Downstairs rads not heating?? I'm stumped

  • 23-10-2011 9:32am
    #1
    Registered Users, Registered Users 2 Posts: 10,258 ✭✭✭✭


    Downstair rads not heating?? See 3 actuator valves in hot press could something be wrong with them?? Rads upstairs are piping hot downstairs rads were barely warming from September just the tops of them mind but now nothing??

    Baby in house need to sort this ASAP??


Comments

  • Registered Users, Registered Users 2 Posts: 1,611 ✭✭✭cgarrad


    Have you bled them?


  • Registered Users, Registered Users 2 Posts: 3,423 ✭✭✭Avns1s


    IS there a separate circulation pump for the downstairs circuit? If so check that its working.

    Also, the motorised valve may not be opening fully.


  • Registered Users, Registered Users 2 Posts: 1,428 ✭✭✭Dotsie~tmp


    Check obvious. Is downstairs room stat set very low? The motor valves likey do up, down and cylinder. Easy to spot wire from cylinder stat to valve, ignore that one. Get help, someone to turn stats to call heat while u listen for which valve is up and down or if its actuating. When u isolate down valve press its manual on lever to the override locked setting and see what happens.


  • Registered Users, Registered Users 2 Posts: 478 ✭✭rightjob!


    one of the actuators is stuck closed,try turning it manually