Welding power lead

  • 04-10-2011 6:33pm
    #1
    Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭


    Hi lads

    One for the 'electricans' out there....

    I want to make up an extension power lead for arc welder. Would 4mm2 cable to ok? A standard 13amp extension lead uses 1.5mm2

    Muckit


Comments

  • Registered Users, Registered Users 2 Posts: 32 fear tuath


    Keep the power lead to the welder as short as possible,long leads loose power and the plant will not operate correctly.
    You can keep your earth and electrode leads as long as you want with out loosing power and your earth will be close to your weld.
    Just try and operate a electric power washer on a long lead and you will see it loose power.


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    fear tuath wrote: »
    Just try and operate a electric power washer on a long lead and you will see it loose power.

    Funny you mention this because I was hoping to use the lead for this aswel!! I thought if I kept the core size large that this would not be the case??

    Would I be better getting another extension of the hose lance? It's already 60'


  • Closed Accounts Posts: 2,279 ✭✭✭snowman707


    4 SQ will be fine, and you will have no losses,

    only thing to bear in mind is roll out the cable fully while in use , i.e. do NOT have it coiled or rolled up, as this will cause inductance and all sorts of problems.


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    snowman707 wrote: »
    4 SQ will be fine, and you will have no losses,

    only thing to bear in mind is roll out the cable fully while in use , i.e. do NOT have it coiled or rolled up, as this will cause inductance and all sorts of problems.

    Thanks snowman. Yes I heard about rolling out leads fully before use and I'I be doing this, as will be using it at it's full length! Also lead won't be going on a reel


  • Registered Users, Registered Users 2 Posts: 349 ✭✭St. Leibowitz


    It depends.

    The most essential piece of information is missing. How long is the lead you want to make up ??

    The length of the cable, power required (or current drawn) of the kit and the power source are needed to properly answer this. We can assume a standard 13A plug with a 230V domestic supply for the second two, but really need to cable length to be sure of giving a correct answer.


  • Advertisement
  • Closed Accounts Posts: 521 ✭✭✭Atilathehun


    The nearest shed I have to the house is 80 meters away. There is an old undrgound armour cable running from the consumer unit in the house to a junction box in the shed. From there I have lights and stuff in a few small sheds close by.
    Now I built a slatted shed a further 50 meters away in the past few years.
    We ran underground cable from the junction box in the shed, to the new shed, and installed a consumer unit in the new shed. We wired up lights and sockets from there.
    Guy who came afterwards to do some welding, who plugged innto the sockets in new shed, worked away fine on most of the work. Occasionally, had a bit of trouble when doing heavy welding, but be enlarge no major issues.
    The hot water washer sometimes trips out the ELCB, on start up. That is to say, I can start the machine fine, and fire up the burner for hot water. However sometimes I do find when I pull the trigger on the lance, to start washing the ELCB may trip.
    I get around that, by holding the lance trigger in the pulled position, before I switch on the machine.

    By the way, Muckit, how is the powerline working:p


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    It depends.

    The most essential piece of information is missing. How long is the lead you want to make up ??

    The length of the cable, power required (or current drawn) of the kit and the power source are needed to properly answer this. We can assume a standard 13A plug with a 230V domestic supply for the second two, but really need to cable length to be sure of giving a correct answer.

    Well the hot washer has a draw of ~2200W (3hp pump). I'd have to check the welder, but it's a standard typical arc stick welder (180A). Does anyone know off hand the power (wattage) draw on these? :confused:

    The powerwasher would need to be fitted with a 16amp fuse (if using a domestic plug), but I've fitted outdoor round plugs on mine, because that's what's fitted in my sheds.

    RE: Length? How long is a piece of string? :p I'd like to make it at least 100', if not 150' for comfort (for using the powerwasher anyway)


  • Registered Users, Registered Users 2 Posts: 950 ✭✭✭Dupont


    Muckit wrote: »
    RE: Length? How long is a piece of string? :p I'd like to make it at least 100', if not 150' for comfort (for using the powerwasher anyway)

    twice the length of half of it:p


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    Well lads

    This is the lead I made up in the end. 30m of 6sq cable. Shouldn't burn this out! Some lump of a cable :D


  • Closed Accounts Posts: 3,087 ✭✭✭vanderbadger


    Muckit wrote: »
    Well lads

    This is the lead I made up in the end. 30m of 6sq cable. Shouldn't burn this out! Some lump of a cable :D

    expensive stuff too id say


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    expensive stuff too id say

    The cable + male/female sockets.....I hadn't much change out of €80 :o

    Still, I have it and I know it'I do the job without damaging or burning anything out. Could work out cheap in the long term ;)


  • Closed Accounts Posts: 8,570 ✭✭✭Rovi


    It's certainly cheaper than burning out a welder or power washer :D


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    Rovi wrote: »
    It's certainly cheaper than burning out a welder or power washer

    This is it :rolleyes: You can't put a price on peace of mind.


  • Registered Users, Registered Users 2 Posts: 227 ✭✭yog1


    are those 16amp or 32amp plug's on the lead


  • Registered Users, Registered Users 2 Posts: 11,174 ✭✭✭✭Muckit


    yog1 wrote: »
    are those 16amp or 32amp plug's on the lead

    16amp