain requirment for each "wet" room and there there is an overall figure

    For a new build I would up the Part F rate for the first while (depending on the time of year you build) to remove the x hundred litres of water from the cements and plasters (also change the filters a little more often in the first period)

    Don;t skip on the ventalation unless you like watching mushrooms grow on the inside of your house :mad::mad::mad::mad:


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    fclauson wrote: »

    just to clarify
    PM'd to say LD is proposing a product by 'an old conqueror (begins with a V) product.. not knocking it, but not convinced by it either. would like to see some data before passing judgement..


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Ventalation is about airflow through a property - prehaps I can compare MHRV with locally placed systems as to trying to cook a shepards pie by having bunsen bruners on a couple of corners or the pie hoping that the pie will get evenly cooked as opposed to having a whole oven which heats evenly, circulates the heat all the time and cooks from all sides


  • Registered Users, Registered Users 2 Posts: 756 ✭✭✭whowantstwoknow


    Hi all,

    Looking to replace old fans in bathrooms and would appreciate the recommendations given out earlier in the thread.

    Note in one room the vent is on an external wall and the other is up through the ceiling and tubed out through the attic to an opening in the fascia.

    Thanks
    W.


  • Registered Users, Registered Users 2 Posts: 2,390 ✭✭✭Bowlardo


    spud65 wrote: »
    Got an extension built a couple of years ago and the builders only put in a extractor fan in the bathroom now the motor is gone on it, just wondering if I put a vent in the wall plus if I take out the extractor fan an got a vent for the roof tile and ran it from the roof to the ceiling would that be alright, the shower is used 3 or 4 times a week.

    spud65
    BryanF wrote: »
    spud, small suggestion - get an extractor fan that is connected to a humidity sensor instead of the usual light or pulley option
    tred wrote: »
    Good stuff. your going to save yourself so much hassle this route. Not sure what Bryanf sent u, but there are also new ones out there not with door type dampers on the front that open and close when fan is on/off. Meaning no cold draughts in the winter blowing in!
    Could one of you point me in the right direction...going to do up the bathroom in the neat future and was looking for some advice....only have access to the external wall but if you could send me on the details of what you ended up using and were they a success?


  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    goggle: mechanical extractor fan humidity Sensitive