Trickle vents

  • 30-05-2011 8:27pm
    #1
    Registered Users, Registered Users 2 Posts: 142 ✭✭


    I have read numerous posts on using trickle vents for background ventilation in dwellings. If someone could point me to a thread which specifically answers the following I would be grateful.

    1. What is the current requirement for background ventilation in dwellings? Is it 6500mm sq for each habitable rooom in the current Part F regs? (I couldn't find any mention of 6500m sq. in the 2009 Part F document.)

    2. Is there a requirement for background (natural) ventilation on top of mechanical ventilation in areas such as bathrooms, WC's, utility rooms and kitchens?

    3. What is the requirement for ventilation in areas such as halls/foyers?

    I would appreciate if someone could give me a direct answer to these questions as I have reviewed several posts and Part F but am still confused :confused:


Comments

  • Registered Users, Registered Users 2 Posts: 142 ✭✭awnow


    awnow wrote: »
    2. Is there a requirement for background (natural) ventilation on top of mechanical ventilation in areas such as bathrooms, WC's, utility rooms and kitchens?

    I meant "mechanical extract" instead of "mechanical ventilation" in this point. :)


  • Closed Accounts Posts: 2,389 ✭✭✭Carlow52


    Part F 2009 tells me the following

    " Ventilation Rates
    1.2.2.1 Where the air permeability is
    5m3/(h.m2) or greater, the minimum total
    equivalent area of background ventilators
    providing general ventilation should be 30,000
    mm2 with an additional 5,000 mm2 for each
    additional 10 m2 floor area above the first 70m2
    of floor area measured. For single storey
    dwellings situated at ground level or on any
    storey up to four storeys, an additional 5,000
    mm2 per dwelling should be provided. Where
    air permeability is less than 5m3/(h.m2) all
    equivalent areas stated above should be
    increased by 40%. As noted in Paragraph
    1.1.15, the areas specified should be
    increased by 25% where free area of
    ventilators is used instead of equivalent area.
    Example calculations are provided in Appendix
    1."

    So we need to know the air permeability of the dwelling.

    Table 1 and Diagram 4 on page 14 spell it out pretty much for a typical dwelling, am not going to repeat it here
    see it here http://www.environ.ie/en/TGD/

    The ans to ur Q2 is yes, see above for where to find answers.

    Halls, foyers are not classed as habitable rooms so there are no specific requirements as can be seen from the example is appendix 1 page 29


  • Registered Users, Registered Users 2 Posts: 142 ✭✭awnow


    thanks carlow52. I had another read through and it makes sense. :)