Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

replacement of bedroom windows - fire regs breached?

  • 02-04-2011 11:15pm
    #1
    Closed Accounts Posts: 16


    Guys
    Ive recently replaced my bedroom windows single pane windows with double-glazed units on a old 2 story cottage.

    Im now thinking of renting out the place but have realized it will be even harder for potential tenents to escape if the worst happens and a fire occur (they would have to break the glass as the top window is too small to get out of).

    Does this contravene current building regs and am I open to prosecution if anything (god forbid) goes wrong in the place?

    thanks


Comments

  • Registered Users, Registered Users 2 Posts: 46,549 ✭✭✭✭muffler


    From Part B of the regs
    Where windows are being replaced in existing
    dwelling houses, it is recommended that bedroom
    windows should meet, in as far as is practicable, the
    provisions outlined at 1.5.6. In the case of other
    habitable rooms, opening sections should not be
    reduced or altered to an extent that reduces their
    potential for escape or rescue.
    Windows for Escape or Rescue
    1.5.6 Windows may provide an alternative means
    of escape or may be used for rescue purposes in
    dwelling houses of limited height. As an alternative, a
    door which gives direct access to a balcony or roof,
    which is suitable for rescue by ladder or for escape
    may be used. Where provision is made in this subsection
    for windows for these purposes (see
    paragraphs 1.5.2, 1.5.3, 1.5.7.6 and 1.5.8.2), such
    windows should comply with the following:
    (a) The window should have an openable section
    which can provide an unobstructed clear open
    area of at least 0.33 m2 with a minimum width
    and height of 450 mm (the route through the
    window may be at an angle rather than straight
    through). The opening section should be capable
    of remaining in the position which provides this
    minimum clear open area.
    (b) The bottom of the window opening should be
    not more than 1100 mm and not less than 800
    mm (600 mm in the case of a rooflight) above the
    floor, immediately inside or beneath the window
    or rooflight. As an exception to the general
    guidance in TGD K (Stairways, Ladders, Ramps
    and Guards) that guarding be provided for any
    window, the cill of which is less than 800 mm in
    height above floor level, guarding should not be
    provided to a rooflight opening provided in
    compliance with this paragraph.
    (c) In the case of a dormer window or rooflight, the
    distance from the eaves to the bottom of the
    opening section of the rooflight, or, where the
    window is vertical, the vertical plane of the
    window, should not exceed 1.7 m measured
    along the slope of the roof.
    (d) The area beneath the window externally should
    be such as to make escape or rescue practicable.
    For example,
    (i) where there is a clear drop from a window in
    an upper storey or attic conversion, the
    ground beneath the window should be
    suitable for supporting a ladder safely and be
    accessible for rescue by the fire services or
    others.
    (ii) Where there is a roof, balcony or canopy
    below a window, it should be structurally
    adequate to support those using the window
    for escape or rescue.
    (e) The opening section of the window should be
    secured by means of fastenings which are readily
    openable from the inside and should be fitted
    with safety restrictors. Safety restrictors can be
    either an integral part of the window operating
    gear or separate items of hardware which can be
    fitted to a window at the time of manufacture or
    at installation. Restrictors should operate so that
    they limit the initial movement of an opening
    section to not more than 100 mm. Lockable
    handles or restrictors, which can only be
    released by removable keys or other tools,
    should not be fitted to window opening sections.


Advertisement