Overhead Power Cable for Shed

  • 05-11-2011 4:24pm
    #1
    Registered Users, Registered Users 2 Posts: 813 ✭✭✭


    I want to run an overhead cable from my house to my shed - the cable will be some 12 feet off the ground and a 5 metre clear span. I just want to operate 2 no 60 watt bulbs and also fit a socket in the wall - charge the lawnmower and run a power tool occasionally.

    So what type of cable do I need to use ? The maximum load will be 2 kw. The cable will be some 12m long, overall. That 5m clear span will be exposed to the weather.

    Do I need SWA cable? Do I need special brackets at each end ? What mm2 cable do I need ?

    Thanks for any advice, in advance.


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2.5 swa off a radial circuit will prob do that

    if you're sure that's all you need


  • Registered Users, Registered Users 2 Posts: 813 ✭✭✭Poulgorm


    Thank you for that. What is the next bigger size of SWA cable (bigger than 2.5) ?

    If there was not a massive difference in cost, I might go a slightly heavier cable - mechanical strength, if nothing else.

    - Thanks


  • Registered Users, Registered Users 2 Posts: 76 ✭✭086lavey


    Poulgorm wrote: »
    Thank you for that. What is the next bigger size of SWA cable (bigger than 2.5) ?

    If there was not a massive difference in cost, I might go a slightly heavier cable - mechanical strength, if nothing else.

    - Thanks
    6sq swa:)


  • Registered Users, Registered Users 2 Posts: 4,890 ✭✭✭meercat


    think 3x4 swa is also available


  • Registered Users, Registered Users 2 Posts: 976 ✭✭✭heffo500


    Would not just run a catenary wire and cable tie MYMJ to it? I think it would be a better job.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i think swa is better
    3*4 is next size up


  • Registered Users, Registered Users 2 Posts: 813 ✭✭✭Poulgorm


    Job done. Lights and socket operational.

    2.5 swa used.

    Thanks for all your help, in particular M cebee. Take a bow!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Poulgorm wrote: »
    Thanks for all your help, in particular M cebee. Take a bow!

    A dickie bow?:)


  • Registered Users, Registered Users 2 Posts: 976 ✭✭✭heffo500


    M cebee wrote: »
    i think swa is better
    3*4 is next size up

    Why do you think swa is better out of curiosity?

    I was under the impression it was only meant for UG applications??


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,655 Mod ✭✭✭✭2011


    heffo500 wrote: »
    Would not just run a catenary wire and cable tie MYMJ to it? I think it would be a better job.

    NYMJ is not suitable for outdoor use unless shielded from the sun. Although it is more resistant to UV than T & E it will beak down.
    I was under the impression it was only meant for UG applications??
    No. On large industrial installations in Ireland SWA is used extensively for everything from GS, lighting, motors, mains and sub mains distribution to generators. The project I am working on now over 90% of all mains cabling is SWA with loads from less than 10W to greater than 300kW.

    SWA is designed for outdoor use and offers superior mechanical protection.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Carrying 300kw wouldnt tell us its certainly a big cable, except we know its an swa connected to 400v.


Advertisement