Low Voltage lighting query

  • 29-11-2011 8:36pm
    #1
    Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭


    I should know how to work this out but I forgot most of my Physics years ago. I am installing some 12 volt garden lighting. Because of the layout I have to run two 10 watt halogen lamps at 80 metres from the transformer & I can't loop.

    Obviously I am going to get a voltage drop over that distance & a dimming of the lamps. Can I overcome this by replacing the 10 watt lamps by 20 watts ? I have loads of capacity in the transformer.

    If I attach more lamps can I spread the voltage loss by putting 10 watt lamps near the transformer & higher wattages further away ?


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    I dont think you can overcome the voltage drop problem easily without oversizing cable or moving trafo closer

    maybe led will work


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    But surely a 20 watt lamp will burn brighter that a 10 watt even if the voltage drops ?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Discodog wrote: »
    But surely a 20 watt lamp will burn brighter that a 10 watt even if the voltage drops ?
    No.
    If the lamp is a higher wattage it will have a higher volt drop.
    Under voltage will cause the higher wattage lamp to be more yellow (less white) and it may even produce less light.

    The best solution is to size the cables correctly or install the transformers local to the lights to limit the volt drop.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the volt drop for a 12v 20watt bulb and 80mts of 1.5 swa seems to be 4v


    you could maybe try an led equivalent on the end of a roll of cable-to see if it works

    seems like a lot of trouble anyhow


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    the volt drop for a 12v 20watt bulb and 80mts of 1.5 swa seems to be 4v

    It would be a great help if you could link me to the calculation.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    20/12 * 80 * 0.031

    watt/volt * distance * voltdrop per amp/per metr


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    20/12 * 80 * 0.031

    watt/volt * distance * voltdrop per amp/per metr

    Thanks but how do I adjust that for different thickness of cable ?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the last table column 3 gives you the rough values
    http://www.csecables.com/power-cable/swa-cable.asp

    bit pointless as the larger cables will be prohibitively expensive -will be cheaper to site trafo closer to lamps for 12volt


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    the last table column 3 gives you the rough values
    http://www.csecables.com/power-cable/swa-cable.asp

    bit pointless as the larger cables will be prohibitively expensive -will be cheaper to site trafo closer to lamps for 12volt

    I know. Unfortunately moving the transformer is not easy. It would mean running outdoor mains cable which wouldn't be cheap either - might as well use mains lights.

    I would imagine that it is going to be a problem for a few people. I was in B&Q yesterday & their lighting display tells you to pick a transformer & the relevant number of lights - there is no mention of distance !

    If I could get an LED replacement bulb would it draw less current for the same output ?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    80m of cable for 12 volt lights will be more expensive than the equivalent for 230v

    you still need the copper and cable has to be suitable so it doesn't degrade


    those garden kits might come with say a 60va trafo and 3* 12v 20watt halogens -the hallogens will have a lead of 5 or 10m or something like that

    they wont work over 80m


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Discodog wrote: »
    If I could get an LED replacement bulb would it draw less current for the same output ?
    Yes


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    80m of cable for 12 volt lights will be more expensive than the equivalent for 230v

    you still need the copper and cable has to be suitable so it doesn't degrade


    those garden kits might come with say a 60va trafo and 3* 12v 20watt halogens -the hallogens will have a lead of 5 or 10m or something like that

    they wont work over 80m

    The kits in B&Q, made by Ring, are separate units that you match up. The cable comes in 75 metre bundles for about €30. It's only when you get home & read the in box instructions that distance comes into play. They say that a 75 metre ring is OK but the cable is pretty thin.

    I think that it's worth me experimenting with an LED "bulb" before I start digging up garden & patio :eek:


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    yes

    theres's a big difference in voltage drop between a light at the end of a 75m radial circuit
    and a light on a 75m ring
    if the light is centred on the ring the volt drop is 1/4 of the radial but the light is only 37.5m max from trafo then

    OK so it's not a linear voltage drop. I would of imagined that a lamp in the middle of the ring ie 37.5m from the transformer, would suffer 50% of the drop of a lamp at the end of 75 m.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    sorry there i was editing that:

    theres's a big difference in voltage drop between a light at the end of a 75m radial circuit

    and a light on a 75m ring

    if the light is centred on the ring the volt drop is 1/4 of the radial but the light is only 37.5m max from trafo then


    a ring would be the best wiring arrangement for those alright if the layout of the lights suited it


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Discodog wrote: »
    OK so it's not a linear voltage drop. I would of imagined that a lamp in the middle of the ring ie 37.5m from the transformer, would suffer 50% of the drop of a lamp at the end of 75 m.

    no it's a quarter

    if you go back to the equation -distance is halved and csa is doubled


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    M cebee wrote: »
    a ring would be the best wiring arrangement for those alright if the layout of the lights suited it

    Unfortunately the return leg has to cross a patio & there is no grout so no easy option.


  • Moderators, Science, Health & Environment Moderators Posts: 1,852 Mod ✭✭✭✭Michael Collins


    I'm not aware of the regulations in this area but is it possible Discodog could use a 24 V power supply and a 12 V regulator at the lamps? It would certainly solve the problem...


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    don't think there would be any difference in regulations

    i assume they're both classed as 'pelv' as you couldn't guarantee separation from ground on the wiring


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    I'm not aware of the regulations in this area but is it possible Discodog could use a 24 V power supply and a 12 V regulator at the lamps? It would certainly solve the problem...


    ebay seems to have 24v halogen and led in mr16 anyhow so that would be simpler


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    don't think there would be any difference in regulations

    I would agree, I just dont think it would be worth the hassle or espense.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Yes there isnt much the op can do except install the 12v kit as per instructions


  • Moderators, Science, Health & Environment Moderators Posts: 1,852 Mod ✭✭✭✭Michael Collins


    M cebee wrote: »
    ebay seems to have 24v halogen and led in mr16 anyhow so that would be simpler

    Yeh that'd be even better, but I guess it's too late now if the kit has already been purchased.


  • Registered Users, Registered Users 2 Posts: 15,961 ✭✭✭✭Discodog


    Had I of seen them I might of gone for 24 volt but then again there is less risk with B&Q. A transformer is a heavy lump to send back if it's faulty. First I am going to try some LED bulbs & if that doesn't work then I will have to cross the patio to complete the ring.

    I have done some really nice layouts before using a 12 volt transformer & car bulbs. They can look nice in old bottles & old lamps etc. It's also really easy to vary the wattage as there is a good available range.


Advertisement