Heating help!! (myson power extra)

  • 30-10-2011 8:56pm
    #1
    Registered Users, Registered Users 2 Posts: 101 ✭✭


    So i have moved into a new house (3 years old) and since then every time i try to turn on hot water the rads and hot water heat up and every time i turn on centrel heating the rads only turn on !
    How do i change it so that my rads only turn on when centrel heating is turned on and that when hot water is turned on that ONLY hot water heats up ??
    Thanks

    PS.. i read up that its something to do with the myson power extra valve or something like that behind the boiler..


Comments

  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    seems like a wiring problem
    may need to get a sparks in
    i dont think its as simple as swapping the mini valves over


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    Thanks for the reply
    I got the plumber in 3 times and every time he changes it, ie. Changes them around like the heating and the water and the last time he was here he left it like this..

    One time it was that HW heated up the rads and the hot water and that CH .. And now its HW heats up hot water and rads and CH Heats up rads ..then i rang the plumber up to change them he changed them wrong.

    But i want CH to heat up the rads and hot water and HW to heat up just hot water .. I think thats what its supposed to do anyway!


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    Yulkmn wrote: »

    But i want CH to heat up the rads and hot water and HW to heat up just hot water .. I think thats what its supposed to do anyway!

    spot on

    best get a sparks i think
    it is just a matter of changing a few wires around


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Sounds like you have a dodgy 3 way mid position diverter valve or something, a picture would speak a thousand words here


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    DGOBS wrote: »
    Sounds like you have a dodgy 3 way mid position diverter valve or something, a picture would speak a thousand words here

    I dont know the myson power extra thing seems fine.. Does anyone know how i could close and open the valves ? Just like the plumbers did they opened and closed it non of them were spot on ..


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    meercat wrote: »

    spot on

    best get a sparks i think
    it is just a matter of changing a few wires around[/Quote]

    The plumber said it all fine .. Its just that he never set up the myson power extra properly i think..


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Its a 3port mid position valve, so it is

    a) either wired incorrectly so calling for both dhw and ch when only dhw is called for

    b) not fully moving to the dhw position (not closing fully)

    Tell your plumber to RTFM, for gods sake, or did he stop learning when he finished his apprenticeship


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    DGOBS wrote: »
    Tell your plumber to RTFM, for gods sake, or did he stop learning when he finished his apprenticeship

    Haha ^^.. I actually dont know! I jus know that he said everything is fine ! And he jus goes into the little boiler room and switches something and it all changes ! I just want to know how can i change them !! ?? I would just changed them around until i got them right...


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    google and follow a wiring 'Y-plan' for 3 port MV


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    DGOBS wrote: »
    google and follow a wiring 'Y-plan' for 3 port MV

    Im not very good with wiring but i just looked at the myson power extra and it has like a picture of 2 rads on it and there are 2 arrows pointin on one of the rads and 1 arrow pointing on the other rad... And above that there is like a sliding switch and it says " manual override only" ... If thats any help...


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    You would need to follow the wiring diagram between your time and temperature controls to the valve and confirm the correct wiring


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    DGOBS wrote: »
    You would need to follow the wiring diagram between your time and temperature controls to the valve and confirm the correct wiring
    i have just checked and the wiring is all fine i found some instructions.. But still problem not solved !


  • Posts: 0 [Deleted User]


    Yulkmn wrote: »
    i have just checked and the wiring is all fine i found some instructions.. But still problem not solved !

    Asper post 8, either wired incorrectly(which I'd go for) or sludge in the system stopping the valve from operating properly.


  • Registered Users, Registered Users 2 Posts: 101 ✭✭Yulkmn


    Does anyone know how i can manualy change the way the valves operate like the plumber does???


  • Posts: 0 [Deleted User]


    Yulkmn wrote: »
    Does anyone know how i can manualy change the way the valves operate like the plumber does???

    The MPE 322/328 is designed to control water circulation in primary hot water and central heating circuits, by diverting flow to either circuit or to both simultaneously using a single valve.

    For convenience the two neon indicator lights illuminate indicating which port is open.

    When the manual lever is moved to the right, ports A and B are open, this is used when filling, venting or draining the system. The spring return, Mid-Position actuator – valve rests in the hot water only position.

    http://www.myson.co.uk/static_files/my/media/downloads/MPE_322_Installation_sheet_Sept_2009.pdf